Smart UPS AVR boost/trim thresholds.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS AVR boost/trim thresholds.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:47 PM . Last Modified: ‎2024-03-01 12:25 AM

0 Likes
6
5021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:47 PM . Last Modified: ‎2024-03-01 12:25 AM

Smart UPS AVR boost/trim thresholds.

Hello.
The question is - what is voltage levels thresholds for switch to AVR trim/boost and swithc back to live?
Thank You.


 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-07 10:48 PM . Last Modified: ‎2024-03-01 12:25 AM

0 Likes
0
5019
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:48 PM . Last Modified: ‎2024-03-01 12:25 AM

Amount of boost or trim depends on the UPS model, which is why Jonathan asked. Lets assume 12%. V_in = Line Voltage RMS; hyst = hysteresis; => means implication. Treatment of hysteresis is for example only and may be different on an actual UPS.

V_in < Lower Transfer Point/(1+0.12)+hyst => UPS is on battery

Lower Transfer Point/(1+0.12)-hyst < V_in < Lower Transfer Point+hyst => UPS in boost

Lower Transfer Point-hyst < V_in < Upper Transfer Point+hyst => UPS normal

Upper Transfer Point-hyst < V_in < Upper Transfer Point/(1-0.12)+hyst => UPS in trim

Upper Transfer Point/(1-0.12)-hyst < V_in => UPS on battery

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:47 PM . Last Modified: ‎2024-03-01 12:25 AM

0 Likes
0
5020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:47 PM . Last Modified: ‎2024-03-01 12:25 AM

Hello Vladimir -

May I please know that model number of the UPS that you have? It can be found on the white barcode sticker attached on the back of your UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:47 PM . Last Modified: ‎2024-03-01 12:25 AM

0 Likes
0
5020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:47 PM . Last Modified: ‎2024-03-01 12:25 AM

This is the common question, based on suppose that AVR is boosting, for example, if input is "Rated Output Voltage"-5% and higher than "Low Transfer Voltage", and trimming if input is (Rated Output Voltage)+5% and lower than "High Transfer Voltage".

I have number of different Smart UPS, from SURT10000 to SMT750.

Thank You.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:47 PM . Last Modified: ‎2024-03-01 12:25 AM

0 Likes
0
5020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:47 PM . Last Modified: ‎2024-03-01 12:25 AM

Generally AVR has a +/- 12% range in the Smart UPS, unless your unit features double boost.  This is not true for the SURT series units as they are Online units rather than Line Interactive.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:47 PM . Last Modified: ‎2024-03-01 12:25 AM

0 Likes
0
5020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:47 PM . Last Modified: ‎2024-03-01 12:25 AM

So, if the output voltage is set to 230 VAC, boost will be activated at point 230-12%(230)=202.4 VAC, trim will be activated at point 230+12%(230)=257.6.
I suppose i misunderstood You.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:48 PM . Last Modified: ‎2024-03-01 12:25 AM

0 Likes
0
5020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:48 PM . Last Modified: ‎2024-03-01 12:25 AM

Sorry my carelessness, from the build-in NMC help:

High Transfer Voltage
The upper limit of acceptable input voltage. When the input reaches this value, the UPS starts to use its AVR Trim feature.
Low Transfer Voltage
The lower limit of acceptable input voltage. When the input reaches this value, the UPS starts to use its AVR Boost feature or switches to battery operation if it does not have this feature.
 
Okay, AVR boost/trim points may be specified obviously, how determine points of switching from AVR to battery.

Thank You.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-07 10:48 PM . Last Modified: ‎2024-03-01 12:25 AM

0 Likes
0
5020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:48 PM . Last Modified: ‎2024-03-01 12:25 AM

Amount of boost or trim depends on the UPS model, which is why Jonathan asked. Lets assume 12%. V_in = Line Voltage RMS; hyst = hysteresis; => means implication. Treatment of hysteresis is for example only and may be different on an actual UPS.

V_in < Lower Transfer Point/(1+0.12)+hyst => UPS is on battery

Lower Transfer Point/(1+0.12)-hyst < V_in < Lower Transfer Point+hyst => UPS in boost

Lower Transfer Point-hyst < V_in < Upper Transfer Point+hyst => UPS normal

Upper Transfer Point-hyst < V_in < Upper Transfer Point/(1-0.12)+hyst => UPS in trim

Upper Transfer Point/(1-0.12)-hyst < V_in => UPS on battery

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore