Smart UPS 2000 Rack Mounts ---- Available Runtime has Been Exceeded

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 2000 Rack Mounts ---- Available Runtime has Been Exceeded
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:21 AM

0 Likes
13
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:21 AM

Smart UPS 2000 Rack Mounts ---- Available Runtime has Been Exceeded

These messages have been showing up in the SYSLOG and being "WALL'd" to folks online ever since
the rackmount UPS units have been installed. Has anyone seen this before and know how to resolve?

"Available runtime has been exceeded."
Feb 10 21:24:13 servername wall: [ID 254490 auth.crit] dtlocal in utmpx is not a tty

Thanks for your help.

Message was edited by: rb9819

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

0 Likes
0
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

Thank you for your replies Buzz and Erasmus.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 13
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:21 AM

0 Likes
0
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:21 AM

Could you please post the data & event logs from the network card?

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:21 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:21 AM

Could you also paste your config.ini (FTP to the card and use the "get config.ini" command to download it) and tell us what your current runtime is and load percentage?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:21 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:21 AM

Buzz & Erasmus -
Thanks for your reply. I will be back onsite next Tuesday afternoon and will be able to post the data at that time.
Thanks for the help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:21 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:21 AM

Buzz-
Once connected to the device via ssh I selected FTP to download the config.ini. It is menu driven and when I select FTP it appears to be in mode to upload. Can you tell me how I can "get" and download to local workstation the config.ini? Thank you kindly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:21 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:21 AM

Event Log:
02/15/2010 17:06:26 System: Set Date or Time.
02/14/2010 17:06:26 System: Set Date or Time.
02/14/2010 12:18:53 UPS: Passed a self-test.
02/14/2010 12:18:38 UPS: Started a self-test.
02/13/2010 17:06:26 System: Set Date or Time.
02/12/2010 17:06:26 System: Set Date or Time.
02/11/2010 17:06:28 System: Set Date or Time.
02/10/2010 17:06:28 System: Set Date or Time.
02/09/2010 17:06:29 System: Set Date or Time.
Data Log:
02/16/2010 10:05:00 210.2 211.6 208.2 7.92 34.0 60.00 100.0 218.1 71.2 27.0 75
02/16/2010 09:55:00 210.2 211.6 208.2 7.92 35.0 59.99 100.0 218.1 71.2 27.0 75
02/16/2010 09:45:00 210.2 211.6 208.2 7.92 34.0 59.99 100.0 218.1 70.1 27.0 75
02/16/2010 09:35:00 210.2 210.2 208.2 7.84 35.0 60.04 100.0 218.1 70.1 27.0 75
02/16/2010 09:25:00 210.2 210.2 208.2 7.84 34.0 60.01 100.0 218.1 71.2 27.0 75
02/16/2010 09:15:00 208.8 210.2 208.2 7.92 34.0 59.98 100.0 218.1 71.2 27.0 75
02/16/2010 09:05:00 208.8 210.2 208.2 7.84 35.0 60.01 100.0 218.1 71.2 27.0 75
02/16/2010 08:55:00 208.8 210.2 208.2 7.92 35.0 60.01 100.0 218.1 70.1 27.0 75
02/16/2010 08:45:00 208.8 210.2 208.2 7.84 34.0 59.99 100.0 218.1 70.1 27.0 75
02/16/2010 08:35:00 208.8 210.2 208.2 7.92 35.0 60.01 100.0 218.1 70.1 27.0 75
02/16/2010 08:25:00 208.8 208.8 208.2 7.92 34.0 60.01 100.0 218.1 70.1 27.0 75
02/16/2010 08:14:59 208.8 208.8 208.2 7.92 35.0 60.00 100.0 218.1 70.1 27.0

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

It might be a better idea to copy/paste ALL of the data to a .txt file and add it to your post as an attachment. That really isn't much information. Same goes for the config file, just make it an attachment.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

Generally you need to use strict FTP access as opposed to SSH terminal to be able to 'get' the files we requested.

Start an FTP session on a graphical tool and point to the card, this should allow easy drag and drop. Otherwise from a command line use ftp , then put in your login credentials. The session will then be in FTP command line mode, and you can use the get command to get the event log, data log, and config.ini.

get data.txt
get event.txt
get config.ini

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

SmartUPS 6000
NS0726006727

Yes, seeing error in syslog

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

Runtime remaining is 23 minutes.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

Generally what is your runtime on the UPS, i.e. if you log into the NMC right now and just view the Runtime, what does it say in hours/minutes? Also, it doesn't look like the low batt/batt discharge event has happened in awhile based on the UPS event logs....are you still getting these messages as of recently via e-mails from the NMC, or just syslog?

Also, can we have the exact model number and serial # on the UPS as shown from the sticker on the back/bottom of the unit?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

So you're not getting an emails about the alarms? Do you have any email alerts setup on the card?

I haven't seen the exact message "Available runtime has been exceeded" so I, at least, was hoping if you got an email alert, you could get the corresponding error code from the alert and we could look it up.

Also, that looks like the description provided by the web interface, not the model number on the white sticker on the unit itself.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

The emails have been turned off for this event via the UPS GUI. Here is an example of what is in the syslog:

Broadcast Message from root (???) on ###### Fri Feb 19 12:56:15...
"Available runtime has been exceeded." No error code shown.

I'll get the other information once I get back onsite. Thanks Buzz. BTW., this is occurring on several of our
servers.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

0 Likes
0
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:44 PM . Last Modified: ‎2024-03-14 01:20 AM

Thank you for your replies Buzz and Erasmus.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore