Silcon SL60KH: Behaviour on utility power restored

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Silcon SL60KH: Behaviour on utility power restored
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 03:41 AM . Last Modified: ‎2024-03-19 01:41 AM

0 Likes
4
654
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:41 AM . Last Modified: ‎2024-03-19 01:41 AM

Silcon SL60KH: Behaviour on utility power restored

What would happen in situation if Silcon SL60KH UPS runs on batteries and servers are shutdowned gracefully and then while UPS is still running utilty power is restored.

Will UPS restart itself. In this way servers will be booted up, but all other equipment will have unecessary restart. Which PCNS settings at UPS and servers are relevant to make this work ?

Can UPS use 'Wake On LAN' to boot up servers via IP in situation described above? If this is possible what are the settings which have to be made on servers both on BIOS and operating system level (driver, power management configuration, ...).

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 03:41 AM . Last Modified: ‎2024-03-19 01:41 AM

0 Likes
0
656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:41 AM . Last Modified: ‎2024-03-19 01:41 AM

Hi Darko,
To turn load on, ie to reapply power, please use switched pdu.

Message was edited by: e7e5

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 4
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-26 03:41 AM . Last Modified: ‎2024-03-19 01:41 AM

0 Likes
0
656
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:41 AM . Last Modified: ‎2024-03-19 01:41 AM

Darko,

Here's the response I received from one of our 3-Phase Engineers:

To ensure your UPS will turn back on when power is restored, you must ensure that the' Auto Start' function of your Silcon is enabled. To verify this, please go into your user parameters by hitting the '#' key on your keypad. Then scroll through this menu until you see 'Auto Start'. If it is set to anything other than 'YES', then press the 'C' key until it does. Then hit the '#' key again to store the 'YES' value.


Keep in mind that there is NO Wake-On LAN support for any APC Networked Devices. It all points to the server BIOS settings and whether or not the last state of the server is set to restore itself when power is restored to it.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 03:41 AM . Last Modified: ‎2024-03-19 01:41 AM

0 Likes
0
654
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:41 AM . Last Modified: ‎2024-03-19 01:41 AM

Hi,

Thank you very much for support.

Still is not clear to me, what happens in situation when servers are shutdowned, UPS (Silcon) still operates on batteries and in that moment utility power is restored.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-26 03:41 AM . Last Modified: ‎2024-03-19 01:41 AM

0 Likes
0
654
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:41 AM . Last Modified: ‎2024-03-19 01:41 AM

Hi Darko,

After everything's shutdown, the UPS will remain on battery unless you log in remotely and power it off. After utility power returns (if still on battery, not fully discharged), it runs a prolonged "Self Test" as I like to call it which allows it to temporarily cut power, cycle between on-battery and on-line, then provide power again to its output.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 03:41 AM . Last Modified: ‎2024-03-19 01:41 AM

0 Likes
0
657
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:41 AM . Last Modified: ‎2024-03-19 01:41 AM

Hi Darko,
To turn load on, ie to reapply power, please use switched pdu.

Message was edited by: e7e5

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of