Smart UPS SMT750I - failed firmware upgrade

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS SMT750I - failed firmware upgrade
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 11:04 PM . Last Modified: ‎2024-03-06 03:25 AM

0 Likes
15
11431
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:04 PM . Last Modified: ‎2024-03-06 03:25 AM

Smart UPS SMT750I - failed firmware upgrade

Hi all

Would appreciate any assistance - I have an SMT750I 230v model manufactured in 2010. It is fitted with an AP9630 NMC card.

I successfully updated the AP9630 to v6.2.1. I then attempted to update the UPS, via the NMC using file SMT17UPS_07-1_Le.enc (UPS hardware ID showed as 17). After a while the NMC log showed it had lost communication with the UPS without reporting the state of the firmware update. The UPS front panel showed 'Firmware update in progress...'. Documentation says this should complete within 10 minutes. After nearly 30 minutes I gave up on it, disconnected power and battery.

On reapplying power the UPS just gives a loud continuous tone, also makes a similar (continuous) noise to that which it briefly gives when doing a self test.

I then tried the firmware update wizard 4.1 via serial cable - this runs, identifies the correct firmware image file (as above) to apply and looks to be uploading the file OK, reaches 95% then fails reporting firmware might be missing and to try again.

Have tried several times without success - is there a way to salvage the UPS?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • beeping
  • firmware
  • network-management-card
  • smart-ups
  • smartups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:24 AM

0 Likes
1
11430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:24 AM

Hi all
Is anybody who found solution after fail upgrade firmeware by NMC tab.... I select firmware to my APC Smart UPS SMT750i file name: SMT18UPS_09-4.enc and try write it by interface web NMC by selecy firmware update. Then window still show uploading firmware. After about 20min i close web browser and then again login and NMC show lost communication with UPS....

Is any chance to recovery this UPS ?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 15
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 11:04 PM . Last Modified: ‎2024-03-06 03:25 AM

0 Likes
0
11430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:04 PM . Last Modified: ‎2024-03-06 03:25 AM

I would contact APC tech support. In my experience, this condition isn't recoverable.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:04 PM . Last Modified: ‎2024-03-06 03:25 AM

0 Likes
0
11430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:04 PM . Last Modified: ‎2024-03-06 03:25 AM

Hi Angela (& Voidstar)

Thanks for the responses, had brief look through the other thread you suggested, will see if any of those suggestions help (don't appear to have worked for the other guy, either that or he got it working and never came back!).

Thanks for the help so far.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:04 PM . Last Modified: ‎2024-03-06 03:25 AM

0 Likes
0
11430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:04 PM . Last Modified: ‎2024-03-06 03:25 AM

Looks like there's hope - can see the 'CCCCCC' response in a Putty session...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:04 PM . Last Modified: ‎2024-03-06 03:25 AM

0 Likes
0
11430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:04 PM . Last Modified: ‎2024-03-06 03:25 AM

Hi Angela

Am able to start the Xmodem file transfer but it stops at 161 or 162 packets sent. Initially used a version of Putty with file transfer ability and then found an executable for Windows Hyperterminal - both give the same result. I can't think what else I can try, any suggestions?

Thanks for your help.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:25 AM

0 Likes
0
11430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:25 AM

Hi Alan,

Sorry, we were on holiday here in the US. I am not sure what the cause would be on why it keeps stopping. You could try re-downloading the firmware file? And you said you verify the ID was 17 so you're sure you got the correct file? As far as I can tell, the SMT17UPS_07-1_Le.enc was accurate if you pushed that.

I've never done the process listed here that you tried from the other post so I can't say I've not really run into this issue.

My only other suggestion would be to try contacting your local tech support office and see if they have any other tricks up their sleeves to recover the unit. You can refer to this post and see if they can ask their escalation group for feedback.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:25 AM

0 Likes
0
11430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:25 AM

Hi Angela

Yes, I realised you were on holiday! I have tried the update from different laptops with the file downloaded separately on both an it always stops at 161 or 162 packets sent.

I did wonder if I would get a different result with an older firmware file (don't have a record of the exact version that was on it but I think it was 5) - but am unable to find anything other than the most recent one - would you be able to send me an earlier version?

When starting the xmodem upload the green online LED flashes, once it stops at 161/162 packets the amber on battery LED is lit and the two red LEDs flash together. I have tried leaving it at this stage as long as I can stand (due to the constant loud alarm tone!) - half an hour plus, in case it decides to continue the xmodem session but no luck there.

Thanks for your continued help. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:25 AM

0 Likes
0
11430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:25 AM

Hi Angela

Thanks for the file - no luck though, that one stops at 96 packets sent, tried it a few times, the behaviour of the LEDs seems to be the same for both files, green LED flashing until the the upload stalls, red wiring fault LED comes on briefly, then changes to amber LED on constant and the two red LEDs flashing together.

Maybe it's loading the initial part of the file and then failing to bootstrap off it to continue - would be nice to know what the LEDs mean!

As you suggested, I'll try talking to the local UK support guys, see if they have any suggestions - I don't think their address is too far from me, maybe I can take it to them.

Thanks for all your assistance, I might need a new UPS:(

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:25 AM

0 Likes
0
11430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:25 AM

Hi

Did you fix that PSU? I own same model and it looks like bricked, nothing except LCD backlight present. No USB communication etc - does your PC find that UPS when you plug the USB cable? Mine does not! Service from APC would be $$$ so I would like to fix that brick on my own. Maybe it is a firmware fault, like you have. But your LCD is fine, text present on the display?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:24 AM

0 Likes
0
11430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:24 AM

Hi Alan

I know it's no consolation to you, but I just did the same thing to my less-than-three year old SMT3000/AP9630 system.  If I find a way to restore mine, I'll let you know and I will be watching this thread in case you can get yours working again.

I am pretty sure that APC did not engineer in any firmware recovery mechanisms that even the most rudimentary system boards have and, as a result, I've created a very expensive and heavy boat anchor for myself.

Best of luck!

Joe 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:24 AM

0 Likes
0
11430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:24 AM

Hi, I'm afraid to report I was unable to recover the UPS - it's since been replaced. I spoke to APC support, they confirmed the unit was unrecoverable.

Your best bet is the Xmodem recovery method but if that stops like mine did I doubt you'll get much further.

LCD display was blank, there was activity with the four LEDs during the Xmodem upload attempt.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:24 AM

0 Likes
0
11430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:24 AM

Hi Alan and thanks for the status update.  I am not familiar with the Xmodem recovery method and I would appreciate you pointing me in the right direction.  My computers no longer have serial ports so I may invest in a USB serial port just to give this one last try.

Please let me know and thanks in advance!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:24 AM

0 Likes
0
11430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:24 AM

It seems I am in a very similar situation with an SMT3000i that I recently purchased second hand.

My first job was to ensure that all the firmware was up to date. I successfully updated the AP9630 NMC from (IIRC) V5.1.3 to V6.4.6 over the network then set about updating the UPS - again, over the network. I located a copy of SMT17UPS_07-1_Le.enc and tried to load it via the web interface of the NMC. The UPS was powered up but with the outputs off and no battery installed. All seemed to go fine until I got, IIRC, an error message something like "Packet Error". I tried again but immediately the UPS alarm started and there was a loud click and a hum as though the UPS was working hard. Further attempts led to the message "No UPS detected" I disconnected the supply and went hunting on the internet.

After discovering this and other threads I then purchased a DB9 to RJ45 serial cable and tried to update the UPS using the Firmware Update Wizard V4.1.1. This seemed to go okay until about 90% of file 2 when it stopped with an error.

I then tried talking to the UPS with HyperTerminal at 9600-8-N-1 and got the response:

APC(R) 2009 Download Manager

Version 07.20

4.5G Smart-UPS Tower

Then came a series of C's. I started an Xmodem transfer and this proceeded to packet 162 when it just hung. I left it for 15 minutes (with the alarm still bleating and loud humming) and then gave up and cancelled the transfer. HyperTerminal was still showing a rotating bar as though something was still happening. I powered off and on and tried again but had exactly the same outcome.

My inclination is that the UPS is actively doing something leading to the loud hum and that somehow this is disturbing the firmware upgrade. If I can disable this somehow then I might stand a better chance with the upgrade.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:24 AM

0 Likes
0
11430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:24 AM

On 6/6/2017 10:12 AM, John said:

My inclination is that the UPS is actively doing something leading to the loud hum and that somehow this is disturbing the firmware upgrade. If I can disable this somehow then I might stand a better chance with the upgrade.

The upgrade stops partway through because there are two processors: the first upgrades fine, the second is bricked.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:24 AM

0 Likes
1
11431
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:05 PM . Last Modified: ‎2024-03-06 03:24 AM

Hi all
Is anybody who found solution after fail upgrade firmeware by NMC tab.... I select firmware to my APC Smart UPS SMT750i file name: SMT18UPS_09-4.enc and try write it by interface web NMC by selecy firmware update. Then window still show uploading firmware. After about 20min i close web browser and then again login and NMC show lost communication with UPS....

Is any chance to recovery this UPS ?

Reply

Link copied. Please paste this link to share this article on your social media post.

abrarahmad000
abrarahmad000
Cadet

Posted: ‎2022-07-05 02:34 AM

In response to Anonymous user
0 Likes
0
10031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-05 02:34 AM

Facing exactly same issue. UPS (SMT750i) gives blank LCD with a continuous beep. Cause of this problem is Unexpected Power Loss wile upgrading firmware.

Firmware Upgrade Wizard Stops at 12% while sending part 2 of file 1.

Hyperterminal/TeraTerminal 9600 BAUD Also stucks at 162 Packets/12%.

I also tried directly connecting to console at 2400 Baud via TTL port pins (J106 Jack) on the Board near EMMC (Like we used to do for setting constants). Its giving no response, but when transfer stucks at 162 packets, it shows YYYYYY..... in terminal. I tried sending file from there too, but it failed too at 0% (probably bcoz CPU was not requesting for file)

 

Anyone found solution for it?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore