We have two Smart-UPS RT 8000 RM XL that are both giving the following alarms.
Replacement Battery Needed |
At least one faulty battery exists. |
Self-Test Failed |
Self-Test Failed |
What are the chances that both need to have batteries replaced? Batteries are only about one year old..
Thanks
Tom
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 03:19 AM . Last Modified: 2024-03-05 10:55 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 03:19 AM . Last Modified: 2024-03-05 10:55 PM
Did you program each UPS with the # of external battery modules? I assumed these where internal batteries because they are in the UPS if that is incorrect, than it was not done and I would need to know how to do that.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 03:19 AM . Last Modified: 2024-03-05 10:56 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 03:19 AM . Last Modified: 2024-03-05 10:56 PM
Each UPS has 4 batteries, Current room temps for one ups is 84.99 F the other is 78.87 F. I don't think a battery calibration has ever been done under a load.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 03:19 AM . Last Modified: 2024-03-05 10:55 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 03:19 AM . Last Modified: 2024-03-05 10:55 PM
Did you program each UPS with the # of external battery modules? I assumed these where internal batteries because they are in the UPS if that is incorrect, than it was not done and I would need to know how to do that.