Smart-UPS SRT 2200: "The battery power is too low to support the load" after battery repl.
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2811:48 AM. Last Modified: 2024-03-1504:20 AM
Smart-UPS SRT 2200: "The battery power is too low to support the load" after battery repl.
Hello,
I have the error "The battery power is too low to support the load; if power fails, the UPS will be shut down immediately." after original APC battery replacement.
The battery have been replaced the 23/09/2020, the error started to show on 12/11/2020.
State of Charge
100.0 %
Runtime Remaining
8min 27sec
Battery Voltage
82.1 VDC
Replacement Battery Cartridge SKU
APCRBC141
Smart-UPS SRT 2200
Last Battery Transfer
Unacceptable utility voltage rate of change
Battery Temperature
25.0°C
Runtime Remaining
8min 13sec
UPS Input
Input Voltage
221.5 VAC @ 50.0 Hz
UPS Output
Output Voltage
229.8 VAC @ 50.0 Hz
Load Current
2.8 Amps
Output VA
28.4 %
Output Watts
28.1 %
Output Efficiency
battery charging
Output Energy Usage
4194.30 kWh
Battery Status
State of Charge
100.0 %
Battery Voltage
82.1 VDC
Next Battery Replacement Date
24.03.2025
I have already run the "Runtime calibration" from UPS Network Management Card 2 web interface.