Smart-UPS RT 7500 XL - 100% capacity, discharged

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 7500 XL - 100% capacity, discharged
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:17 PM . Last Modified: ‎2024-03-12 12:57 AM

0 Likes
3
1292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:17 PM . Last Modified: ‎2024-03-12 12:57 AM

Smart-UPS RT 7500 XL - 100% capacity, discharged

Hello,

we recently replaced all batteries from our Smart-UPS RT 7500 XL. After that the APC network management card reports: Discharged, No Other Alarms Present

After that we let it untouched for a week and then ran a selftest, but the status remained unchanged.

UPS status

Discharged, No Other Alarms Present

Batteries discharged.

Reason For Last Transfer To Battery:  Due to software command or UPS's test control.

Internal Temperature:  031.9 °C

Runtime:  17 minutes

Battery status 

Battery Capacity:  100.0  %

Battery Voltage:  216.0  VDC

Number of  External  Batteries:   001

Self-Test Result:  Passed

Self-Test Date:  01/08/2014

Calibration Result:  Unknown

Calibration Date:  Unknown

The battery date is 09/2013

Eventlog:

01/08/2014 23:37:01 UPS: Passed internal self-test.

01/08/2014 23:36:56 UPS: Returned from a Low-Battery condition.

01/08/2014 23:36:56 UPS: Batteries discharged.

01/08/2014 23:36:46 UPS: Battery power is low and will soon be exhausted.

01/08/2014 23:36:46 UPS: Battery discharge condition cleared.

After the self-test the battery capacity dropped to 96%, which looks quite normal to me. Also, an available runtime of 17 minutes looks promising.

On the frontpanel, all leds are showing normal operation. Load is 60%.

So why is the management card showing a discharged battery state?

I read that it may have to do something with a battery constant which could be reset by doing a runtime test, which unfortunately isn't possible in this productive state.

Any suggestions?

Thank you in advance.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:17 PM . Last Modified: ‎2024-03-12 12:57 AM

0 Likes
0
1291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:17 PM . Last Modified: ‎2024-03-12 12:57 AM

You're welcome - so yes, that was the issue. If the UPS runtime remaining is within two minutes of that low battery duration value, you'll see this as well as a flashing battery bar graph on the front of the UPS.

It's trying to tell you "hey, you want me to signal things to shut down (if configured) when 20 minutes remains (maybe to allow a safe shutdown) but I only have 17 minutes left!!" Thus, you may want to check into why this was set to 20 minutes in the first place. The default setting is 2 minutes.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:17 PM . Last Modified: ‎2024-03-12 12:57 AM

0 Likes
0
1291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:17 PM . Last Modified: ‎2024-03-12 12:57 AM

Hello,

we recently replaced all batteries from our Smart-UPS RT 7500 XL. After that the APC network management card reports: Discharged, No Other Alarms Present

After that we let it untouched for a week and then ran a selftest, but the status remained unchanged.

UPS status

Discharged, No Other Alarms Present

Batteries discharged.

Reason For Last Transfer To Battery:  Due to software command or UPS's test control.

Internal Temperature:  031.9 °C

Runtime:  17 minutes

Battery status 

Battery Capacity:  100.0  %

Battery Voltage:  216.0  VDC

Number of  External  Batteries:   001

Self-Test Result:  Passed

Self-Test Date:  01/08/2014

Calibration Result:  Unknown

Calibration Date:  Unknown

The battery date is 09/2013

Eventlog:

01/08/2014 23:37:01 UPS: Passed internal self-test.

01/08/2014 23:36:56 UPS: Returned from a Low-Battery condition.

01/08/2014 23:36:56 UPS: Batteries discharged.

01/08/2014 23:36:46 UPS: Battery power is low and will soon be exhausted.

01/08/2014 23:36:46 UPS: Battery discharge condition cleared.

After the self-test the battery capacity dropped to 96%, which looks quite normal to me. Also, an available runtime of 17 minutes looks promising.

On the frontpanel, all leds are showing normal operation. Load is 60%.

So why is the management card showing a discharged battery state?

I read that it may have to do something with a battery constant which could be reset by doing a runtime test, which unfortunately isn't possible in this productive state.

Any suggestions?

Thank you in advance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:17 PM . Last Modified: ‎2024-03-12 12:57 AM

0 Likes
0
1291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:17 PM . Last Modified: ‎2024-03-12 12:57 AM

Hello Angela,

it was set to 20 minutes. Changing it to 15 minutes cleared the error state.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:17 PM . Last Modified: ‎2024-03-12 12:57 AM

0 Likes
0
1292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:17 PM . Last Modified: ‎2024-03-12 12:57 AM

You're welcome - so yes, that was the issue. If the UPS runtime remaining is within two minutes of that low battery duration value, you'll see this as well as a flashing battery bar graph on the front of the UPS.

It's trying to tell you "hey, you want me to signal things to shut down (if configured) when 20 minutes remains (maybe to allow a safe shutdown) but I only have 17 minutes left!!" Thus, you may want to check into why this was set to 20 minutes in the first place. The default setting is 2 minutes.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore