Hi Everyone,
I have two UPS SU3000RMXL backups and each unit is connected to three external batteries. I had a power outage yesterday and I am quite concerned that it took one of the UPS units 8 hrs to reach a full charge (where the other unit charged more quickly). The powerload on both units is the same (three bars on the display).
Why does the UPS take a long time to charge?
Thank you,
D
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:32 PM . Last Modified: 2024-03-15 03:58 AM
The recharge rate of the batteries is roughly 10x the discharge. So it is normal to have an 8 hour recharge. Additionally, the batteries will charge to 80% rather quickly but it is the last 20% that takes the time. If the batteries are more than 3 years old you might want to consider getting the batteries replaced and the unit recalibrated.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 PM . Last Modified: 2024-03-15 03:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 PM . Last Modified: 2024-03-15 03:58 AM
Hello,
Is it OK to install 6 external batteries to one "command unit" (aka SU3000RMXL)?
Thanks,
D
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 PM . Last Modified: 2024-03-15 03:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 PM . Last Modified: 2024-03-15 03:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 PM . Last Modified: 2024-03-15 03:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 PM . Last Modified: 2024-03-15 03:58 AM
Its also advised that you use batteries that are generally around the same age too. Same age being roughly within 1 year of one another. ie. Don't mix 3-4 year old batteries with new ones.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 PM . Last Modified: 2024-03-15 03:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 PM . Last Modified: 2024-03-15 03:58 AM
Hi,
Thank you for your post. Could you please explain why the same UPS unit (same setup of three batteries) charged much quicker? Is it normal for 3 external batteries + 3000XL take approx 8 hrs to charge?
Thank you,
D
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 PM . Last Modified: 2024-03-15 03:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 PM . Last Modified: 2024-03-15 03:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 PM . Last Modified: 2024-03-15 03:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 PM . Last Modified: 2024-03-15 03:58 AM
Hello,
How old are the two units? Are they both the same age or is one older than the other?
Do they also have the same exact type of batteries, or does one have larger extended batteries than the other?
A Smart UPS, by itself with no external batteries, will take about 3-5 hours to recharge fully. Each extended run battery could add upwards of 2-3 hours, depending on the size, to recharge fully. If the unit with three extended batteries recharged in 8 hours, this sounds normal.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 PM . Last Modified: 2024-03-15 03:58 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:31 PM . Last Modified: 2024-03-15 03:58 AM
That shouldn't be a problem. Just keep in mind that you will have a very long charge time as stated in the previous posts. Also, If you are using this UPS to gracefully shutdown any computers, you will want to make sure you program the UPS to know how many external battery are attached so it will calculate the correct runtime. This would be done through whatever PowerChute software you are currectly using. If you are not using this UPS with PowerChute software then don;t worry about programming the UPS with the number of batteries.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:32 PM . Last Modified: 2024-03-15 03:58 AM
The recharge rate of the batteries is roughly 10x the discharge. So it is normal to have an 8 hour recharge. Additionally, the batteries will charge to 80% rather quickly but it is the last 20% that takes the time. If the batteries are more than 3 years old you might want to consider getting the batteries replaced and the unit recalibrated.
Link copied. Please paste this link to share this article on your social media post.