First post here so please go easy. 🙂
I've just recently got into the world of Smart UPS 'tweaking' after acquiring two (2) Smart UPS 700 (SU700INT), practically from the trash bin. I cleaned them up (both have suffered severe battery leaks) and fixed the corroded battery connectors, I gave them new batteries and now they're back from the dead.
Now, it wasn't that smooth, to be honest. I had to play around with the battery calibration register ('0') so the units will report a more accurate runtime duration with the new batteries. I also adjusted the float voltage using the 'B' register so they'll read 27.33V. They were previously set to 27.60 and 27.73, respectively.
One last issue I see is that, both identical units are reporting different Load % even when I applied the exact same load in both of them. I used three 100W bulbs, which reads approx. 318W at 230V with a power factor of 0.99-1.00 on the power meter.
So, with the PF=1 or unity, VA in this case is equals to W. Doing the math, 318W / 700VA yields 45.4% Load. On UPS1, the Load reported is 53% while UPS2 reported it as 77%.
I then played around with the 'P' register to get the Load % down to 49.8% (I gave it about +4% buffer from the 45.4%).
The question is, is this at least a valid way of calibrating the Load % offset?
I am of course, referring to information found here: http://networkupstools.org/protocols/apcsmart.html
Thanks in advance!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:18 AM . Last Modified: 2024-03-17 11:58 PM
Nobody?
Anyway, I came to a realization that the Smart UPS 700 is rated for 450W. So I re-calibrated the Load% to use 450W (as opposed to 700VA) as the max load reference point.
Assuming now that 450W is 100% load, using the same test load I used before (318W at 230V), I calculated the Load% using the following formula: (Measured Watts / System Max Watts) x 100 = Load%
So,
(318W / 450W) x 100 = 70.6%. That means 318W is taking up approx. 70% of the UPS load capacity.
With the load still connected, I dialed in 70.8% in the 'B' register and now, the Load% and LED indicators properly reflect the actual load.
I understand that this calibration is only as good as the power meter's accuracy (I used a Kill-a-Watt clone), but I'm fairly confident that it is 'good enough', given that I used three (3) 100W incandescent bulbs, the measurements were close enough.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:18 AM . Last Modified: 2024-03-17 11:58 PM
Nobody?
Anyway, I came to a realization that the Smart UPS 700 is rated for 450W. So I re-calibrated the Load% to use 450W (as opposed to 700VA) as the max load reference point.
Assuming now that 450W is 100% load, using the same test load I used before (318W at 230V), I calculated the Load% using the following formula: (Measured Watts / System Max Watts) x 100 = Load%
So,
(318W / 450W) x 100 = 70.6%. That means 318W is taking up approx. 70% of the UPS load capacity.
With the load still connected, I dialed in 70.8% in the 'B' register and now, the Load% and LED indicators properly reflect the actual load.
I understand that this calibration is only as good as the power meter's accuracy (I used a Kill-a-Watt clone), but I'm fairly confident that it is 'good enough', given that I used three (3) 100W incandescent bulbs, the measurements were close enough.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.