Smart-UPS 3000VA Error during software update network adapter 9631

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 3000VA Error during software update network adapter 9631
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 06:02 AM . Last Modified: ‎2024-03-04 11:57 PM

0 Likes
5
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:02 AM . Last Modified: ‎2024-03-04 11:57 PM

Smart-UPS 3000VA Error during software update network adapter 9631

Dear,


This morning I replaced an older UPS with a new one, but I also wanted to update the software of the network mnagement card.  I downloaded what I think I needed too (update for 9631 on Smart UPS), the installation program started with the boot monitor, but after that step and the restart, I can't access it anymore.

Starting Upgrade 09/04/14 15:07:10
-----------------
[09/04/14 15:07:10] 53.154.100.26: Pinging (via ICMP) device
[09/04/14 15:07:10] 53.154.100.26: Device connection passed
[09/04/14 15:07:11] 53.154.100.26: Testing FTP Log-in
[09/04/14 15:07:14] 53.154.100.26: FTP Log-in passed
[09/04/14 15:07:15] 53.154.100.26: Saving data file
[09/04/14 15:07:16] 53.154.100.26: AOS Prior to firmware transfer: Network Management Card AOS v6.0.6

[09/04/14 15:07:16] 53.154.100.26: APP Prior to firmware transfer: Smart-UPS & Matrix-UPS APP v6.0.6

[09/04/14 15:07:16] 53.154.100.26: Saving event & configuration files
[09/04/14 15:07:39] 53.154.100.26: Transferring firmware file (1/3): Boot Monitor
[09/04/14 15:07:47] 53.154.100.26: Boot Monitor transfer successful
[09/04/14 15:07:49] 53.154.100.26: Restarting network interface
[09/04/14 15:08:20] 53.154.100.26: Device connection passed
[09/04/14 15:08:22] 53.154.100.26: Testing FTP Log-in
[09/04/14 15:08:56] 53.154.100.26: ERROR --> FTP Log-in failed

If I ping the device, most of the time I get no reply, meaning that it can happen it replies (I also verified with Wireshark).  I think the card is in an "endless reboot loop", but I'd like to know if there is an option to get it working again ... preferably without shutting the UPS down...

Thanks,

Alain

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 06:02 AM . Last Modified: ‎2024-03-04 11:57 PM

0 Likes
0
1683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:02 AM . Last Modified: ‎2024-03-04 11:57 PM

Everything gets loaded into the app's spot, and then if not corrupt, copied into the appropriate space. That way if, for example, the AOS transfer fails, it will only overwrite the APP and the previous AOS will continue work accepting .bin files.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-07-01 06:02 AM . Last Modified: ‎2024-03-04 11:57 PM

0 Likes
0
1683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:02 AM . Last Modified: ‎2024-03-04 11:57 PM

Dear,


This morning I replaced an older UPS with a new one, but I also wanted to update the software of the network mnagement card.  I downloaded what I think I needed too (update for 9631 on Smart UPS), the installation program started with the boot monitor, but after that step and the restart, I can't access it anymore.

Starting Upgrade 09/04/14 15:07:10
-----------------
[09/04/14 15:07:10] 53.154.100.26: Pinging (via ICMP) device
[09/04/14 15:07:10] 53.154.100.26: Device connection passed
[09/04/14 15:07:11] 53.154.100.26: Testing FTP Log-in
[09/04/14 15:07:14] 53.154.100.26: FTP Log-in passed
[09/04/14 15:07:15] 53.154.100.26: Saving data file
[09/04/14 15:07:16] 53.154.100.26: AOS Prior to firmware transfer: Network Management Card AOS v6.0.6

[09/04/14 15:07:16] 53.154.100.26: APP Prior to firmware transfer: Smart-UPS & Matrix-UPS APP v6.0.6

[09/04/14 15:07:16] 53.154.100.26: Saving event & configuration files
[09/04/14 15:07:39] 53.154.100.26: Transferring firmware file (1/3): Boot Monitor
[09/04/14 15:07:47] 53.154.100.26: Boot Monitor transfer successful
[09/04/14 15:07:49] 53.154.100.26: Restarting network interface
[09/04/14 15:08:20] 53.154.100.26: Device connection passed
[09/04/14 15:08:22] 53.154.100.26: Testing FTP Log-in
[09/04/14 15:08:56] 53.154.100.26: ERROR --> FTP Log-in failed

If I ping the device, most of the time I get no reply, meaning that it can happen it replies (I also verified with Wireshark).  I think the card is in an "endless reboot loop", but I'd like to know if there is an option to get it working again ... preferably without shutting the UPS down...

Thanks,

Alain

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:02 AM . Last Modified: ‎2024-03-04 11:57 PM

0 Likes
0
1683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:02 AM . Last Modified: ‎2024-03-04 11:57 PM

Hi Alain,

Yes, that is the correct file.

Are you local to the UPS/AP9631? If so, can you tell me what is going on with the LEDs on the AP9631 itself? There is the status LED (which is most important) which has a checkmark or X next to it and then the 10/100 network link LED. If it is easier, you could temporarily unplug the network cable to make sure you focus on the status LED. I need to know what color(s) it is and if it is solid or flashing. Observe it for about 2-3 minutes and let me know. That should be enough time to help me understand if it is indeed in a reboot cycle or not.

Depending on what you find, we can try a few different things.

