Smart-UPS 3000 lost connection (ping timeout)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 3000 lost connection (ping timeout)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:42 AM

0 Likes
5
1091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:42 AM

Smart-UPS 3000 lost connection (ping timeout)

Hello out there,

i have a problem with my Smart-UPS 3000.
sometimes it isn't available in the network.

I noticed the problem since we got a network monitoring here. maybe you know "nagios" the open source one.
there are all the day a flapping state at the APC UPS.
Only a simple ping is send from the nagios server.
Here are the results of a manual ping sequence from my local machine: (sry its a german one ^^)

-----
Ping wird ausgef?ührt fü?r 10.1.0.120 mit 32 Bytes Daten:

Antwort von 10.1.0.120: Bytes=32 Zeit=4ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=3ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=99ms TTL=255
... after some minutes (2-3) ...
Antwort von 10.1.0.120: Bytes=32 Zeit=3ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=3ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=107ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=4ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=2ms TTL=255
Zeit?überschreitung der Anforderung.
Zeit?überschreitung der Anforderung.
... after some minutes (2-3) ...
Zeitü?berschreitung der Anforderung.
Zeitü?berschreitung der Anforderung.
Antwort von 10.1.0.120: Bytes=32 Zeit=3ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=3ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=27ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=4ms TTL=255
-----

i got the same problem at a second Smart-UPS 3000. at nearly the same time
nothing related in the eventlog.

all other machines and stuff is available all the time. only the 2 apc ups not.

how to solve the problem?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:42 AM

0 Likes
0
1091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:42 AM

Hello out there,

i have a problem with my Smart-UPS 3000.
sometimes it isn't available in the network.

I noticed the problem since we got a network monitoring here. maybe you know "nagios" the open source one.
there are all the day a flapping state at the APC UPS.
Only a simple ping is send from the nagios server.
Here are the results of a manual ping sequence from my local machine: (sry its a german one ^^)

-----
Ping wird ausgef?ührt fü?r 10.1.0.120 mit 32 Bytes Daten:

Antwort von 10.1.0.120: Bytes=32 Zeit=4ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=3ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=99ms TTL=255
... after some minutes (2-3) ...
Antwort von 10.1.0.120: Bytes=32 Zeit=3ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=3ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=107ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=4ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=2ms TTL=255
Zeit?überschreitung der Anforderung.
Zeit?überschreitung der Anforderung.
... after some minutes (2-3) ...
Zeitü?berschreitung der Anforderung.
Zeitü?berschreitung der Anforderung.
Antwort von 10.1.0.120: Bytes=32 Zeit=3ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=3ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=27ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=4ms TTL=255
-----

i got the same problem at a second Smart-UPS 3000. at nearly the same time
nothing related in the eventlog.

all other machines and stuff is available all the time. only the 2 apc ups not.

how to solve the problem?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:42 AM

0 Likes
0
1091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:42 AM

how frequently does this happen? can you tell us the exact model of the network card inside the UPS? i would try to rule out a network issue by directly connecting to the network management card on a peer to peer network if possible and doing a constant ping.

since both cards are doing it, it seems as though something else is going on. if you could indeed post the event.txt from the network cards when the timeouts occur, that'd be handy too.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:42 AM

0 Likes
0
1091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:42 AM

ok i will try the things that you describe.
wait some days and i will post the results

where do i get the management card info?
the webinterface of the ups tells me.
UPS -> About:
About UPS

Model: Smart-UPS 3000 RM
Serial Number: JS0750018352
Firmware Revision: 666.6.I
Manufacture Date: 12/15/07

Message was edited by: Besth

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:42 AM

0 Likes
0
1091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:42 AM

Ok after some tests i found out that there is a problem with our Allied Telesys Switch. I put the 2 UPS on an other switch (netgear) and it works without problems. maybe the at switch have problems with only 100mbit/s? i dont know ...
thx for the advices!

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:42 AM

0 Likes
0
1091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:42 AM

>
Ok after some tests i found out that there is a problem with our Allied Telesys Switch. I put the 2 UPS on an other switch (netgear) and it works without problems. maybe the at switch have problems with only 100mbit/s? i dont know ...
thx for the advices!
>

You may want to try setting a fixed port speed rather than having the NMC auto-negotiate.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:42 AM

0 Likes
0
1092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:32 AM . Last Modified: ‎2024-03-14 12:42 AM

Hello out there,

i have a problem with my Smart-UPS 3000.
sometimes it isn't available in the network.

I noticed the problem since we got a network monitoring here. maybe you know "nagios" the open source one.
there are all the day a flapping state at the APC UPS.
Only a simple ping is send from the nagios server.
Here are the results of a manual ping sequence from my local machine: (sry its a german one ^^)

-----
Ping wird ausgef?ührt fü?r 10.1.0.120 mit 32 Bytes Daten:

Antwort von 10.1.0.120: Bytes=32 Zeit=4ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=3ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=99ms TTL=255
... after some minutes (2-3) ...
Antwort von 10.1.0.120: Bytes=32 Zeit=3ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=3ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=107ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=4ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=2ms TTL=255
Zeit?überschreitung der Anforderung.
Zeit?überschreitung der Anforderung.
... after some minutes (2-3) ...
Zeitü?berschreitung der Anforderung.
Zeitü?berschreitung der Anforderung.
Antwort von 10.1.0.120: Bytes=32 Zeit=3ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=3ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=27ms TTL=255
Antwort von 10.1.0.120: Bytes=32 Zeit=4ms TTL=255
-----

i got the same problem at a second Smart-UPS 3000. at nearly the same time
nothing related in the eventlog.

all other machines and stuff is available all the time. only the 2 apc ups not.

how to solve the problem?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.