Smart UPS 3000 XL

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 3000 XL
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:37 AM

0 Likes
9
2351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:37 AM

Smart UPS 3000 XL

At our company we have a smart ups 3000 xl. The device is bought in 2004. In 2008 the batteries where changed.
Since a few days we keep getting warm-starts. I upgraded the firmware but no luck.
If i want to calibrate the batteries are empty right away and the ups shut down.
If i look at the logs the batteries are always (full and empty) on 55.05 vdc.

What do you think? Do I have to buy a new ups or could it be something else.

Kind regards, Martijn

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:36 AM

0 Likes
0
2351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:36 AM

ok, well based on the info you provided, i tend to think that there is an issue with the batteries themselves. they are 2+ years old now and if they have been used heavily and affected by heat from the UPS, they could be failing a little earlier than the 3 year mark.

if it were me, i would try replacing the batteries first. if you don't want to do that, you can look into trading the UPS in for a discount on a new one and having a new UPS with new 2 year warranty on both the batteries and UPS but again, i am making an educated decision here in suggesting to replace the batteries first. it could be something else that is not obvious but to me, that would be the first step. or, if you have another unit that uses the same batteries, you could try to swap them and see if the issue follows the batteries.

hope that helps.

after the battery issue is resolved, i'd like to see if the warmstart issue clears up. i see no reasons for the warmstarts except that you are getting spammed with battery related UPS issues. this is rare to see this cause a warmstart but i see no other reasons in the log.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:37 AM

0 Likes
0
2351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:37 AM

hi

a warmstart is related to the installed network management card only. it generally does not have anything to do with the UPS or its function.

i'd suggest reading [this article|http://nam-en.apc.com/app/answers/detail/a_id/2572/] that explains what it means.

first course of action i would suggest is posting your event.txt here for us using [these instructions|http://nam-en.apc.com/app/answers/detail/a_id/9321/] so we can see if the warmstarts are being caused by something. pending review of the event.txt, we may suggest a network management card firmware upgrade or different course of action.

anyway, there is no immediate cause for concern with these messages.

thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:37 AM

0 Likes
0
2351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:37 AM

It is not only the warm start but the ups isn't possible to do a self test any more.

I turned the ups manually off but it took me 30min or so to turn it on again.
When i pressed the on button it blinks en turns off. Sometimes the ups turns on the net led is blinking and when it turns on the led the ups fails.
Then is disconnected everything and tried again eventually the ups turned on.

I have also added the data.txt. There you can see that even when the batteries are empty there is always 55.05 vdc??

Message was edited by: ict@paswerk.nl

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:37 AM

0 Likes
0
2351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:37 AM

ok, i took a look at the logs.

how much runtime does the UPS report via the network management card interface? it seems to be that the UPS thinks it does not have a lot of runtime left - either by mistake or because the battery is indeed a couple of years old and has been used fairly often.

these messages are spamming the log that point me towards that:

12/28/2010 10:04:41 UPS: A discharged battery condition no longer exists. 0x0108
12/28/2010 10:04:32 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately. 0x0107
12/28/2010 10:04:31 UPS: A discharged battery condition no longer exists. 0x0108
thus, i would need to know the runtime reported by the UPS versus the amount of on battery time you have observed during a recent discharge. i want to fix that and then look into the warmstarts. the NMC might be getting spammed by all of the error messages coming from the UPS about the runtime and batteries so it may keep rebooting.

let me know what you see in the interface for runtime and how much time the UPS actually runs on battery and we'll go from there.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:37 AM

0 Likes
0
2350
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:37 AM

With a load of 40% at the moment the runtime is 13min according to the NMC.
But when I run a battery test they are depleted immediately.

I just measured the batteries with a multi meter and they are about 54 volts. When I unplug the connection to de ups it drops to 53.8 v. But the ups keeps reporting 55.05v.

Message was edited by: ict@paswerk.nl

Message was edited by: ict@paswerk.nl

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:37 AM

0 Likes
0
2351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:37 AM

one last thing, in the NMC, what is the "low battery duration" value set to? this is under UPS tab->Configuration->Shutdown.

the default is two minutes but did you raise this value for some reason? is it close to the total runtime of 13 mins?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:36 AM

0 Likes
0
2352
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:36 AM

ok, well based on the info you provided, i tend to think that there is an issue with the batteries themselves. they are 2+ years old now and if they have been used heavily and affected by heat from the UPS, they could be failing a little earlier than the 3 year mark.

if it were me, i would try replacing the batteries first. if you don't want to do that, you can look into trading the UPS in for a discount on a new one and having a new UPS with new 2 year warranty on both the batteries and UPS but again, i am making an educated decision here in suggesting to replace the batteries first. it could be something else that is not obvious but to me, that would be the first step. or, if you have another unit that uses the same batteries, you could try to swap them and see if the issue follows the batteries.

hope that helps.

after the battery issue is resolved, i'd like to see if the warmstart issue clears up. i see no reasons for the warmstarts except that you are getting spammed with battery related UPS issues. this is rare to see this cause a warmstart but i see no other reasons in the log.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:36 AM

0 Likes
0
2351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:36 AM

No it's the default 2 min.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:36 AM

0 Likes
0
2351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:25 AM . Last Modified: ‎2024-03-13 05:36 AM

Indded, it where the batteries. I changed them with another 3000xl and the problem is over.
So we have bought new batteries. Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

faziog
faziog
Cadet

Posted: ‎2024-03-25 03:26 AM

0 Likes
0
1789
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-25 03:26 AM

Can i add a network card to my Smart UPS 3000 XL?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore