Smart-UPS 2200 RM - regular hum every 45 seconds

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 2200 RM - regular hum every 45 seconds
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:35 AM . Last Modified: ‎2024-03-18 04:23 AM

0 Likes
3
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:35 AM . Last Modified: ‎2024-03-18 04:23 AM

Smart-UPS 2200 RM - regular hum every 45 seconds

Hi,

I have a rack mount 2200 Smart UPS - SUA2200RMI2U

The unit was originally in the UK and now lives in Europe.

Admittedly our electricity supply is not the greatest, hence the UPS, but I have noticed that the SmartBoost is continually cutting in and out.

The LOTRANS value is set at 204v and I set the sensitivity to low but it still seems to flick in for a few seconds every minute or two. Presumably it is seeing a lower voltage than I can see reported. As far as I can see from voltage reporting that I can do the voltage rarely drops below about 220v

I believe EU supply is rated at 230v +/-6v so I would expect to see it down to around 216v anyway.

Batteries are fairly new - within the last 6 months.

Any suggestions on this ? The voltage does not seem low enough to trip the SmartBoost so presume there is another issue.

B. Rgds

John

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 2200
  • rm
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:35 AM . Last Modified: ‎2024-03-18 04:23 AM

0 Likes
0
1276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:35 AM . Last Modified: ‎2024-03-18 04:23 AM

After much hunting the issue was tracked down to a PoE wifi repeater which had an issue. Unit looked OK but clearly had a problem with the power supply

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:35 AM . Last Modified: ‎2024-03-18 04:23 AM

0 Likes
0
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:35 AM . Last Modified: ‎2024-03-18 04:23 AM

A side note - I have a domestic consumption meter I thought I would try and see if I noticed anything.

The consumption seems to jump by about 1/2 Kw whenever the UPS goes on to SmartBoost.

Even more perplexed now !

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:35 AM . Last Modified: ‎2024-03-18 04:23 AM

0 Likes
0
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:35 AM . Last Modified: ‎2024-03-18 04:23 AM

Hmmmm. Really scratching my head now.

Disconnected everything but noticed the humming still continues. Lasts about 3-4 secs every 45 seconds, regular as clockwork.

Happens even with the UPS off - just the power connected. Disconnected batteries etc but still happens the moment the power is connected even though the unit is not 'on'.

Decided to revert back to my trusty old Smart-UPS 1000 - sensitivity set to low via the rear button.

Hooked it all up and connected the power and instantly I get the dreaded hum even before I fire up the UPS. Same pattern. Just quieter than the big UPS.

Clearly something is not right round here. My Fluke shows a steady 235v tonight. Nothing to show that a Low voltage is running SmartBoost.

Guess I need to go round and disconnect the whole house tomorrow and see if something else is up.

What on earth would trigger the UPS to hum for 3-4 secs every 45 seconds ? It is not as loud as when the UPS is on full load when the power is removed.

Any suggestions appreciated.........

B. Rgds

John

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:35 AM . Last Modified: ‎2024-03-18 04:23 AM

0 Likes
0
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:35 AM . Last Modified: ‎2024-03-18 04:23 AM

After much hunting the issue was tracked down to a PoE wifi repeater which had an issue. Unit looked OK but clearly had a problem with the power supply

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore