Smart-UPS: Battery too low alert spamming

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS: Battery too low alert spamming
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

0 Likes
5
2660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

Smart-UPS: Battery too low alert spamming

I have multiple Smart-UPS Rack Mounted units and I have had the same problem with them. I will use one of them in this example.

Smart-UPS 3000 RM:

The battery is 100% charged and the load is 43%. The battery run time says 4 minutes available. The unit is spamming the following two emails:

UPS: The Battery Power is too low to support the load...

UPS: A discharged battery condition no longer exists.

The unit is right on the edge and so the condition arises and then clears. It has sent out over 100 emails already. How do I stop this unit from spewing emails? I don't want to "turn them off" because I want the notifications when they are true. Can I adjust the set point for when this alert triggers?

Regards,

J

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:09 PM

0 Likes
0
2660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:09 PM

Hi again,

To begin, AP9617 is discontinued so no updates will be done to this card. Any updates would be applied to AP9630/31 these days but they pretty much work the same way in this department as the AP9617 you have.

With that said, we're going to have to work with what we have on that screen. Perhaps you could delay the notification and see how that works? There should be an option on that screen to delay it for X seconds and you can also maybe adjust the repeat option to see what works. The only other thing would be to disable it completely.

You could also go to that page and use the Hex code for the clearing event (No longer discharged) to disable that from coming which doing that is outlined here in a different example -> Configuring clearing events with APC Network Management Cards | FAQs | Schneider Electric US

This would be one less email.. undecided

Lastly, any change you make to this event could be cascaded out to multiple cards using the config.ini. You can put a text file together for the configurations of just these events and push them out to multiple cards.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:10 PM

0 Likes
0
2660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:10 PM

I have multiple Smart-UPS Rack Mounted units and I have had the same problem with them. I will use one of them in this example.

Smart-UPS 3000 RM:

The battery is 100% charged and the load is 43%. The battery run time says 4 minutes available. The unit is spamming the following two emails:

UPS: The Battery Power is too low to support the load...

UPS: A discharged battery condition no longer exists.

The unit is right on the edge and so the condition arises and then clears. It has sent out over 100 emails already. How do I stop this unit from spewing emails? I don't want to "turn them off" because I want the notifications when they are true. Can I adjust the set point for when this alert triggers?

Regards,

J

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:10 PM

0 Likes
0
2660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:10 PM

Your runtime is low and must be teetering within 2 minutes of your low battery signal time (which is by default 2 minutes). So when your runtime is 2 or 3 minutes, you're getting this message and when it jumps to 5 based on load fluctuations, you probably get the "discharged battery condition no longer exists." This is usually indicative of older batteries.

Anyway, to configure the alerts, I need to know what model management card you have and the firmware version. This is available via the web interface.

Thanks.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:10 PM

0 Likes
0
2660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:10 PM

Yup!

Go to Administration->Notification and then for this particular event, click on By Event on the left had side under Event Actions. You're going to want to click on Power Events and then they you'll see this event bugging you on the list. Click on it and adjust notification preferences accordingly.

Let me know if you have any trouble with that or have further questions.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:09 PM

0 Likes
0
2660
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:09 PM

Angela,

Thanks for the fast response however my question still remains unanswered.

I know how to go into the settings and adjust them. Currently the settings are as follows:

Repeat interval: 2 Minutes

Repeat Times: 4

This is my standard setting. The problem is, no matter which setting I adjust the issue keeps clearing and returning so I will keep getting spammed by the email. Is there a way to suppress notifications for X amount of time to avoid getting repeat emails every few minutes in this situation?

I realize the fix in this situation is that the battery needs to be replaced however that isn't possible in the near future. And I would like to keep the notification at least once every day/week or so and not have to turn off the notification entirely. Maybe a product feature update?

Considering I have 90+ units, it isn't feasible for me to cost out a new battery for all the units at this time. Or remember the settings of each unit. So I want to maximize my ride through capability for as long as that battery will last. Run to Fail... 

I anticipate a "not possible" response but I wanted to see if there was something I had not thought of. So if that is the case just let me know.

Regards,

J

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:09 PM

0 Likes
0
2661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:41 AM . Last Modified: ‎2024-03-12 11:09 PM

Hi again,

To begin, AP9617 is discontinued so no updates will be done to this card. Any updates would be applied to AP9630/31 these days but they pretty much work the same way in this department as the AP9617 you have.

With that said, we're going to have to work with what we have on that screen. Perhaps you could delay the notification and see how that works? There should be an option on that screen to delay it for X seconds and you can also maybe adjust the repeat option to see what works. The only other thing would be to disable it completely.

You could also go to that page and use the Hex code for the clearing event (No longer discharged) to disable that from coming which doing that is outlined here in a different example -> Configuring clearing events with APC Network Management Cards | FAQs | Schneider Electric US

This would be one less email.. undecided

Lastly, any change you make to this event could be cascaded out to multiple cards using the config.ini. You can put a text file together for the configurations of just these events and push them out to multiple cards.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of