1.) Just try to reseat/power cycle the AP9631 by removing it from the UPS SmartSlot for 5-10 seconds and sticking it back in. We'd recheck status LED behavior again for 2-3 minutes. (The card is hot swappable so you won't ever need to turn off the UPS itself.)

2.) Depending on status LED, we can try to serial into the card itself if you have the 940-0299 DB-9 to Tip Ring Sleeve 2.5mm cable that came with it.

3.) We can try formatting the card by holding the reset button for 20 seconds (which there are a few more details to that process I'll tell you if we get that far before you go ahead) but this does erase every piece of configuration on the card (TCP/IP settings, etc) so it will require some reconfiguration.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 06:02 AM . Last Modified: ‎2024-03-04 11:57 PM

0 Likes
0
1683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:02 AM . Last Modified: ‎2024-03-04 11:57 PM

Hi Angela,


I didn't work till this afternoon, and then the device reacted to ping again, but gave an error when I tried to access it again via the web interface.

I though it would be smart trying to do the installation again, but it wasn't, the device didn't react anymore.  The Status LED was always green (just until the reboot).  I tried the first step (removing the card for a while, and then putting it back).  Again the status led came green, but no IP-reaction ...

After a while (30 minutes?)  I saw it reacted to ping again, but the web-interface said it fails to load.  Via telnet I could get in, giving me the following "about":

Application Module
---------------
Name:                   bootmon
Version:                v1.0.8
Date:                   Apr  8 2014
Time:                   10:59:40

APC OS(AOS)
---------------
Name:                   aos
Version:                v6.0.6
Date:                   Apr  5 2013
Time:                   10:36:37

APC Boot Monitor
---------------
Name:                   bootmon
Version:                v1.0.8
Date:                   Apr  8 2014
Time:                   10:59:40

I don't think that was the idea of the update of the Application Module...

Tried ftp with filezilla, login ok, but I couldn't transfer the bin file for the aos.  Ftp manually didn't work ... until I gave the device some rest again smile  next attempt via ftp from the dos box worked for the aos-software, and secondly for the sumx-software as well.  "About" now shows the correct information (sumx v6.2.0 for application ; and aos v6.2.0) ; but I didn't have to do a restart of the device... (which is ok for me, as long as something works .. I think it just restarts when it recognizes the new bin file)

Also the webinterface is ok ...

But .. as I have 3 more to update, I was wondering what they would do ...

I though for the worst (but I knew the work around), but on the first it crashed a step later (so after update of bootmon & aos it stopped again, and the application module now shows it is aos v6.2.0)...

The second one had no problems, the third neither.

So, finally all is good for the management cards... Next on the planning ... update of the UPS-firmware, but as this involves a power down, this has to be scheduled a bit better... How useful is this to do, because of the impact I don't want to do just a 'nice to have'... (3 of the FJX3000RMHV2UNC-devices run on 05.8, the 4th on 06.1)? The last one could be possible next week, the others I have to be much more careful about..

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:02 AM . Last Modified: ‎2024-03-04 11:57 PM

0 Likes
0
1683
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:02 AM . Last Modified: ‎2024-03-04 11:57 PM

Hmm OK. To help you understand, when you upgrade the .bin firmware files, they get stored in different spots in memory.

Bootmon goes first and I believe that goes in the application module section in flash, it reboots, then goes in its own section. Then, the AOS goes into the application's spot/location, reboots and goes in its own AOS spot in memory, and then the new application file goes in the old AOS's spot and eventually reboots and goes into the application spot. So, there is sort of an overwrite of things since the NMC does have space limitation.

Something must be failing mid firmware upgrade some place to get stuck. Usually what I see is customers with two AOS files and you just need to FTP to it and see what it says at the FTP prompt for the AOS version. I have not seen the two bootmonitor scenario but I am glad you got it working. Firmware upgrade via bootmonitor (which requires a serial connection) can always be done to recover the cards worst case. I cannot explain specifically what happened but can usually help depending on what files are present on the card.

Now, on your UPS firmware - I understand it is a hassle and you want it to be worth it. The latest for that UPS is actually UPS 06.5. I looked at the release notes for that and saw "Improve the reliability and behavior of system during a Self-Test." Doesn't mean there wasn't other fixes though smile For UPS 06.1, I see:

  • Resolves issue where following reset to factory defaults, the Power Quality setting shows up with incorrect default value.
  • Improve interoperability with software when updating the UPS Sensitivity setting.
  • Improve interoperability with some HP servers.
  • Improve reliability of repeated SNMP commands issued to optional network card.
  • Improve the LCD behavior when a Legacy Communications Card (LCC) is installed or removed.


So of course, the UPS 06.1 updates would be in UPS 06.5 too. You can also use your NMC to update your UPS versus using the serial or USB cable to do it (which your UPS is just a variant of SMX mentioned in this article)-> How do I upgrade my SMT/SMX/SRT Smart-UPS firmware using my AP9630/AP9631 Network Management Card? |... but it does not change the fact that the output of the UPS must be off and also that you likely want to make sure that the network connection to your NMC is not powered by the UPS.


Let me know if you have any questions.


Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 06:02 AM . Last Modified: ‎2024-03-04 11:57 PM

0 Likes
0
1684
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:02 AM . Last Modified: ‎2024-03-04 11:57 PM

Everything gets loaded into the app's spot, and then if not corrupt, copied into the appropriate space. That way if, for example, the AOS transfer fails, it will only overwrite the APP and the previous AOS will continue work accepting .bin files.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore