Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-1201:29 PM
Smart-UPS SRT 3000 "battery pack incompatible"
So in April I purchased an Smart-UPS SRT 3000 (SRT3000UXI-NCLI). Today, (finally) arrived a pair of 1U battery packs (XBP48RM1U-LI), which at the time, I thought were the right ones.. However, when I connected them all up, it appeared to go through some sort of firmware upgrade, and now the main unit is telling me "battery pack incompatible". Is this because they're not the "XBP48RM1U2-LI" models?..
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-1609:14 AM
If the information you’ve provided up above is accurate. You’re correct the extended battery pack you have on site is the wrong one! ☹️
The XBP48RM1U2-LI is the correct extended battery pack for this specific APC UPS Lithium model. You can affirm this in the APC resource link for compatible batteries:
Let me know if you have more questions. If not and this information helped resolve the question please do mark this as a solution to assist the next person asking the same. 👍