Smart UPS 750 (LCD Display) almost blew up

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 750 (LCD Display) almost blew up
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:09 AM . Last Modified: ‎2024-03-07 03:28 AM

0 Likes
3
1593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:09 AM . Last Modified: ‎2024-03-07 03:28 AM

Smart UPS 750 (LCD Display) almost blew up

Hi there,

I have two Smart UPS 750 in use (the newer LCD version) + a UPS 5k RM also with a display.

Last week one of the Smart UPS 750 devices started smelling burned and when I located where the smell came from, I noticed that the case had at least about 70 or 80 degree (far beyond being able to touch it, so measured it with an IR thermometer). I disconnected everything, including the battery connector and the batteries + the unit took several hours too cool down. Also, the fuse in the house which served the UPS blew.

The batteries were bulged and the battery cases started to crack.

The red battery light turned on one or two days ago. I know that the batteries CAN expand but I've only experienced that when ignoring the red battery light for an extended period of time.

The UPS and battery is quite some years old but I never worried about the battery because it worked just fine, had its specified battery holding time and the battery replacement light wasn't on until a few days ago.

So my question: although the device isn't most certainly under warranty anymore: Is this supposed to happen? I mean if I weren't there, the UPS might have burned the house down if the fuse in the house didn't blew. Shouldn't a UPS protect against power outages, not producing them?

Can I just put new batteries in (the defective ones were genuine APC batteries!) or do I have to replace to unit? Is there some kind of compensation from APC? I mean, batteries shouldn't just heat up like this and burn your house down, isn't that clearly a quality issue? If the light would have come on earlier, I would have replaced the batteries in time and I guess none of those things would have happened.

Thanks.

BR

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:10 AM . Last Modified: ‎2024-03-07 03:27 AM

0 Likes
0
1593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:10 AM . Last Modified: ‎2024-03-07 03:27 AM

Batteries eventually will fail no matter who manufactured them (CSB batteries are high quality by the way, I have several 12V 17Ah GP series batteries which are over 18(!) years old and still retain around 40% capacity). How and when they fail is very much dependent on the operating temperature, charging voltage and number / frequency / depth of discharge cycles. These parameters are essential and usually specified by the manufacturer. Batteries in smaller APC units like the the 750VA version have to endure elevated temperatures due to the small space shared with heat generating components like the MOSFETs and the transformer. Most SLA batteries are rated for operating temperatures between 20-25 degrees celsius, each degree above that temperature shortens useful battery life by a certain amount. Therefore it is very important to operate the UPS in a cool environment, because the internal heat generating components are going to heat up the batteries well above the room's ambient temperature anyway. Though I have never owned an SMT750 LCD ups, I do know that the previous generation (SUA750) ups had temperature compensated battery charger. The problem is that all SUA750 units I have seen, have their float voltage set too high for such a small UPS size (27.5 volts), so even with the help of temperature compensated charger it cannot reach the optimal life span of the batteries. Eg. when room temperature is 20 degrees celsius, batteries are sitting at 30-32 degrees celsius inside the UPS case. For such temperatures, float charge should be reduced to 26.8-27.0 volts at maximum for optimal battery life, which is not done in these UPSes. 27.5 volts would be perfectly fine if the batteries were sitting at 20-25 celsius.

If you are not someone who is really technically knowledgeable about these devices, the best you can do is to observe the normal operating temperature of the ups, and check it regularly. If it starts to elevate for seemingly no reason while the ambient temperature stays the same, it is very likely that the batteries are going bad and the UPS has not yet had the chance to detect the problem by itself. If you don't want to bother with this, you can just replace the batteries every 2-3 years, preventing the problem altogether.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:09 AM . Last Modified: ‎2024-03-07 03:28 AM

0 Likes
0
1593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:09 AM . Last Modified: ‎2024-03-07 03:28 AM

Hi Lu - 

Batteries can expand when they experience a thermal runaway event. I certainly understand why you would be alarmed by this experience. This can be caused by operating in an overly warm environment, not replacing bad batteries promptly, or using very old batteries. Typical battery life is 3-5 years is a good environment ( 20-25°C). Swollen or venting batteries can be very concerning, but are not a fire hazard. In very extreme situations you could find some small leakage of electrolyte. You can find the battery safety datasheets here: http://www.apc.com/us/en/who-we-are/sustainability/battery-safety/battery-compliance.jsp 

In reading your post, I'm having a hard time understanding the exact sequence of events you experienced. Was the replace battery light already on when you found that the batteries had swollen? If so, how long had it been illuminated for? Are you saying that the UPS tripped the input breaker in your house? if so, at what point did that happen? You mentioned burning - was there any visible flame or smoke?

