Smart-UPS RT 6000 RM XL - in bypass in response to an internal hardware fault
  • Smart-UPS RT 6000 RM XL - in bypass in response to an internal hardware fault
5060
142
Posted: ‎2021-06-30 11:56 PM . Last Modified: ‎2024-03-06 03:07 AM
1164
We have a rack-mounted UPS, model number :
APC | UPS Network Management Card 2
Model: Smart-UPS RT 6000 RM XL
Position: RACK
Serial Number: IS1131001323
Firmware Revision: 452.18.W
Manufacture Date: 07/26/11
We receive the following alarms, as viewed from the browser:
Inverter Fault
In Bypass: Hardware Fault
and the battery bar graph display a particular pattern:
1
    Bypass LED is amber
    Fault LED is red
Do I need to replace the Battery?
Thank You.
Thank you..
Mostafa,
The inverter is an internal component of the UPS that is non-user replaceable.  I highly recommend calling in to local support for assistance or running the "braindead" procedure (this procedure can be found in other forum posts).  If a braindead does not clear the fault, the UPS would need to be replaced as the inverter is critical to UPS function.