Smart-UPS VT 10 kVA: A Weak Battery Exists

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS VT 10 kVA: A Weak Battery Exists
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 09:21 PM . Last Modified: ‎2024-03-06 11:57 PM

0 Likes
3
621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:21 PM . Last Modified: ‎2024-03-06 11:57 PM

Smart-UPS VT 10 kVA: A Weak Battery Exists

Our Smart-UPS VT 10 kVA: ran a scheduled weekly self test, the test failed with 'A weak battery exists', contacted our UPS maintenance company who sent tech to site, he tested and could not fine the weak battery, in fact he said it was all good (waiting on report from tech who did the testing).  we're still getting the alert every 2 minutes though for weak battery and self test failed ??, below are the SNMP traps being generated.  Anyone seen this before?  Tech thinks it may well be system generated alert has been triggered after X amount of time, UPS has been in production for about 2 years 8 months.

snmpTrapEnterprise = PowerNet-M​IB:apc
experimental.1057.1.0 = 10.9.128.2​51
sysUpTime = 354 days 21 hours 36 minutes 55.30 seconds
snmpTrapOID = PowerNet-M​IB:apc.0.3
mtrapargsString = UPS: Self-Test Failed

snmpTrapEnterprise = PowerNet-M​IB:apc
experimental.1057.1.0 = 10.9.128.2​51
sysUpTime = 354 days 21 hours 36 minutes 52.80 seconds
snmpTrapOID = PowerNet-M​IB:apc.0.7​7
mtrapargsInteger = 36
mtrapargsString = UPS: A weak battery exists.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 09:21 PM . Last Modified: ‎2024-03-06 11:57 PM

0 Likes
0
621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:21 PM . Last Modified: ‎2024-03-06 11:57 PM

Thx Bill, ran the self-test via NMC and it failed.  Looks like the default setup is that a notification is generated every 2 minutes until problem is fixed, do you if you can stop the alarm notification ?

26-Jul-16 10:50:41 UPS: Self-Test Failed
 26-Jul-16 10:26:24 System: NTP update successful.
 26-Jul-16 09:57:23 UPS: Started a self-test.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:21 PM . Last Modified: ‎2024-03-06 11:57 PM

0 Likes
0
621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:21 PM . Last Modified: ‎2024-03-06 11:57 PM

Paul,

When the tech was on site did he run a self-test and if so did it fail? If he did not run a self-test I suggest doing so to see if the error clears. You can run the self-test via the NMC. 

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-06-30 09:21 PM . Last Modified: ‎2024-03-06 11:57 PM

0 Likes
0
621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:21 PM . Last Modified: ‎2024-03-06 11:57 PM

My experience with the SURT 10kVA is that if there is one bad battery in any of the four cages (out of a total of 32 batteries!), it will fail the "load" test upon startup.  The "VT" series is advertised to have more "intelligent" charging system - it is possible that it can determine if any of the (many) batteries are about to fail.  Just checking voltages of the battery cages will not indicate a single (or more) bad batteries due to "surface" charge.  There must be some type of "load" test.  Check how the technician did the test and the results.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 09:21 PM . Last Modified: ‎2024-03-06 11:57 PM

0 Likes
0
622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:21 PM . Last Modified: ‎2024-03-06 11:57 PM

Thx Bill, ran the self-test via NMC and it failed.  Looks like the default setup is that a notification is generated every 2 minutes until problem is fixed, do you if you can stop the alarm notification ?

26-Jul-16 10:50:41 UPS: Self-Test Failed
 26-Jul-16 10:26:24 System: NTP update successful.
 26-Jul-16 09:57:23 UPS: Started a self-test.
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of