Smart-UPS SRT 10000 "An inverter fault exists"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS SRT 10000 "An inverter fault exists"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All
Related Products
product field
Schneider Electric
Uninterruptible Power Supply (UPS)
product field
Schneider Electric
Smart-UPS On-Line

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Hunda67
Crewman Hunda67
Crewman

Posted: ‎2022-12-27 11:48 PM

0 Likes
9
10181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-27 11:48 PM

Smart-UPS SRT 10000 "An inverter fault exists"

Hi,

 

We have several Smart-UPS SRT 10000 (model: SRT 10KRMXLI). They are 5 years old and had new battery packs fitted 6 months ago. Two of them came up with an the following error: "An inverter fault exists". First one was 6 months ago and we replaced the entire UPS. Second one happened one month ago. When the mains power failed the UPS came back up bit did not turn the outlets back on. We went to site and cleared all faults, turned the outlets back on using front panel controls and it came back to life with no errors. We run several self tests and all passed. We simulated several power failures and all was good. 5 days ago it reported theat "an inverter fault exists" again. The fault can not be cleared remotely. Last night there was a power failure and again once power was restored a few minutes later the site has not come back up - I'm assuming same as before but can't be sure until we get out there (site is difficult to reach).

 

Several questions:

1. Can parts be bought for these UPS's - can we replace the inverter PCB? If so where can we get spare parts.

2. Can a new UPS be bought without the batteries? It seems a waste not to re-use the 6 month old batteries.

3. Is there any way in which this UPS can be set to run in bypass mode and turn on outlets on (even if an inverter fault exists) after a power outage?

4. Is this a common fault with these UPS's? Will updating the firmware help?

 

At the moment these UPS's are causing issues (turning of the equipment) more than they are preventing issues.

 

Any help appreciated.

 

Thanks.

Labels
  • Labels:
  • Datacenter UPS
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • english
  • inverter fault
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
JonPro
Commander JonPro Commander
Commander

Posted: ‎2023-01-01 05:15 PM

0 Likes
1
10154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-01 05:15 PM

Hi @Hunda67 

 

First, let me apologize for the inconvenience this has caused.   Please see my responses below.

 

1. The only user-replaceable part on the UPS is the battery.  Its internal components cannot be replaced.

2. As far as I know, the UPS cannot be purchased without a battery.

3. It would depend on the fault, since it is a logical bypass the UPS bain needs to be ON in order to command the UPS into bypass.

4. Kindly retrieve the 3-digit event code via the LCD display to determine what is the sub-system fault that it has encountered.  You may also download the NMC log files so that we can check that it reports.

 

Video: How can I download Event, Data, Configuration, and Debug files from my Network Management Car... 

Reply

Link copied. Please paste this link to share this article on your social media post.

Hunda67
Crewman Hunda67
Crewman

Posted: ‎2023-01-03 04:35 AM

In response to JonPro
0 Likes
0
10130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-03 04:35 AM

Hi. Thanks for the reply. It's a shame about not being able to buy parts or a unit without batteries.

I did not get the 3 digit event code from the LCD display, but I assume it is the same code as in the event logs which was 0x0165. As I say it has happened twice. Both times power down and then clearing the fault from the front panel solved the problem (until it happens again). I have attached the event log in case it helps further. The first time the problem occurred was 03/12/22 at 20:51hrs and then again on 23/12/22 at 17:17hrs.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2023-01-03 07:08 PM

0 Likes
6
10124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-03 07:08 PM

The 0x0165 is the event code used by the network card itself to identify the NMC event and there is a different code for the UPS itself which would tell us exactly what caused the Internal Hardware Failure.

 

Depending on the fault encountered, we could end up on clearing the fault or replacing the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Hunda67
Crewman Hunda67
Crewman

Posted: ‎2023-01-03 09:56 PM

In response to JonPro
0 Likes
5
10119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-03 09:56 PM

Aha I did not realise that. I'm guessing that the code for the UPS itself would have been displayed only on the LCD panel and now that the fault is cleared will no longer be visible? Is there any other place it would have been recorded or should I wait until the issue returns?

Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2023-01-03 10:43 PM

In response to Hunda67
0 Likes
4
10116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-03 10:43 PM

You may download the network management card debug file by following the FAQ article below or viewing the UPS event log via the LCD.

 

Video: How can I download Event, Data, Configuration, and Debug files from my Network Management Car... 

Reply

Link copied. Please paste this link to share this article on your social media post.

Hunda67
Crewman Hunda67
Crewman

Posted: ‎2023-01-04 12:30 AM

In response to JonPro
0 Likes
3
10112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-04 12:30 AM

Thanks. I can't visit the site until next week to view the LCD (remote location). However, I followed the FAQ article and have downloaded the attached files including debug.txt. Not sure what I should be looking for in these.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2023-01-04 07:59 PM

In response to Hunda67
0 Likes
2
10105
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-04 07:59 PM

Hi @Hunda67 

 

Unfortunately, the mlEvent file that would show the event code is not available and this is where I will be able to see the event code.  I also see that the UPS firmware is UPS 04.4 (ID1014) and the latest one for your UPS is UPS15.0.

 

There is no guarantee that the firmware upgrade would resolve the issue but I would put in here the FAQ article on how to update it.

 

I would also recommend that you reach out to our Local Technical Support Team to raise the issue to our UPS Team to interpret the files that you have provided.

 

How do I update the firmware of my CSH, SCL, SMC, SMT, SMTL, SMX, SRT, SRTL, XP and XU series Smart-... 

Reply

Link copied. Please paste this link to share this article on your social media post.

Hunda67
Crewman Hunda67
Crewman

Posted: ‎2023-01-05 09:27 PM

In response to JonPro
1 Like
1
10094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-05 09:27 PM

Hi, OK and thanks for your help. I will try upgrading the firmware and also raise the issue to Local Technical Support and see what happens. Thanks for all the ideas and links. I'll post back here with the outcome from Local Technical Support.

Reply

Link copied. Please paste this link to share this article on your social media post.

Hunda67
Crewman Hunda67
Crewman

Posted: ‎2023-02-07 08:47 AM

In response to Hunda67
0 Likes
0
9909
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-07 08:47 AM

Hi,

I upgraded the firmware to the latest version and also contacted Technical Support. They got me to "Brain dead" the unit (see here https://www.apc.com/uk/en/faqs/FA156611/). It has now been 3 weeks and the fault has not returned but I'm continuing to monitor it as the last time the fault appeared 3 weeks apart.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore