Smart UPS 2200 without Network Card, only USB.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 2200 without Network Card, only USB.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:09 PM

0 Likes
4
1365
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:09 PM

Smart UPS 2200 without Network Card, only USB.

Smart UPS 2200 without Network Card, only USB.
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

0 Likes
0
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

See response to your duplicate post here

http://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/75036/esxi-...

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:09 PM

0 Likes
0
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:09 PM

Hi,

PowerChute Business Edition is not supported on VMware vMA communicating with UPS over USB. Is is supported communicating with the UPS over serial. PowerChute Business Edition Agent is supported on VMware vMA. It can be access using the web interface or through the PowerChute Server and Console but the Server and Console need to be installed on Windows OS. The Server and Console will not install on VMware vMA. 

You need to install VMware vMA and configure it with a serial port. Then install the PowerChute Agent on the vMA. 

We offer a few FAQs on this subject

FA165747 How to install PowerChute Business Edition version 9.1.x and 9.2 on VMware vMA 5.0, 5.1, 5.5, or 6.x

FA166093 How to upload - copy PowerChute Business Edition installation file from PC to VMware vMA

FA159688 Configure virtual machine shutdown on standalone VMware ESX and ESXi hosts protected by PowerChute.

I suggest downloading PowerChute Business Edition version 9.2.1 from this link FA304446

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

0 Likes
0
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

Hi,

Thanks for the reply. 

So I plugged in cable with RJ45 at the 1st end to my UPS, and another end which is serial to my VMware ESXi server, and configured the VMA settings as provided by the URL link earlier:

 http://www2.schneider-electric.com/resources/sites/SCHNEIDER_ELECTRIC/content/live/FAQS/165000/FA165...

and followed by installing the Linux Powerchute Business Edition Agent inside the VMA.

I tried both DB9 and RJ45 during installation and seems like both not working, when I browse my VMA web interface at https://:6547, it still shows that "communication lost" or "Not established".

Any idea on what's missing from my end?

Thank you.

Best regards,

Kong

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

0 Likes
0
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

Hi support,

OK now my VMware ESXi host is able to communicate with my UPS, but another weird thing:

1) Once my PowerChute agent service is up in my vMA, maybe around 2-3 minutes, my ESXi host will be auto shutdown. If I power off my vMA, it won't shutdown again. Is there any misconfiguration from vMA? I'm unable to do the troubleshooting as it will shutdown everytime I want to login to vMA web interface and check on what's going on. I can see that my vMA status "On battery" before it goes shutdown. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

0 Likes
0
1363
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:24 AM . Last Modified: ‎2024-02-29 10:08 PM

See response to your duplicate post here

http://forums.apc.com/spaces/7/ups-management-devices-powerchute-software/forums/general/75036/esxi-...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore