Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
APC USV with APC appliance
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-0606:34 AM
APC USV with APC appliance
Hello,
I have a question for the APC UPC SMX750I with Network Management Card AP9640 installed.
Our scenario:
A single ESXi 7.0 server without Vcenter connected to the APC. We have installed the APC Shutdown appliance on the ESXi server. We configure a threshold time when the APC should initiate the shutdown command for the VMs. This is working fine.
Question is:
What is needed to initiate the start command for the ESXi server from the APC when the power has been restored while APC is still on battery power?
We see it works fine when there is no power and the battery is empty, So when the power is restored the APC also initiates a power command to the ESXi server.
Like any other software application PowerChute cannot run when the OS is off, so it cannot restart the server. To allow the server to automatically restart when AC is restored configure the BIOS of the server. The BIOS should be set to Always On