Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Smart-UPS X 3000 Firmware update failure via NMC web upgrade

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS X 3000 Firmware update failure via NMC web upgrade
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
msadmin11
msadmin11
Cadet

Posted: ‎2024-01-22 03:55 AM

0 Likes
1
2405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-22 03:55 AM

Smart-UPS X 3000 Firmware update failure via NMC web upgrade

Hi all,

I have a Smart-UPS X 3000 SKU SMX3000RMHV2U Firmware Rev 07.4 (ID1003) and after doing the firmware update via the NMS 3 web interface I'm suffering the dreaded bootloop. Firmware update was the correct FW SMX1003UPS_15-0.enc. Have tried all sorts to get this to re-flash but not having much joy. Can Telnet and FTP over to the NMC and UPS via serial, can dump the SMX1003UPS_15-0.enc into the tmp dir, but when trying to run the upsfwupdate -install -file /tmp/SMX1003UPS_15-0.enc CLI the response is E101 Command not found. Looking at some previous posts, I found out that some devices don't have the upsfwupdate option on them, it looks like mine is one of those devices. The FW Configuration Utility is of no use, as the time it takes to launch it and agree the terms and conditions as well as choosing the port, the UPS is already starting to reboot. Does anyone have any idea of what .exe or other CLI command I could dump onto the tmp dir in order to get the FW upgrade to initiate, or does anyone has any other ideas of how I can recover this box. The firmware upgrade via the web interface must have failed prior to fully installing the latest firmware as the error on the front screen is "firmware update in progress".  

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Teken
Kirk Teken
Kirk

Posted: ‎2024-01-31 06:10 AM

0 Likes
0
2351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-31 06:10 AM

I would suggest you try the same using the supplied serial cable connect directly to the UPS and using the wizard instead. Also, even if your UPS allows the output to be left on (enabled) turn it off when you attempt to load the firmware.

 

The NMC should be removed if you use the direct serial connection to the UPS.

 

Lastly, there is a APC FAQ that relates to the SRT UPS models which says to use the LCD Menu to force the UPS to continue the firmware upgrade process. I call this out because on a couple of SMX units the options and steps were not (obviously there) but pressing the menu to I believe about / firmware caused the process to complete. 🤦‍♂️

 

Regardless, I would contact APC Support first. Next find the serial cable and download the previous, same, and newer firmware so it’s available.

 

Remove the NMC . . . Turn off the load (given it’s bricked) just disconnect the loads as it’s too late now. 🙁 Give it another try and report back the outcome. You may also want to ask (APC Support) how to use the USB port to update the firmware through the NMC. 

Good luck 🤞 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore