I would appreciate some advice before I purchase new batteries for this unit.
For several weeks I have had the red battery warning light and beep for 1 minute every 5 hours indicating battery replacement. As this is non critical application and I have not had spare funds I have ignored the warning until I could afford to replace the batteries. However events have progressed which has now forced me to do something.
After returning one evening I opened my workshop door the UPS was beeping constantly and the room was hot and full of the smell of acid. When I touched the UPS it was very hot. I shut everything down and removed the UPS to the garage to cool down.
I have now had chance to open the case and inspect the batteries both have which have swollen and stuck together.
My question therefore is. Do you think the UPS control circuits have been damaged as a result of this overcharging as I assume this is what has happened or is the charging circuit robust enough to cope with this for several hours?
Is there a way to run some tests to see if the system is still operational without the batteries or temporarily reconnecting the old batteries?
I really don't want to spend circa £90 on two replacement batteries only to find the UPS itself has been damaged. The unit itself is probably too big for the task and I would perhaps try and purchase a smaller replacement and put the £90 towards an new UPS.
I am aware that I am asking people to Crystal Ball Gaze and the stock answer is to send it to a service department for testing, but perhaps people on this forum have experienced similar overcharging with no long term damage to the UPS and can give real world experience.
Many thanks
John
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:33 PM . Last Modified: 2024-03-06 11:57 PM
Hi John,
It's hard to say whether or not a failed and run-away charging circuit destroyed the batteries or a failure in one or both batteries was the cause of the overheating and venting.
In theory, if you had a digital volt meter you could check the battery voltage and get a rough idea of whether or not the charging circuit was working. The two 12volt batteries when connected in series should be floating at about +13.6 VDC each, give or take, or about +27.2 for the pair. Any higher than that and the charger would cook the batteries over time.
How old were the batteries that were installed? If not too old, say less than three years, I'd bet the battery charging circuit took off on you and cooked the batteries. If the UPS is older than five or six years, I'd invest in a new, appropriately sized, model because the battery management circuitry has improved considerably.
Good luck!
Joe
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:33 PM . Last Modified: 2024-03-06 11:57 PM
Hi John,
It's hard to say whether or not a failed and run-away charging circuit destroyed the batteries or a failure in one or both batteries was the cause of the overheating and venting.
In theory, if you had a digital volt meter you could check the battery voltage and get a rough idea of whether or not the charging circuit was working. The two 12volt batteries when connected in series should be floating at about +13.6 VDC each, give or take, or about +27.2 for the pair. Any higher than that and the charger would cook the batteries over time.
How old were the batteries that were installed? If not too old, say less than three years, I'd bet the battery charging circuit took off on you and cooked the batteries. If the UPS is older than five or six years, I'd invest in a new, appropriately sized, model because the battery management circuitry has improved considerably.
Good luck!
Joe