Smart-UPS & AP9630

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS & AP9630
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:57 AM . Last Modified: ‎2024-03-13 04:30 AM

0 Likes
8
1922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:57 AM . Last Modified: ‎2024-03-13 04:30 AM

Smart-UPS & AP9630

Trying to connect to the management card by I always get this error now: This object on the APC Management Web Server is protected.

Have tried /logout.htm but I still get the same error.

What does pressing on the "reset" button on the Management Card?  from what I saw it keeps the same IP and security settings so it's kind of useless.

Smart-UPS 1500

aos f/w rev: apc_hw05_aos_513

app f/w rev: apc_hw05_sumx_513

Any ideas??? I also need to replace the battery, we had a lot out power outages lately..

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:29 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:29 AM

Thank you Angela, will give it a try this evening as I am currently at a client site.

Cheers!

Luis

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:30 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:30 AM

Hey Luis,

The reset button just reboots the card.

That message is generally because the card has TLS enabled for the web. Try adding https:// in front of your IP address to access the card. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:29 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:29 AM

Hi David, I tried that since I'm the one securing my severs, firewalls and web services.

Still, nothing works in order to fully reset that card as I can't even get to the login screen.

cheers!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:29 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:29 AM

hold the reset in for more than 20 seconds, the green flashing light will turn to an orange flashing light to say the card has been formatted. You may need the device IP configuration app to find it on the network again unless your router has a fixed IP set.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:29 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:29 AM

Hi Gareth,

will give it a try.

will post my results afterwards.

regards.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:29 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:29 AM

Just a disclaimer. Format function, while one of my favorite things to try when starting over, will erase ALL settings and configuration on the NMC. I am not sure if that was clear already.

The original issue could've been that someone changed the default HTTPS port to something different as well which is another security option the NMC offers.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:29 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:29 AM

Hi Angela,

But how to clear all settings from the AP6930 without even been able to remotely log into it?

Is it by pressing the Reset button for 20 seconds or more??

Regards,

Luis

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:29 AM

0 Likes
0
1921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:29 AM

Yes, that's right - press and hold the reset button for 20 seconds. It will "pulse" green and then change to orange when you can let go. If it does not do this, then the action won't complete so just make sure you hold it steady and long enough. We call this sequence a "format" and I just wanted to clearly explain it will clear ALL settings and it resets everything. You'll have to reconfigure from scratch. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:29 AM

0 Likes
0
1922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:58 AM . Last Modified: ‎2024-03-13 04:29 AM

Thank you Angela, will give it a try this evening as I am currently at a client site.

Cheers!

Luis

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore