Smart-UPS RT 8000XLi

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 8000XLi
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
avago_apc
Crewman avago_apc
Crewman

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:20 PM

0 Likes
4
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:20 PM

Smart-UPS RT 8000XLi

Hi

  We have just installed a new UPS running on 3phase, In the instruction manual its not very clear as to which way the rocker switch should be ( page 3 of the manual ) I have put an amp-clamp on each phase at the distrubution board L1 = 2.6A  L2=3.4A  L3=3.4A. Looking at the information it indicates that it will draw 15A/phase and when in bypass 40A on L1.. If you look at the web base management page it show the input voltage as 240v Shouldn't this be 400/415V with the outpot as being 230/240v.

We have via the web page put the UPS in to bypass but this seems to have no affect on L1 .  I would have expected that all L1/L2/L3 should all be pulling the same ?

Any advice Please

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • config
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:20 PM

0 Likes
0
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:20 PM

Some more feedback:

If you need full 3ph functionality, you would need a 3ph in 3 ph out UPS. This unit offers 3ph in 1 ph out as an added feature, but it is primarily a 1ph device and monitors power as such.

It may not allow it in 3ph mode so you don't accidentally enable it and overload ph1

Beyond that, I'd have to recommend you contact your local support for further details or feedback because we do not have this unit in North America so some of the answers are difficult to provide.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:20 PM

0 Likes
0
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:20 PM

For this unit, if you want to feed it 3 phase voltage, the switch should be on 3. The phase draw will not be perfectly balanced and in bypass, all of the load will be pulled on L1. So, we believe what you're seeing is normal for this model of UPS. I don't have this available to set up so I can speak too much to the web interface information you're seeing as it may only show one of the phases.

Reply

Link copied. Please paste this link to share this article on your social media post.

avago_apc
Crewman avago_apc
Crewman

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:20 PM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:20 PM

Thanks for the reply, I guessed that it need to be on 3 to get the 3phase in, I'm suprised that they have no indiaction on the front or via the web monitoring that shows you are running on 3PH, If you were to loose a phase would you know, other that having a current / CT dispay on the dist board, The web monitoring should show the input supply as 400/414V not 230/240v as this would indicate single phase. Also noticed that if you try and put the UPS is bypass via the Web Gui it doen't work, If you do it on the UPs via the rocker switch it does and they L1's Amps start to rise as you would expect.

maybe some for the R&D bods to look at ?

smile

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:20 PM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:20 PM

I will forward your comments appropriately since I am flying blind on this one! 😉

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:20 PM

0 Likes
0
988
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:36 AM . Last Modified: ‎2024-03-12 11:20 PM

Some more feedback:

If you need full 3ph functionality, you would need a 3ph in 3 ph out UPS. This unit offers 3ph in 1 ph out as an added feature, but it is primarily a 1ph device and monitors power as such.

It may not allow it in 3ph mode so you don't accidentally enable it and overload ph1

Beyond that, I'd have to recommend you contact your local support for further details or feedback because we do not have this unit in North America so some of the answers are difficult to provide.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of