I got a site wiring fault warning this morning that lasted 3 seconds. Could this be caused by a power sag? Last week I turned the sensitivity to medium because I was getting a power failed every morning for several seconds. After that no more power failed, but this week I get a Site Wiring Fault in the morning for 3 seconds. Any ideas?
Mike
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:19 AM . Last Modified: 2024-03-08 12:19 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:19 AM . Last Modified: 2024-03-08 12:19 AM
I got a site wiring fault warning this morning that lasted 3 seconds. Could this be caused by a power sag? Last week I turned the sensitivity to medium because I was getting a power failed every morning for several seconds. After that no more power failed, but this week I get a Site Wiring Fault in the morning for 3 seconds. Any ideas?
Mike
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:19 AM . Last Modified: 2024-03-08 12:19 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:19 AM . Last Modified: 2024-03-08 12:19 AM
Thanks, I'm going to try moving the UPS to another circuit. I update to Business Edition 7.0.5 last week, plus changed the sensitivity of the UPS to medium. Related?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:19 AM . Last Modified: 2024-03-08 12:19 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:19 AM . Last Modified: 2024-03-08 12:19 AM
Moving the UPS will be a good identifier if the first circuit is at fault. Updating Business Edition could rule out the erroneous factor. Sensitivity will not have anything to do with a Site Wiring Fault on our SmartUPS/BackUPS line.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:19 AM . Last Modified: 2024-03-08 12:19 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 06:19 AM . Last Modified: 2024-03-08 12:19 AM
I got a site wiring fault warning this morning that lasted 3 seconds. Could this be caused by a power sag? Last week I turned the sensitivity to medium because I was getting a power failed every morning for several seconds. After that no more power failed, but this week I get a Site Wiring Fault in the morning for 3 seconds. Any ideas?
Mike