Smart-UPS VT 40 kVA and mechanical bypass

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
chaser_apc
Crewman
Crewman
0 Likes
2
467

Smart-UPS VT 40 kVA and mechanical bypass

This was originally posted on APC forums on 12/3/2015


Hello,

We have Smart-UPS VT 40 kVA w/4 Batt Mod Exp to 4, int Maint Bypass, Parallel Capable SUVTP40KH4B4S, PS0813240713, Firmware Revision: 912.0405.I.

There are two critical mistakes:

In bypass in response to an internal hardware fault.

A power module fault exists.

Can we try to reboot to get rid of them?

Bellow – our adventures…

01.12.2015

07:53:13

UPS: In bypass in response to the UPS front-panel or a user-initiated software command, typically for maintenance.

01.12.2015

07:53:12

UPS: Restored the local network management interface-to-UPS communication.

01.12.2015

07:52:47

System: Network service started. System IP is 10.4.142.230 from manually configured settings.

01.12.2015

07:52:47

System: Warmstart.

01.12.2015

07:51:49

UPS: The output power is now turned on.

01.12.2015

07:51:48

UPS: In bypass in response to the UPS front-panel or a user-initiated software command, typically for maintenance.

01.12.2015

07:48:50

UPS: An internal mechanical bypass no longer exists.

01.12.2015

07:48:30

UPS: The output power is turned off.

01.12.2015

07:48:29

UPS: The external Switch Gear Q003 has opened.

01.12.2015

07:47:38

System: NTP update failure.

01.12.2015

07:47:28

UPS: The output power is now turned on.

01.12.2015

07:47:28

UPS: An internal mechanical bypass exists.

01.12.2015

07:47:28

UPS: The external Switch Gear Q003 has closed.

01.12.2015

07:46:04

UPS: An internal mechanical bypass no longer exists.

01.12.2015

07:46:03

UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.

01.12.2015

07:45:47

UPS: The external Switch Gear Q003 has opened.

01.12.2015

07:45:41

UPS: The output power is turned off.

01.12.2015

07:45:28

UPS: An internal mechanical bypass exists.

01.12.2015

07:45:28

UPS: The external Switch Gear Q003 has closed.

01.12.2015

07:40:42

UPS: An input voltage or frequency problem prevents switching to bypass mode.

 

02.12.2015

01:53:51

UPS: In bypass in response to an internal hardware fault.

02.12.2015

01:53:51

UPS: A power module fault exists.

02.12.2015

00:15:39

UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.

02.12.2015

00:15:18

UPS: An input voltage or frequency problem prevents switching to bypass mode.

02.12.2015

00:15:17

UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.

02.12.2015

00:14:57

UPS: An input voltage or frequency problem prevents switching to bypass mode.

02.12.2015

00:14:57

UPS: In bypass in response to an internal hardware fault.

Tags (2)

Accepted Solutions
chaser_apc
Crewman
Crewman
0 Likes
0
467

Re: Smart-UPS VT 40 kVA and mechanical bypass

This was originally posted on APC forums on 12/14/2015


Bill, thanks a lot for your reply.

We have done restart of the device. And “raw status” now is OK. No mistakes at all!

M States = 07 04 04

00000000 00000000

00000000 02

Thank you!

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
467

Re: Smart-UPS VT 40 kVA and mechanical bypass

This reply was originally posted by Bill on APC forums on 12/4/2015


Hello Vladimir,

I suggest first contacting the technical support group for your region:
http://www.apc.com/site/support/index.cfm/contact-information/ (choose your county with the drop down menu, so it will give you the approriate tech support phone#)

They will be able to help you gather Raw Data on the faulted module, decode it, and suggesting the next steps.

This may include reseating the UPS power module, but I would not suggest taken any action till going over the data with tech support.

If it does get to point where you will be reseating the module. I would suggest putting the whole system to external bypass as you have done before. Power the UPS down completely (opening the input breaker, and pulling out all the batteries). then reseat the module (With the batteries still pulled out). Then restore power (insert all batteries, and supply input power). And continue to return from bypass operation if the UPS appears to be running without fault (if faults persists, you will likely need to replace the UPS power module).

chaser_apc
Crewman
Crewman
0 Likes
0
468

Re: Smart-UPS VT 40 kVA and mechanical bypass

This was originally posted on APC forums on 12/14/2015


Bill, thanks a lot for your reply.

We have done restart of the device. And “raw status” now is OK. No mistakes at all!

M States = 07 04 04

00000000 00000000

00000000 02

Thank you!