Smart-UPS RT 5000 battery calibration question

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
ABaciu_apc
Crewman
Crewman
0 Likes
6
391

Smart-UPS RT 5000 battery calibration question

This was originally posted on APC forums on 11/7/2016


 Hello, I have a Smart-UPS RT 5000 model and I'm trying to run a battery calibration on it. The question is that during this process the load (which consists of server and other network equipment) will be shut down ?


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
391

Re: Smart-UPS RT 5000 battery calibration question

This reply was originally posted by Jonathan on APC forums on 11/7/2016


Hello Andrei,

There are two types of calibrations - Manual and User Commanded and depending on the method that you will use, there is a possibility of load drop.

User Commanded:

  • This is the preferred method for all Smart-UPS except for models beginning with SU (IE: SU700NET). 
  • Calibration is initiated from Power Chute Business Edition, the Network Management Card, or the LCD Screen of the UPS (if so equipped).
  • Ensure that the normal load is attached
  • Ensure Battery is charged to 100% before beginning Calibration
  • Load should be more than 30% for best results
  • UPS will drain the battery, then switch back online and charge back up
  • Calibration must not be interrupted to deliver valid results

 

Manual Calibration:
  • This is the preferred method for "SU" series Smart-UPS, or any time that a User Commanded Calibration is not possible
  • Stop the Power Chute software from running and disconnect the serial, USB, or Ethernet cable(s).
  • There must be at least a 30% load attached to the UPS during this procedure, and this load cannot fluctuate more than +/- 5%. THIS IS IMPORTANT
  • Attach a non-critical load to the UPS and then force the UPS on battery by disconnecting it from utility power
  • Allow the unit to run on battery until it turns off completely. The load attached to the UPS will drop.
  • If the Load is not at least 30% or if the calibration is ended before the UPS drops the load, the calibration will not work.
  • Plug the UPS back into the wall outlet and allow it to recharge (preferably turned off)

See Answer In Context

6 Replies 6
BillP
Administrator Administrator
Administrator
0 Likes
0
392

Re: Smart-UPS RT 5000 battery calibration question

This reply was originally posted by Jonathan on APC forums on 11/7/2016


Hello Andrei,

There are two types of calibrations - Manual and User Commanded and depending on the method that you will use, there is a possibility of load drop.

User Commanded:

  • This is the preferred method for all Smart-UPS except for models beginning with SU (IE: SU700NET). 
  • Calibration is initiated from Power Chute Business Edition, the Network Management Card, or the LCD Screen of the UPS (if so equipped).
  • Ensure that the normal load is attached
  • Ensure Battery is charged to 100% before beginning Calibration
  • Load should be more than 30% for best results
  • UPS will drain the battery, then switch back online and charge back up
  • Calibration must not be interrupted to deliver valid results

 

Manual Calibration:
  • This is the preferred method for "SU" series Smart-UPS, or any time that a User Commanded Calibration is not possible
  • Stop the Power Chute software from running and disconnect the serial, USB, or Ethernet cable(s).
  • There must be at least a 30% load attached to the UPS during this procedure, and this load cannot fluctuate more than +/- 5%. THIS IS IMPORTANT
  • Attach a non-critical load to the UPS and then force the UPS on battery by disconnecting it from utility power
  • Allow the unit to run on battery until it turns off completely. The load attached to the UPS will drop.
  • If the Load is not at least 30% or if the calibration is ended before the UPS drops the load, the calibration will not work.
  • Plug the UPS back into the wall outlet and allow it to recharge (preferably turned off)
ABaciu_apc
Crewman
Crewman
0 Likes
0
393

Re: Smart-UPS RT 5000 battery calibration question

This was originally posted on APC forums on 11/8/2016


Thank you for the answer...so If I understood correctly If I initiate the calibration procedure from the web interface (method 1 ) it won't have any load drop ?

BillP
Administrator Administrator
Administrator
0 Likes
0
393

Re: Smart-UPS RT 5000 battery calibration question

This reply was originally posted by Jonathan on APC forums on 11/8/2016


That is correct Andrei.

ABaciu_apc
Crewman
Crewman
0 Likes
0
393

Re: Smart-UPS RT 5000 battery calibration question

This was originally posted on APC forums on 11/8/2016


Thank you for information Jonathan!

Gerard_apc
Ensign
Ensign
0 Likes
0
394

Re: Smart-UPS RT 5000 battery calibration question

This was originally posted on APC forums on 11/10/2016


Sir my question is not about calibration.. My question is up to how many battery packs can a Smart UPS SRT5000KXLI can support? Because i installed 2 battery packs already and on the third battery pack when I plugged the third battery pack it gives me an error of over voltage or something. Also if I update the firmware of UPS will it give the setting that i can install/mount more battery packs? Coz in the product manual i have read that it can support up to 10 battery packs.. Thank you sir..

Gerard

BillP
Administrator Administrator
Administrator
0 Likes
0
394

Re: Smart-UPS RT 5000 battery calibration question

This reply was originally posted by George on APC forums on 7/26/2018


I have 8 battery packs running on a similar model UPS. I'm thinking if you received an overvoltage??? that to me would indicate a voltage problem in that particular battery pack, maybe something is not wired correctly, usually you have about 52 volts DC from each group o4 4 batteries, 4 * 13 = 52 volts and each deck has 2 sets of those batteries. Im thinking I would measure the voltage on that one deck. Batteries would not otherwise be overvoltage unless maybe hooked up wrong internally?