Smart-UPS 1000 (with AP9606 NMC) - how to calculate the energy cost ?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 1000 (with AP9606 NMC) - how to calculate the energy cost ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:14 PM . Last Modified: ‎2024-03-15 04:13 AM

0 Likes
6
1751
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:14 PM . Last Modified: ‎2024-03-15 04:13 AM

Smart-UPS 1000 (with AP9606 NMC) - how to calculate the energy cost ?

Hello all,

I have a Smart-UPS 1000 with AP9606 NMC for my server.

I use PowerChute Network Shutdown to shutdown my ESX when I have a power failure.

I will need to calculate the energy cost but I don't know how to calculate this ! With my previously UPS wired toUSB, I had an estimation with Powerchute business edition.

So, how to calculate the energy cost (estimation) based on UPS load ? Do you have a formula ? A software ? Other ?

Below, the detail of my UPS :

Describes utility power status
    Input Voltage: 244.8 VAC
    Input Frequency: 50.00 Hz
    Maximum Line Voltage: 243.3 VAC
    Minimum Line Voltage: 236.1 VAC

Describes output power status
    Output Voltage: 243.3 VAC
    Output Frequency: 50.00 Hz
    Load Power: 019.5 % Watts

Describes battery status
    Battery Capacity: 100.0 %
    Runtime Remaining: 0101 Minutes
    Battery Voltage: 27.40 VDC

 

And the server power supply is a 460 Watts.

Thanks & regards,

Romain

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 12:14 PM . Last Modified: ‎2024-03-15 04:12 AM

0 Likes
0
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:14 PM . Last Modified: ‎2024-03-15 04:12 AM

Hello,

Ok, thanks for your help ! I'll think about it !

Best regards,

Romain

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:14 PM . Last Modified: ‎2024-03-15 04:13 AM

0 Likes
0
1750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:14 PM . Last Modified: ‎2024-03-15 04:13 AM

What do you mean by energy cost?

The amount used by the server, the UPS of the whole system?

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:14 PM . Last Modified: ‎2024-03-15 04:13 AM

0 Likes
0
1750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:14 PM . Last Modified: ‎2024-03-15 04:13 AM

Hello Gavan,

My UPS is only used by my server.

With the UPS statistics, I would like to estimate the number of watts used by the server and deduce the number of KWh.

Finally, I would like to know the energy consumed by the server (estimation). I think that maybe with the load and other information from the UPS, I can estimate this consumption.

 

Thanks & regards,

Romain

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:14 PM . Last Modified: ‎2024-03-15 04:13 AM

0 Likes
0
1750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:14 PM . Last Modified: ‎2024-03-15 04:13 AM

Hi Romain,

Sorry, I just realised you have an SNMP web card and not an NMC that type of card is probably close to 15/20 years old and well before my time. 

If you can log into it and find the Amps used then it's:

Voltage * Amps = Watts

Watts / 1000 = KW

KW * Unit cost of electricity = Cost per Hour

Cost per Hour * Runtime = Cost

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:14 PM . Last Modified: ‎2024-03-15 04:12 AM

0 Likes
0
1752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:14 PM . Last Modified: ‎2024-03-15 04:12 AM

Hello Gavan,

Thanks for your answer !

Unfortunately I can't find this information.

here is the information I have :

Internal Temperature: 033.7 Degrees Celsius
_
   Describes utility power status
  Input Voltage: 243.3 VAC
  Input Frequency: 50.00 Hz
  Maximum Line Voltage: 244.8 VAC
  Minimum Line Voltage: 236.1 VAC
_
   Describes output power status
  Output Voltage: 243.3 VAC
  Output Frequency: 50.00 Hz
  Load Power: 018.2 % Watts
_
   Describes battery status
  Battery Capacity: 100.0 %
  Runtime Remaining: 0098 Minutes
  Battery Voltage: 27.27 VDC
  Number of External Batteries: 000
  Self-Test Result: Passed
  Self-Test Date: UNKNOWN
  Calibration Result: Passed
  Calibration Date: UNKNOWN
_
   About UPS
  Model: Smart-UPS 1000
  Firmware Revision: 652.13.I
  Manufacture Date: 07/14/07
  Serial Number: XXXXX

 

I can't do anything with this information ?

 

Thanks for your help !

Best regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 12:14 PM . Last Modified: ‎2024-03-15 04:12 AM

0 Likes
0
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:14 PM . Last Modified: ‎2024-03-15 04:12 AM

Your best bet might be to add an external power monitoring socket in line with the UPS outlet.

Personally I've used a few TP-Link HS110s but there is dozens of similar devices on amazon, your other option is to work out it out based on the load taking into account power factor and efficiency but that would neither be worth the effort nor would it be accurate. 

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 12:14 PM . Last Modified: ‎2024-03-15 04:12 AM

0 Likes
0
1750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 12:14 PM . Last Modified: ‎2024-03-15 04:12 AM

Hello,

Ok, thanks for your help ! I'll think about it !

Best regards,

Romain

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore