Smart-UPS 1500 Runtime issues, new battery?
We have a pair of Smart-UPS 1500s in our server location powering some equipment.
I noticed in Powerchute that one of the units has suddenly started complaining of insufficient runtime. At full battery charge, it was listed as 5 minutes with a 52% load. I started a Runtime Calibration, and the battery seemed to drop very quickly (at least according to the UPS's battery meter) and now at full battery charge the runtime is listed at 2 minutes and the battery meter is flashing on the UPS itself.
The other Smart-UPS 1500 shows a runtime of 15 minutes at 56% load, which seems more normal to me.
Is there any possible solution to this issue other than replacing the battery or entire UPS? The strange thing is that I BELIEVE we replaced this battery less than a year ago (but the battery replace counter was not reset). Is it possible that I have a bad UPS?
Last question - any experience using batteries other than APC-brand?
Thanks in advance!
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:28 AM
Thanks for the advice.
For the record, I appreciate the comments from both end-users and people representing APC. I understand both sides of the coin.
Thanks again.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:29 AM
The battery bar graph on the front flashes to tell you that your runtime is within 2 minutes of the low battery signaling time (the point also when anything running powerchute will be forced to shutdown), which is set to 2 minutes by default, which makes sense because powerchute is reporting 2 minutes.
If this battery is brand new, what I would suggest doing is letting it discharge completely until the UPS turns off, then it let charge back up. (So you'd want to unplug your critical equipment because we need to run the UPS down to nothing. You could use some non critical load to put on the system so it discharges faster.) There could be sort of a ghost image of the runtime left in the system, especially if you replaced the battery recently.
Once it charges back up, check that runtime again.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:29 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:29 AM
We have a pair of Smart-UPS 1500s in our server location powering some equipment.
I noticed in Powerchute that one of the units has suddenly started complaining of insufficient runtime. At full battery charge, it was listed as 5 minutes with a 52% load. I started a Runtime Calibration, and the battery seemed to drop very quickly (at least according to the UPS's battery meter) and now at full battery charge the runtime is listed at 2 minutes and the battery meter is flashing on the UPS itself.
The other Smart-UPS 1500 shows a runtime of 15 minutes at 56% load, which seems more normal to me.
Is there any possible solution to this issue other than replacing the battery or entire UPS? The strange thing is that I BELIEVE we replaced this battery less than a year ago (but the battery replace counter was not reset). Is it possible that I have a bad UPS?
Last question - any experience using batteries other than APC-brand?
Thanks in advance!
If you're certain that battery pack was replaced, there's a possibility that the "new" battery was kept stocked too long and degraded.
As to your last question I'm apparently not at liberty to publicly discuss parts and accessories other than Genuine APC-MGE parts on this particular forum.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:29 AM
Relating to using third party batteries:
Here are five reasons why you should only use a genuine APC RBC in your APC UPS:
•Use of a non-APC battery may result in lower run time, damage the UPS, create a hazardous condition, or void UL, CSA, VDE, and other safety certifications on the UPS.
•Use of a non-APC battery will void APC's Equipment Protection Policy.
•APC recycles used batteries and almost 100% of the battery lead content is reused, protecting the environment. With each purchase of a genuine APC RBC, you get free freight back to APC for proper disposal of your old batteries (currently available in USA only, excluding RBC14 and Symmetra batteries.)
•APC provides a 1-year warranty on each Replacement Battery Cartridge.
•APC supplies the appropriate instructions for your UPS, along with any needed wires and connectors. All connections are made with high current gas-tight crimps for high reliability.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:29 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:29 AM
Relating to using third party batteries:
Here are five reasons why you should only use a genuine APC RBC in your APC UPS:
•Use of a non-APC battery may result in lower run time, damage the UPS, create a hazardous condition, or void UL, CSA, VDE, and other safety certifications on the UPS.
•Use of a non-APC battery will void APC's Equipment Protection Policy.
•APC recycles used batteries and almost 100% of the battery lead content is reused, protecting the environment. With each purchase of a genuine APC RBC, you get free freight back to APC for proper disposal of your old batteries (currently available in USA only, excluding RBC14 and Symmetra batteries.)
•APC provides a 1-year warranty on each Replacement Battery Cartridge.
•APC supplies the appropriate instructions for your UPS, along with any needed wires and connectors. All connections are made with high current gas-tight crimps for high reliability.
Most state requires battery dealer to accept used batteries and many are willing to accept them even if you didn't buy it from them.
1 year warranty is also provided by many third party suppliers.
If you don't want to do research before clicking "Buy it" then buying from APC at their price is the best idea, but if you're willing to do a bit of digging around, third party batteries offer great values.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:29 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:29 AM
KVAr,
You are correct. This is in APC's knowledge base article/policy of why we recommend APC batteries.
We are all entitled to our own opinion and reasons. :8}
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:29 AM
KVAr,
You are correct. This is in APC's knowledge base article/policy of why we recommend APC batteries.
We are all entitled to our own opinion and reasons. :8}
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:28 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:28 AM
APC has never manufactured batteries. So, all you can find on the market is batteries labeled as APC batteries by stickers. But price is too high "for the stickers".
Most important: when batteries was manufactured.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:28 AM
Yes, I am an APC employee and representing APC's opinion/policy on the subject.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:28 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:28 AM
I take the description of this group literally.
"Welcome to APC's discussion forums, home to our on-line *peer-to-peer* support community"
Calling APC tech support and viewing the official knowledge base are the best ways to get the APC orthodox instructions/procedure/policies. however this being a peer to peer support group, what is the point in duplicating what APC staff would say?
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:28 AM
KVar,
While I completely agree with you on the Peer To Peer aspect of the discussion boards, how many posters/users out there are like yourself that not only a) have the knowledge behind the scenes of APC products without ever having worked for, or represented APC, or b) have the time to carouse through the APC Forums boards to find answers to questions for which you may be looking for additional information?
Yes the call center is always busy, and yes every person on the phones with whom you speak may have an added two cents or another workaround in which they've seen.
Yes email support takes at least 24 hours for a reply, which sometimes infuriates customers, but then again, why not call in?
And YES these boards are Peer to Peer. I will not argue that. But as it is hosted and represented on the APC Website. APC Moderators, Admins and any level of APC Tech Support are capable of maintaining and moderating this board and posting information to users who are looking for a workaround or simply looking for help from a Technical Support Group.
If people do not want to call in, email, or search the Knowledge Base, and information is pasted in here pertaining to APC documentation as posted by an APC Moderator, that's fine.
If you want to add any extra additional information to that, that's fine as well.
But since you and I have had a few bumps in the past, I'm asking you to PLEASE just disregard information that you don't agree with that comes from APC Documentation. Feel free to clarify or express your opinion on it, but don't take it out on someone like Angela (who for the record, is going nowhere and will become as much of a cornerstone of these boards as I) who is trying to provide Tech Support for customers who're looking for information, whether you or they find it as helpful or not.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:28 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:28 AM
"If you want to add any extra additional information to that, that's fine as well."
Are you sure? I responded to a user who asked a legitimate question about sourcing after market batteries. That portion of his question and my response to him magically vanished.
Did you delete it?
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:28 AM
I highly doubt it. I've never had a problem with your information pertaining to third party batteries. In fact, it's become beneficial for our legacy UPS's which we do not have replacement batteries for anymore.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:28 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:28 AM
APC has never manufactured batteries. So, all you can find on the market is batteries labeled as APC batteries by stickers. But price is too high "for the stickers".
Most important: when batteries was manufactured.
Some APC packs look the same, but have different RBC numbers depending on if it's based on 7.2Ah or 9Ah.
Panasonic, Yuasa and CSB make good batteries. So far, Universal has been alright. Some unknown Chinese manufacturers, I'm not so certain about.
To APC's credit there are some advantages to buying OEM APC battery pack directly from APC. They won't slap their name on garbage batteries, so even though batteries are made by someone else, they've been pre-screened for quality as they have to pass APCs quality expectations and I would think that they'll make sure you won't receive some stagnant inventory that's gone stale.
There's more to refurbishing UPSs than loading batteries and claiming it works. A properly refurbished UPS unit should meet or exceed factory runtime specs under maximum load.
The battery is more or less the engine, with the rest of the UPS being the power train.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:30 AM . Last Modified: 2024-03-08 02:28 AM
Thanks for the advice.
For the record, I appreciate the comments from both end-users and people representing APC. I understand both sides of the coin.
Thanks again.