Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-28 10:38 AM . Last Modified: 2024-03-15 05:53 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:38 AM . Last Modified: 2024-03-15 05:53 AM
Hi there,
In our environment we are monitoring the devices with PRTG.
I've tried all options it has for APC devices but I cannot find a sensor for the current error state.
The Smart-UPS X 1000 states: Battery Disconnected but in PRTG it shows me all is fine.
Does anybody know which OID I should be using to capture this error?RXDisqghaOZKN6Gak5d3LA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
XfByaGUHvTlYDq8QxYHimA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:38 AM . Last Modified: 2024-03-15 05:53 AM
Hi Ronald,
To give you an additional data point - the OID .1.3.6.1.4.1.318.1.1.1.11.1.1.0 (upsBasicStateOutputState) has a bunch of flags that can be triggered based on different UPS events. Flag 33 for "no batteries attached" should be flipped to "1" when a battery disconnect event occurs.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:38 AM . Last Modified: 2024-03-15 05:53 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:38 AM . Last Modified: 2024-03-15 05:53 AM
Hi there,
I have found a work around for my issue.
By using the OID 1.3.6.1.4.1.318.1.1.1.2.3.4.0 and setting upper & lower limits I can check the voltage and verify the battery connectivity.
#closed
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:38 AM . Last Modified: 2024-03-15 05:53 AM
Hi Ronald,
To give you an additional data point - the OID .1.3.6.1.4.1.318.1.1.1.11.1.1.0 (upsBasicStateOutputState) has a bunch of flags that can be triggered based on different UPS events. Flag 33 for "no batteries attached" should be flipped to "1" when a battery disconnect event occurs.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of