Smart-UPS 3000 automatically shuts off if wrong serial cable is connected

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 3000 automatically shuts off if wrong serial cable is connected
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:26 AM . Last Modified: ‎2024-03-08 02:35 AM

0 Likes
4
2952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:26 AM . Last Modified: ‎2024-03-08 02:35 AM

Smart-UPS 3000 automatically shuts off if wrong serial cable is connected

I have tested four different Smart-UPS 3000 units, and all of them automatically turn off if you plug in a regular serial cable in the unit. Unfortunately I had to learn the hard way... I did not have the serial cable that came with the UPS at hand, so I plugged in a regular serial cable, and the UPS unit that was currently in production turned off, causing severe data loss on some of my servers. It is unbelievable that a company like APC will place a tag on the port that says "Serial Port" but it doesn't give you any warnings that if you plug in any serial cable that's not the one that came with the unit, it will shut off. I'm very disappointed with this product.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:26 AM . Last Modified: ‎2024-03-08 02:34 AM

0 Likes
0
2951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:26 AM . Last Modified: ‎2024-03-08 02:34 AM

what UPS model do you have specifically? it should be on a sticker on the back of the UPS.

sounds like a Smart UPS RT 3000?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:26 AM . Last Modified: ‎2024-03-08 02:35 AM

0 Likes
0
2951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:26 AM . Last Modified: ‎2024-03-08 02:35 AM

Hi,

I am sorry for the inconvenience on this issue. I will certainly note this on our end with the appropriate team as far as the label/sticker goes on the actual serial port on the back of the UPS because that is a good idea. I was under the impression, some of them had labels over them when you buy them but they can be ripped off of course. Since they have a special pinout, that is what causes the UPSs to shutdown.

Although, it is noted in the manual (see attached screenshot).

I am assuming you have the tower model, but it is the same idea. Here is the link to the [SUA3000 manual|http://www.apcmedia.com/salestools/ASTE-6YWRZE_R0_EN.pdf].

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:26 AM . Last Modified: ‎2024-03-08 02:34 AM

0 Likes
0
2951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:26 AM . Last Modified: ‎2024-03-08 02:34 AM

2 years later...I learned the same lesson. Luckily I was not in production yet.
Also, way to go with USB design....it does not look like RJ45 at all.
Anyhow...thanks for posting this, it saved some of my sanity.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:26 AM . Last Modified: ‎2024-03-08 02:34 AM

0 Likes
0
2951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:26 AM . Last Modified: ‎2024-03-08 02:34 AM

Guys-
Same thing happened to me. We plugged in a regular cable and it turned off our whole EDM; thankfully it wasn't operational yet or something bad would have happened!

BUT we wanted to make sure that's what did it so we plugged it in again after powering everything back up. NOW we have a fault light and the bottom and middle battery LEDs illuminated. Great. Now I can't meet my service window....can anyone help?? This thing is brand new!

Tad

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:26 AM . Last Modified: ‎2024-03-08 02:34 AM

0 Likes
0
2952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:26 AM . Last Modified: ‎2024-03-08 02:34 AM

what UPS model do you have specifically? it should be on a sticker on the back of the UPS.

sounds like a Smart UPS RT 3000?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore