Smart-UPS 5000: "The battery power is too low to continue to support the load" even changed batteries

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 5000: "The battery power is too low to continue to support the load" even changed batteries
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
kelvinchanswann
kelvinchanswann
Cadet

Posted: ‎2024-01-13 08:16 PM

0 Likes
4
977
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-13 08:16 PM

Smart-UPS 5000: "The battery power is too low to continue to support the load" even changed batteries

Hi there, after changing the batteries in late last year, the UPS still got the error of "The battery power is too low to continue to support the load". Not sure what to do. Appreciate with anyone can help. Thanks. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Teken
Kirk Teken
Kirk

Posted: ‎2024-01-15 06:45 AM

0 Likes
2
956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-15 06:45 AM

First thing I would do is check the production date of the battery cartridge. If they were made several years before your purchase and install - begin a RMA warranty on them. In the interim visually inspect all cells in the cartridge to be properly and securely connected. Confirm no cells are swelling or bulging. Pull each cell apart and measure their resting voltage. This would be a good time load test each cell to see how they perform and if any cell fails you know there was a bad cell in the pack.

 

If still under warranty request a RMA. If not under warranty simply replace the bad cell(s).

Reply

Link copied. Please paste this link to share this article on your social media post.

dpierce4776
Lt. Commander dpierce4776
Lt. Commander

Posted: ‎2024-01-16 06:39 AM

0 Likes
0
935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-16 06:39 AM

To branch off of what @Teken said if you have an NMC card there is a setting under Configuration > Shutdown that sets the amount of runtime you want the UPS to start shutting down out. I believe the default is 10 minutes. This is to protect the batteries though extended runtime and power outages. As completely draining the batteries can result in shorter battery life.

 

Anyways check the setting to see where it is set. If it is too high or higher than the runtime the UPS tells you it can do under your current load you will get that message. 

Reply

Link copied. Please paste this link to share this article on your social media post.

kelvinchanswann
kelvinchanswann
Cadet

Posted: ‎2024-01-16 08:40 PM

In response to Teken
0 Likes
1
935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-16 08:40 PM

Thanks Teken. It works after recalibrated the batteries. I didn't recognised it as I didn't need to recalibrated the batteries on the other same model UPS. Anyway, thanks for your input. 

Reply

Link copied. Please paste this link to share this article on your social media post.

dpierce4776
Lt. Commander dpierce4776
Lt. Commander

Posted: ‎2024-01-18 10:26 AM

In response to kelvinchanswann
0 Likes
0
916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-18 10:26 AM

@kelvinchanswann Its a good idea to re-calibrate after every battery swap and they are charged to 100%. The UPS will do self test over time and though that calibrate itself to give you and approximate run time at the current load. 

 

Which is more than likely why your device continued to give the alert even after you changed the batteries. By re-calibrating the batteries you get a more accurate reading than the self test does. Calibration takes runs on battery until it reaches 20% then recharges the battery back up. This gives you a better understanding of how your batteries are going to handle than a 15 second draw.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore