Hi everybody,
We are about to sell an APC VT model UPS.
The last thing we need to know is if the UPS can work on an IT grounding system (neutral to earth).
The UPS will be used to supply security lightning in a cinema.
Thank you!
Samy
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:21 AM . Last Modified: 2024-03-19 01:36 AM
Hello,
The SUVT ups requires a standard neutral that is bonded to ground at the service entrance. In this case, so long as your neutral (earth ground) and the input ground are electrically the same point, I do not see how there would be an issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:21 AM . Last Modified: 2024-03-19 01:36 AM
Hello,
The SUVT ups requires a standard neutral that is bonded to ground at the service entrance. In this case, so long as your neutral (earth ground) and the input ground are electrically the same point, I do not see how there would be an issue.