Given that you have safety concerns, it might be most effective if you contact your local support team directly for assistance rather than the forum. They will be able to answer your questions more quickly and effectively. It will be helpful to have the exact model and serial number of your UPS handy, as well as whether or not the battery was the original battery or a replacement. You can find your local contact information here: http://www.apc.com/us/en/support/contact-us/index.jsp

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-30 08:10 AM . Last Modified: ‎2024-03-07 03:27 AM

0 Likes
0
1593
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:10 AM . Last Modified: ‎2024-03-07 03:27 AM

I'm just another customer, so treat my advice accordingly.

A number of things combine to make this sort of thing more common than we'd like:

  • The manufacturers of the batteries (like CSB, etc. - not APC) operate on pretty thin margins and have a lot of competition. So their products are engineered down to a price point - it is hard to find a "premium grade" battery.
  • APC UPS charging voltages tend to drift out-of-spec over long periods of time. This almost always (due to circuit design reasons too complex to go into here) is a drift to a higher voltage. That shortens the life of the batteries. My experience is that you'll get 3 years out of the original new UPS + batteries, 2 years on the first replacement batteries, and only 1 year on the second replacement batteries, unless you adjust the voltage (a technical task, will void your warranty, etc.).
  • On all but the lowest-capacity models, there are strings of batteries in series. This might be as few as 2, or as many as 16 batteries. All the UPS sees is the voltage across the whole string of batteries (some more advanced models like the Symmetra RM have a sense line mid-string to try to get a better idea of what is going on in the battery pack, but it is still mostly guesswork). If one of those batteries fails in a high-resistance mode, it will become a point heat source which will damage nearby batteries. If a battery fails in a low-resistance mode, the remaining batteries in the string will see a higher than expected voltage and they will all begin to overheat, which will damage them as well as any nearby batteries.
  • Many APC UPS models have a series-parallel design, where more than one series string (see above item) are connected in parallel. This includes any of the expandable units (Matrix, Symmetra, any UPS that accepts an extended runtime pack) as well as some fixed-configuration models where all of the batteries are internal to the main chassis. Even if the UPS detected a problem early on (hard to do, see the above item) and completely cut power to the batteries, the remaining parallel battery strings are still connected to the bad string and will attempt to discharge into the bad string in an attempt to equalize voltage. In larger systems, we're talking about well over 100 Amps trying to go through what may well be a small 7AH 12V battery. Most of the modular APC units only have a single battery bus. Some models have battery packs with individual status reporting (Matrix, Symmetra) so the UPS can report which battery pack is bad. But with only a single battery bus, the only option the UPS has is to increase the battery bus voltage in order to charge a pack that is reporting low (even if it is fully charged). That subjects the other packs to a slight additional stress which, over time, can cause damage to the other packs. By the way, this is why I always recommend replacing ALL batteries at one time rather than only some packs as they fail.

I have quite a few APC units here, including a Matrix 5000 that is over 20 years old and still working. I change the batteries pro-actively every 3 years and verify the float voltage at that time.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:10 AM . Last Modified: ‎2024-03-07 03:27 AM

0 Likes
0
1594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:10 AM . Last Modified: ‎2024-03-07 03:27 AM

Batteries eventually will fail no matter who manufactured them (CSB batteries are high quality by the way, I have several 12V 17Ah GP series batteries which are over 18(!) years old and still retain around 40% capacity). How and when they fail is very much dependent on the operating temperature, charging voltage and number / frequency / depth of discharge cycles. These parameters are essential and usually specified by the manufacturer. Batteries in smaller APC units like the the 750VA version have to endure elevated temperatures due to the small space shared with heat generating components like the MOSFETs and the transformer. Most SLA batteries are rated for operating temperatures between 20-25 degrees celsius, each degree above that temperature shortens useful battery life by a certain amount. Therefore it is very important to operate the UPS in a cool environment, because the internal heat generating components are going to heat up the batteries well above the room's ambient temperature anyway. Though I have never owned an SMT750 LCD ups, I do know that the previous generation (SUA750) ups had temperature compensated battery charger. The problem is that all SUA750 units I have seen, have their float voltage set too high for such a small UPS size (27.5 volts), so even with the help of temperature compensated charger it cannot reach the optimal life span of the batteries. Eg. when room temperature is 20 degrees celsius, batteries are sitting at 30-32 degrees celsius inside the UPS case. For such temperatures, float charge should be reduced to 26.8-27.0 volts at maximum for optimal battery life, which is not done in these UPSes. 27.5 volts would be perfectly fine if the batteries were sitting at 20-25 celsius.

If you are not someone who is really technically knowledgeable about these devices, the best you can do is to observe the normal operating temperature of the ups, and check it regularly. If it starts to elevate for seemingly no reason while the ambient temperature stays the same, it is very likely that the batteries are going bad and the UPS has not yet had the chance to detect the problem by itself. If you don't want to bother with this, you can just replace the batteries every 2-3 years, preventing the problem altogether.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of