Smart-UPS 3000 RM DL3 - discharged battery condition no longer exists

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 3000 RM DL3 - discharged battery condition no longer exists
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

0 Likes
8
3188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

Smart-UPS 3000 RM DL3 - discharged battery condition no longer exists

Hello,

I've got a Problem with a SmartUPS 3000 RM. We replaced the Batery Packs and now we get the following error massege:

A discharged battery condition no longer exists
he battery power is too low to support the load; if power fails, the UPS will be shut down immediately.


Is that (maybe) a Problem with the rechargeble Unit?
And how can I find out what exactly the Problem is?

Thanks for helping

Sven

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

0 Likes
0
3185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

we really need to be absolutely sure of the exact model number on the UPS so I can give you the correct instructions. i will PM you what I have.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

0 Likes
0
3185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

hi

is this a genuine APC replacement battery?

what is the total percentage of load you have on the UPS? How much runtime is the UPS reporting? What is the low battery signaling time/low battery duration set to?

All of these items should be found in the software interface that it seems you already have set up.

let us know

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

0 Likes
0
3185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

Now we've got it.

Here is the description of the USV:

DLA3000RMI2U
serienr: YS0330310483

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

0 Likes
0
3185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

Hey,

Yes, it is a geniune Replacement from APC. Its the RBC43.

Load in Watts 61,7%
Battery Capacity 100%
Runtime Remaining: 5 minutes
Last Battery Transfer: Detection of a line voltage notch or spike
low battery duration set 2 minutes

regards,

Sven

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

0 Likes
0
3185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

i think what is happening is possibly your load is fluctuating a couple of minutes and getting close to the low battery signaling time (since its set to two minutes). Once the runtime gets close to the low battery signaling time, it starts to give you battery discharged messages.

do you know how much actual runtime you get on battery? is 5 minutes accurate to what you have seen in the past? it may be time to do a runtime calibration of sorts.

can you confirm the exact model number of the UPS from the UPS itself (the little white sticker on the back or bottom of the UPS)? we can try to adjust the UPS runtime constant through hyperterminal/terminal emulation if you are comfortable doing so or we can look into doing an actual runtime calibration and discharging the UPS batteries and letting it charge up to recalcuate the correct runtime. this is more time consuming and would require the load to be brought down so that the UPS completely turns off.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

0 Likes
0
3185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

Well, we've done a RuntimeCalibration Test since 3 Days ago, and the resoult was 5 minutes Runtime.

The runtime befor was about 3 minutes, that was the reason to change the baterie pack.

At the moment, I can't look at the USV for the exact modell number, but I hope that this is also OK:

Model: Smart-UPS 3000 RM DL3
Serial Number: YS0330310483
Firmware Revision: 666.1DL3.I
Manufacture Date: 07/26/03

That is a good idea to discharge the Batteries or maybe Calibrate them.
Next Saturday we have a Desaster Recovery test and we can do anything with the USV.

Do you have a dicumentation how to do a recalibration or Discharge the baterie with the command line over a hyper terminal session?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

0 Likes
0
3185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

ok yes, i would hold off on an actual runtime calibration and we can proceed with the hyperterminal once you can confirm one thing - is this unit 3U in size? i believe it is and once you confirm, i will PM you the instructions to do the hypterterminal procedure which wont require any downtime.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

0 Likes
0
3185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

no, it is a 2U Unit, I am a little bit confused, because the description is 3U. Is it normal?

Thanks for the Documentation ๐Ÿ™‚

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

0 Likes
0
3186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 09:35 PM . Last Modified: โ€Ž2024-03-14 11:48 PM

we really need to be absolutely sure of the exact model number on the UPS so I can give you the correct instructions. i will PM you what I have.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of