Smart-UPS 3000 Stuck in Self Test Mode

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 3000 Stuck in Self Test Mode
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:41 PM

0 Likes
14
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:41 PM

Smart-UPS 3000 Stuck in Self Test Mode

I have a Smart-UPS 3000. It continually goes into self test mode until the batteries are depleted.
Here is a snippet of the event log - note the time stamps.
I have tried setting Perform self-test = Never.

Is there a way to upgrade the firmware, or flash the system?
Firmware Revision: 90.14.D
Serial No. YS0306210449

8/27/10 09:01:46 Self Test Passed
8/27/10 09:01:38 Self Test Initiated
8/27/10 09:01:22 Self Test Passed
8/27/10 09:01:05 Self Test Initiated
8/27/10 09:00:49 Self Test Passed
8/27/10 09:00:24 Self Test Initiated
8/27/10 09:00:24 Battery Discharged
8/27/10 09:00:15 Self Test Passed
8/27/10 09:00:07 Insufficient Runtime Available
8/27/10 09:00:07 Self Test Initiated
8/27/10 08:59:59 Self Test Failed
8/27/10 08:59:42 Self Test Initiated
8/27/10 08:59:34 Self Test Passed
8/27/10 08:59:17 Self Test Initiated
8/27/10 08:58:12 Self Test Passed
8/27/10 08:58:04 Self Test Initiated
8/27/10 08:53:12 Sufficient Runtime Available
8/27/10 08:53:04 Insufficient Runtime Available
8/27/10 08:52:47 Sufficient Runtime Available
8/27/10 08:52:31 Insufficient Runtime Available
8/27/10 08:52:23 Sufficient Runtime Available
8/27/10 08:52:15 Insufficient Runtime Available
8/27/10 08:52:07 Sufficient Runtime Available
8/27/10 08:51:51 Insufficient Runtime Available
8/27/10 08:51:51 Self Test Passed
8/27/10 08:51:43 Sufficient Runtime Available
8/27/10 08:51:42 Self Test Initiated
8/27/10 08:51:34 Self Test Passed
8/27/10 08:51:26 Insufficient Runtime Available
8/27/10 08:51:17 Self Test Initiated
8/27/10 08:51:09 Self Test Passed
8/27/10 08:51:00 Self Test Initiated
8/27/10 08:50:52 Self Test Passed
8/27/10 08:50:44 Self Test Initiated
8/27/10 08:50:35 Self Test Passed
8/27/10 08:50:27 Self Test Initiated
8/27/10 08:50:19 Self Test Passed

Message was edited by: rdennisak

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:40 PM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:40 PM

I have a Smart-UPS 3000. It continually goes into self test mode until the batteries are depleted.
Here is a snippet of the event log - note the time stamps.
I have tried setting Perform self-test = Never.

Is there a way to upgrade the firmware, or flash the system?
Firmware Revision: 90.14.D
Serial No. YS0306210449

8/27/10 09:01:46 Self Test Passed
8/27/10 09:01:38 Self Test Initiated
8/27/10 09:01:22 Self Test Passed
8/27/10 09:01:05 Self Test Initiated
8/27/10 09:00:49 Self Test Passed
8/27/10 09:00:24 Self Test Initiated
8/27/10 09:00:24 Battery Discharged
8/27/10 09:00:15 Self Test Passed
8/27/10 09:00:07 Insufficient Runtime Available
8/27/10 09:00:07 Self Test Initiated
8/27/10 08:59:59 Self Test Failed
8/27/10 08:59:42 Self Test Initiated
8/27/10 08:59:34 Self Test Passed
8/27/10 08:59:17 Self Test Initiated
8/27/10 08:58:12 Self Test Passed
8/27/10 08:58:04 Self Test Initiated
8/27/10 08:53:12 Sufficient Runtime Available
8/27/10 08:53:04 Insufficient Runtime Available
8/27/10 08:52:47 Sufficient Runtime Available
8/27/10 08:52:31 Insufficient Runtime Available
8/27/10 08:52:23 Sufficient Runtime Available
8/27/10 08:52:15 Insufficient Runtime Available
8/27/10 08:52:07 Sufficient Runtime Available
8/27/10 08:51:51 Insufficient Runtime Available
8/27/10 08:51:51 Self Test Passed
8/27/10 08:51:43 Sufficient Runtime Available
8/27/10 08:51:42 Self Test Initiated
8/27/10 08:51:34 Self Test Passed
8/27/10 08:51:26 Insufficient Runtime Available
8/27/10 08:51:17 Self Test Initiated
8/27/10 08:51:09 Self Test Passed
8/27/10 08:51:00 Self Test Initiated
8/27/10 08:50:52 Self Test Passed
8/27/10 08:50:44 Self Test Initiated
8/27/10 08:50:35 Self Test Passed
8/27/10 08:50:27 Self Test Initiated
8/27/10 08:50:19 Self Test Passed

Message was edited by: rdennisak

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 14
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:41 PM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:41 PM

The logs are from the PowerChute Business Edition. To me this is irrelevant.

The UPS is connected via a Serial cable. There is not a usb option.

I have not tried removing the cable, but I will do that.

How do I monitor/configure the UPS without the cable connected?

Thanks,
Rick

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:41 PM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:41 PM

Hi Rick,

We wouldn't really unplug/ remove the cable that long. I've seen cases wherein a bad cable that is connected to the UPS is the one that is causing the problem. Can we remove the cable for 3 minutes just to check if the UPS would still continue doing the self-test? By the way, are you just seeing the logs or you can actually see the UPS do a self-test?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:41 PM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:41 PM

I will be on site today and I'll disconnect the cable and see what happens.

The UPS is physically performing the tests - it beeps/clicks and the fan goes on, lights go amber, etc.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:41 PM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:41 PM

Thanks Rick. Please keep us posted. Should you need a immediate assistance you can contact the APC Technical Support at 800.800.4272

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:41 PM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:41 PM

I've been experiencing the same problem recently and came across this thread and was wondering if there was an answer. UPS is an SUA3000 tower connected to a Dell 2950 with the same serial to serial cable since the UPS was installed 4 to 5 years ago. Recently the UPS began to stop suppling power to the 2950 for almost exactly 20 minutes on a random basis. After a week or so of I moved that power cord to another UPS (the 2950 has dual power supply) and ordered new batteries.

Installed the batteries and that is when the constant self test cycles began. Some time the self tests fail, some times they pass but they continue many times a minute until I disconnected the serial cable. Then they stopped.

Other than replacing the batteries no other changes made.

I suspect that the UPS itself is failing but can't be sure. The load on the UPS is very light (less than 30%) and I have had perhaps one power outage in the past 5 years.

Any thoughts? Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:41 PM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:52 AM . Last Modified: ‎2024-03-13 11:41 PM

To be clear if the cable is disconnected it wont do a self test and if so, try pushing and holding the self test button and if it passes the ups is most likely fine,
also please provide the model and serial number of the unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:41 PM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:41 PM

I agree on what Wallander has said, if the unit stops doing self-test after disconnecting the cable and it all works well then the cable one possible culprit. To check if it is the cable, I would advise you to try a different APC cable on this UPS or try that cable on another UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:41 PM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:41 PM

Test

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:41 PM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:41 PM

Thanks to both for the helpful reply. Sorry for delay in response, was offsite on another project. With cable disconnected ran self test on unit which passed. Installed new (serial to serial) cable and everything worked fine. Re-installed the original cable and the unit has been runing fine for over an hour now. Did a self test from the console which passed. Note that I now have the unit configured to not run scheduled self tests ( had made this configuration change on the 15th but it did not make a difference on that day ). So at this point it looks like the unit is back to normal with new batteries. I suspect that the batteries I removed are still good so I'll hang on to them. (FYI: this is a Smart-UPS 3000, Serial JS0749008115, mfr date: 12-5-07, firmware 655.17.D) Thanks again to both. jc.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:41 PM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:41 PM

I posted a reply a few minutes ago stating that all was well. After pausing to wipe the egg off my face I have to report that the problem is not resolved and the unit is still performing continuous self tests. What I noticed is that on the self-test panel on the console there is a message stating that the battery does not have sufficient charge to run a self test. However, the APCBEAgent reports a continue stream of self test passed/failed events to the Windows Event Log. At this point I've disconnected the serial cable and will wait for the battery to come up to full charge, reconnect the cable and see what happens. (On the Self Test panel there is a message that says the unit does not have scheduled self tests.) I'll report back what I see in a day or so. jc.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:41 PM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:41 PM

this really sounds like a faulty serial cable to me or something touching the UPS serial port causing there to be voltage on the pins. are you able to leave that secondary cable hooked up to rule out the cable?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:40 PM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:40 PM

Sure. I have brand new serial cable which i'll install after the battery comes up to charge. thanks. jc.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:40 PM

0 Likes
0
2564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:40 PM

no problem - will await your feedback on trying that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:40 PM

0 Likes
0
2565
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:53 AM . Last Modified: ‎2024-03-13 11:40 PM

I have a Smart-UPS 3000. It continually goes into self test mode until the batteries are depleted.
Here is a snippet of the event log - note the time stamps.
I have tried setting Perform self-test = Never.

Is there a way to upgrade the firmware, or flash the system?
Firmware Revision: 90.14.D
Serial No. YS0306210449

8/27/10 09:01:46 Self Test Passed
8/27/10 09:01:38 Self Test Initiated
8/27/10 09:01:22 Self Test Passed
8/27/10 09:01:05 Self Test Initiated
8/27/10 09:00:49 Self Test Passed
8/27/10 09:00:24 Self Test Initiated
8/27/10 09:00:24 Battery Discharged
8/27/10 09:00:15 Self Test Passed
8/27/10 09:00:07 Insufficient Runtime Available
8/27/10 09:00:07 Self Test Initiated
8/27/10 08:59:59 Self Test Failed
8/27/10 08:59:42 Self Test Initiated
8/27/10 08:59:34 Self Test Passed
8/27/10 08:59:17 Self Test Initiated
8/27/10 08:58:12 Self Test Passed
8/27/10 08:58:04 Self Test Initiated
8/27/10 08:53:12 Sufficient Runtime Available
8/27/10 08:53:04 Insufficient Runtime Available
8/27/10 08:52:47 Sufficient Runtime Available
8/27/10 08:52:31 Insufficient Runtime Available
8/27/10 08:52:23 Sufficient Runtime Available
8/27/10 08:52:15 Insufficient Runtime Available
8/27/10 08:52:07 Sufficient Runtime Available
8/27/10 08:51:51 Insufficient Runtime Available
8/27/10 08:51:51 Self Test Passed
8/27/10 08:51:43 Sufficient Runtime Available
8/27/10 08:51:42 Self Test Initiated
8/27/10 08:51:34 Self Test Passed
8/27/10 08:51:26 Insufficient Runtime Available
8/27/10 08:51:17 Self Test Initiated
8/27/10 08:51:09 Self Test Passed
8/27/10 08:51:00 Self Test Initiated
8/27/10 08:50:52 Self Test Passed
8/27/10 08:50:44 Self Test Initiated
8/27/10 08:50:35 Self Test Passed
8/27/10 08:50:27 Self Test Initiated
8/27/10 08:50:19 Self Test Passed

Message was edited by: rdennisak

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore