Matrix 5000 Smartcell (not XR) one cell smells, is hot, and has deformed batteries!!

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Matrix 5000 Smartcell (not XR) one cell smells, is hot, and has deformed batteries!!
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

0 Likes
9
1600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

Matrix 5000 Smartcell (not XR) one cell smells, is hot, and has deformed batteries!!

I entered the server room today to find that one of the smartcells in my Matrix 5000 smells, is hot, and has deformed batteries!!

It was the last cell in the series.

I quickly placed ups in bypass, and removed the cell, then placed the unit back online.

BOTH smartcells were professionally rebuilt and factory reset, and had been fine since then, but in the last 48 hours, this happened.

Anyone ever heard of this?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

0 Likes
0
1600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

I forgot - is this a SMARTCELL or SMARTCELL-XR? SMARTCELLs are not supposed to be opened up and repaired so if that's the case then cry

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

0 Likes
0
1600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

I entered the server room today to find that one of the smartcells in my Matrix 5000 smells, is hot, and has deformed batteries!!

It was the last cell in the series.

I quickly placed ups in bypass, and removed the cell, then placed the unit back online.

BOTH smartcells were professionally rebuilt and factory reset, and had been fine since then, but in the last 48 hours, this happened.

Anyone ever heard of this?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

0 Likes
0
1600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

Where were these batteries from? It sounds like batteries from the vendor that rebuilt and reset the unit?

You could have measured the voltage on this SmartCell or it could have just been a bad cell. I was thinking potentially a charger issue so if the voltage was super high, then that would be a concern or the bad cell depending on the quality of the battery itself.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

0 Likes
0
1600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

The batteries were from BatteriesPlus and the brand is "Werker".

Two cells were rebuilt at the same time, and these two were the only two attached to the unit.

Only one of the cells had the problem and it was the last one in the series.

The other is fine.

This APC unit is the same one that had the problem listed in the following post:

Matrix 5000 faulty battery alert comes and goes constantly in new smartcell.

According to the  logs, the unit started to alert that looked like this:

08/18/2013 16:01:12 UPS: An external battery pack was installed.
08/18/2013 16:00:57 UPS: An external battery pack was removed..
08/18/2013 16:00:10 UPS: Restored communication with the battery packs.
08/18/2013 15:59:40 UPS: Lost communication with the battery packs.
08/18/2013 15:58:38 UPS: An external battery pack was installed.
08/18/2013 15:58:23 UPS: An external battery pack was removed..
08/18/2013 15:57:37 UPS: Restored communication with the battery packs.
08/18/2013 15:57:06 UPS: Lost communication with the battery packs.
08/18/2013 15:55:49 UPS: Restored communication with the battery packs.
08/18/2013 15:55:34 UPS: Lost communication with the battery packs.
08/18/2013 15:55:03 UPS: An external battery pack was installed.
08/18/2013 15:54:48 UPS: An external battery pack was removed..
08/18/2013 15:53:00 UPS: Restored communication with the battery packs.
08/18/2013 15:52:45 UPS: Lost communication with the battery packs.
08/18/2013 15:51:59 UPS: Restored communication with the battery packs.

Just horrible crap happening to this cell for some reason.

Any thoughts are appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

0 Likes
0
1600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

Those types of alarms could occur with low battery voltage. If there was a bad cell, it could've dipped.

If you just have the "good" Smartcell connected, do you see this type of behavior?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

0 Likes
0
1600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

Correct, everything is working as expected/is normal with the remaining smart smartcell connected.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

0 Likes
0
1600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

That's right, as I first stated, this is not an XR unit.  I know they are not supposed to be rebuilt. but never had this issue after having done several of these.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

0 Likes
0
1600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

OK - missed that in the title. Or maybe I remembered but someone else asked me and I forgot embarassed

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

0 Likes
0
1600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

Is that SmartCell that was just re-worked under warranty? Beyond checking the charging voltage to make sure the UPS did not damage good batteries, not much we can do as far as I know.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

0 Likes
0
1601
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:40 AM . Last Modified: ‎2024-03-12 11:10 PM

I forgot - is this a SMARTCELL or SMARTCELL-XR? SMARTCELLs are not supposed to be opened up and repaired so if that's the case then cry

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore