Smart-UPS 1000 RM Battery capacity problem

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 1000 RM Battery capacity problem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:21 AM . Last Modified: ‎2024-03-12 04:32 AM

0 Likes
5
1184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:21 AM . Last Modified: ‎2024-03-12 04:32 AM

Smart-UPS 1000 RM Battery capacity problem

Hi!

I have Smart-UPS 1000 RM

From time to time "battery capacity" suddenly falls down from 100% to 3-7%, but the battery voltage seems not to be changed (27, 67V).... as well as output load.

What can cause such a strange operation?

Thanx in advance

datetimeVminVmaxVoutIout%Wout Freq%CapVbat TupsC%VAout
12/17/2013 06:02:54 221.7 226.0 223.2 0.58 20.8 50.00 84.0 27.67 17.5 20.8
12/17/2013 05:52:54 220.3 224.6 223.2 0.58 21.4 50.00 77.0 27.67 17.5 20.8
12/17/2013 05:42:55 220.3 224.6 221.7 0.58 21.4 50.00 70.0 27.67 16.6 21.4
12/17/2013 05:32:55 220.3 223.2 221.7 0.61 21.4 50.00 63.0 27.67 16.6 20.8
12/17/2013 05:22:55 218.8 226.0 221.7 0.60 21.4 50.00 56.0 27.67 16.6 21.4
12/17/2013 05:12:55 220.3 224.6 224.6 0.57 20.8 50.00 49.0 27.67 16.6 20.8
12/17/2013 05:02:55 220.3 227.5 221.7 0.59 20.8 50.00 42.0 27.67 16.6 21.4
12/17/2013 04:52:55 220.3 223.2 223.2 0.58 20.8 50.00 35.0 27.67 16.2 21.4
12/17/2013 04:42:55 220.3 224.6 221.7 0.58 20.8 50.25 28.0 27.67 17.1 20.8
12/17/2013 04:32:55 221.7 226.0 221.7 0.58 20.8 50.00 21.0 27.67 18.0 21.4
12/17/2013 04:22:55 221.7 226.0 224.6 0.58 20.8 50.00 14.0 27.67 18.0 20.8
12/17/2013 04:12:55 221.7 224.6 223.2 0.58 20.8 50.00 7.0 27.67 17.5 20.8
12/17/2013 04:02:55 221.7 226.0 223.2 0.58 20.8 50.00 100.0 27.67 17.5 20.8
12/17/2013 03:52:55 221.7 224.6 223.2 0.58 21.4 50.00 100.0 27.67 17.5 20.8
12/17/2013 03:42:55 220.3 224.6 223.2 0.60 21.4 50.00 100.0 27.67 16.6 20.8
12/17/2013 03:32:55 220.3 224.6 223.2 0.59 20.8 50.00 100.0 27.67 16.6 20.8
12/17/2013 03:22:55 220.3 226.0 224.6 0.60 20.8 50.00 100.0 27.67 16.6 21.4
12/17/2013 03:12:55 220.3 224.6 223.2 0.60 20.8 50.25 100.0 27.67 16.6 21.4
12/17/2013 03:02:55 218.8 224.6 223.2 0.58 20.8 50.00 100.0 27.67 16.2 20.8
12/17/2013 02:52:55 218.8 223.2 218.8 0.61 21.4 50.25 100.0 27.67 16.6 20.8
12/17/2013 02:42:54 218.8 224.6 220.3 0.59 21.4 50.00 100.0 27.67 17.5 21.4
12/17/2013 02:32:54 220.3 224.6 221.7 0.61 20.8 50.00 100.0 27.67 18.0 20.8

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:21 AM . Last Modified: ‎2024-03-12 04:32 AM

0 Likes
0
1184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:21 AM . Last Modified: ‎2024-03-12 04:32 AM

Hi

just try to make calibration for your ups

log in to your ups , you will find UPS CALIBRATION startups calibration but make sure your battery capacity is 100%

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:21 AM . Last Modified: ‎2024-03-12 04:32 AM

0 Likes
0
1184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:21 AM . Last Modified: ‎2024-03-12 04:32 AM

Do you have the event log for this same time period please? That'd be helpful.

How old is the battery? If it is the original battery, we could tell based on the first several digits of the UPS serial number to see how old it is. My first thought is the UPS did a self test and I suspect it is an aging battery that cannot support the UPS load any longer. I need the event log and age though to verify my theory.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:21 AM . Last Modified: ‎2024-03-12 04:32 AM

0 Likes
0
1184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:21 AM . Last Modified: ‎2024-03-12 04:32 AM

While I agree with you for the most part, you could still have some type of battery issue and the voltage shows as good, especially if the load on the UPS/battery is not large.

What I am seeing is that your UPS is very new as you said, less than a year old. I also see the UPS switching back and forth frequently to and from battery operation. I think we need to figure out what that is happening. I don't see any obvious power events in the data log (which logs every 10 minutes). The first thing you could do is adjust your sensitivity/line quality. Lowering these settings a notch will make the UPS less sensitive to power issues. We can see if this makes a difference. I am assuming this is a 230V model UPS but you seem to be feeding it 220V which should be OK..

Do you know what the exact SKU is of your UPS? It appears to be a 230V model as I noted. If you have a newer version of firmware on your Network Management Card (v6.0.6) which is green or white, you can see the exact SKU under About->UPS. If you have an older version that is blue and white, just tell me what you see under UPS->About for firmware versions and ID and I can maybe tell by that if you cannot check the sticker on the back of your UPS to verify.

If lowering the sensitivity does not at least help or make a difference in the amount of transfers back and forth to battery, then I'll want to know that firmware to see if there are any issues we've identified with hysteresis that cause too many transfers (just as an example of what else could be a problem).

What is the attached load on the UPS? Servers, routers, etc?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:21 AM . Last Modified: ‎2024-03-12 04:32 AM

0 Likes
0
1184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:21 AM . Last Modified: ‎2024-03-12 04:32 AM

While I agree with you for the most part, you could still have some type of battery issue and the voltage shows as good, especially if the load on the UPS/battery is not large.

What I am seeing is that your UPS is very new as you said, less than a year old. I also see the UPS switching back and forth frequently to and from battery operation. I think we need to figure out what that is happening. I don't see any obvious power events in the data log (which logs every 10 minutes). The first thing you could do is adjust your sensitivity/line quality. Lowering these settings a notch will make the UPS less sensitive to power issues. We can see if this makes a difference. I am assuming this is a 230V model UPS but you seem to be feeding it 220V which should be OK..


I'm afraid to lower sensitivity settings because it will increase "high transfer voltage" parameter. In that case, voltage for server (load) protected by ups can be out of band.


Do you know what the exact SKU is of your UPS? It appears to be a 230V model as I noted. If you have a newer version of firmware on your Network Management Card (v6.0.6) which is green or white, you can see the exact SKU under About->UPS. If you have an older version that is blue and white, just tell me what you see under UPS->About for firmware versions and ID and I can maybe tell by that if you cannot check the sticker on the back of your UPS to verify.


About UPS
Model:Smart-UPS 1000 RM
Serial Number:AS1306125428
Firmware Revision:669.19.I
Manufacture Date:02/07/13

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:21 AM . Last Modified: ‎2024-03-12 04:32 AM

0 Likes
0
1184
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:21 AM . Last Modified: ‎2024-03-12 04:32 AM

It will increase the high transfer voltage parameter yes but depending on the piece of equipment, this is likely not out of range. A UPS is designed to protect IT type equipment and it would not allow too high or too low of a voltage through to damage any of your average type of equipment. Do you have a specification on the type of equipment where it says it cannot accept a voltage below or above a certain amount specifically? This UPS also has boost and trim (Automatic Voltage Regulation) functionality.

This seems like an older generation UPS, perhaps SUA1000RMI2U or similar is my guess based on the information you provided. I think there is something happening on the input that is causing it to constantly transfer to and from battery and our typical remedy is to lower the sensitivity. I believe that is causing the battery capacity issue. Beyond moving the UPS to a different circuit to try, the next step is to try and adjust the sensitivity just to see.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:21 AM . Last Modified: ‎2024-03-12 04:32 AM

0 Likes
0
1185
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:21 AM . Last Modified: ‎2024-03-12 04:32 AM

Hi

just try to make calibration for your ups

log in to your ups , you will find UPS CALIBRATION startups calibration but make sure your battery capacity is 100%

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore