Hi all.
I've just replaced an incompatible AP9630 card with an AP9617 which I'm told is the right card for this UPS. Even that is a bit iffy since the page for the AP6017 says the AP6930 is its replacement... Anyway, I've configured it on the lan and am able to log in to it. However, when I access the monitoring page I get a message saying that it's not a recognised UPS and that I need an APP file.
I presume it's related to a firmware update for the card as I've found some other threads about similar issues but I can't even be sure I'm finding the right download page for the UPS as it's quite an old model and DP320E doesn't even seem to come up in searches. I've looked at the [download page for the AP6917|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9617&tab=software] card but there's an awful lot of stuff there and I'm not sure what if anything I need.
Any advice please?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:41 AM . Last Modified: β2024-03-19 12:39 AM
sorry, i must have missed your previous response.
i just noticed, you are already at AOS 2.6.4 - why are you trying to put 2.0.2 on it? you should be attempting to put 3.7.3 on it. and yes the device account does not have permission to do this.
i found that this would happen to me and it was actually my VPN client service blocking me even though I was not using it at the time but the service was still active.
anyways, you can do it over Xmodem it will just be really slow. you'd send over AOS 3.7.3 then dp3e app 3.7.2.
directions for XMODEM should be in the same document i sent you if you want to try it but it still appears the FTP data port is blocked on the computers or network to me. π
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:41 AM . Last Modified: β2024-03-19 12:39 AM
hello,
AP9630 replaces AP9617 for all applications EXCEPT for your UPS since it has been discontinued for several years now.
You need the dp3e app.
Here is how to get it:
1.) Go here -> http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9617&tab=software
2.) You want this file: SFDP3E372
3.) Refer to http://www.apc.com/site/support/index.cfm/faq/ and knowledge base FA156047 if you need help updating after you download the file.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:41 AM . Last Modified: β2024-03-19 12:39 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:41 AM . Last Modified: β2024-03-19 12:39 AM
Thanks for that. I tried updating over the lan but it complained after some time that it couldn't connect. I'm going to visit the site with a laptop and do it locally as I imagine there might be some vlan issue or firewalling going on.
Is it possible to save the old firmware off the card before updating? I've been asked to ensure a rollback plan is in place. π
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:41 AM . Last Modified: β2024-03-19 12:39 AM
unfortunately no, but i can always get you what you need.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:41 AM . Last Modified: β2024-03-19 12:39 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:41 AM . Last Modified: β2024-03-19 12:39 AM
I tried the firmware update directly (network cable back to back with the monitoring card) but no success. Log below:
NMC Upgrade Tool v1.2
American Power Conversion Network Management Card AOS v3.7.3
+(c) Copyright 2004 All Rights Reserved Silcon DP300E Series APP v3.7.2+
Warning: User name and passord information will displayed
to the screen in clear text.
IP Address of target to upgrade: 10.67.2.18
User Name: apc
Password: (blanked out)
You have entered:
IP Address: 10.67.2.18
Username: apc
Password: (blanked out)
+1: Continue with upgrade+
+2: Enter new parameters+
+3: Quit+
Action: 1
Starting Upgrade to 10.67.2.18.
Checking network connection ... OK
Testing login ... OK
Checking version information ... OK
Attempting to log in to 10.67.2.18 ... OK
Loading OS, please wait ... Firmware download failed.
Attempting to log in to 10.67.2.18 ...
Could not log in to 10.67.2.18.
Upgrade Summary
Encountered 1 failures during upgrade.
View 'result.txt' for details
results.txt shows:
Using AOS file : AOS = apc_hw02_aos_373.bin
Using Application file: APP = apc_hw02_dp3e_372.bin
Checking network connection ... Checking version information ...
*************** Next **************
Before Upgrading the NMC the AOS is: ΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓΓPΓ²Γ
* Detected early version, two AOS upgrades required
Attempting to log in to 10.67.2.18 ... Log in sucessful
Loading OS, please wait ... Firmware download failed.
Attempting to log in to 10.67.2.18 ...
Could not log into 10.67.2.18.
Not all Network Management Cards were upgraded successfully:
+10.67.2.18: Could not log into the Management Card's FTP server.+
Encountered 1 failures during upgrade.
I checked the card's logs and it shows me logging on to the web console with the same username and password successfully, then the failures with the FTP connection.
+10/03/2012 09:11:21 System: Web user 'apc' logged in from 10.67.2.207.+
+10/03/2012 09:10:42 System: File transfer failed.+
+10/03/2012 09:09:25 System: FTP user 'apc' logged in from 10.67.2.207.+
+10/03/2012 09:09:25 System: FTP user 'apc' logged out from 10.67.2.207.+
+10/03/2012 09:08:10 System: FTP user 'apc' logged in from 10.67.2.207.+
+10/03/2012 09:08:10 System: FTP user 'apc' logged out from 10.67.2.207.+
+10/03/2012 09:08:10 System: FTP user 'apc' logged in from 10.67.2.207.+
+10/03/2012 09:07:49 System: Web user 'apc' logged out from 10.67.2.207.+
+10/03/2012 09:07:42 System: Web user 'apc' logged in from 10.67.2.207.+
I checked and FTP is enabled on port 21, but there's little else to be configured. π
Thanks again for your help picKed. π
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:41 AM . Last Modified: β2024-03-19 12:39 AM
i'd suggest just using the .bin files you extracted and trying FTP manually. i also wonder if it is possible that if on your computer, the FTP data port is blocked. i have had that issue before and the symptoms are that you can log in via FTP but any data transfers are blocked.
are you familiar with FTPing manually, such as with Windows command prompt?
instructions are here -> http://www.apc.com/site/support/index.cfm/faq/ -> search for FA156047 and follow NMC1 instructions for manual FTP.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:41 AM . Last Modified: β2024-03-19 12:39 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:41 AM . Last Modified: β2024-03-19 12:39 AM
Tried it manually, from a different network machine (a server which I know isn't firewalled), but with similar results.
C:\Temp\apc>ftp 10.67.2.18
Connected to 10.67.2.18.
+220 AP9617 Network Management Card AOS v2.6.4 FTP server ready.+
User (10.67.2.18:(none)): apc
+331 User name okay, need password.+
Password:
+230 User logged in, proceed.+
ftp> bin
+200 TYPE Command okay.+
ftp> put apc_hw02_aos_202.bin
+200 PORT Command okay.+
+150 File status okay; about to open data connection.+
I left it and it stayed on that for 10 minutes. Resource monitor showed no traffic to the UPS from ftp or cmd. I aborted and had a look at the log on the UPS and that seems to confirm it failed after a minute and a half (timeout period?).
+10/05/2012 13:28:35 System: FTP user 'apc' logged out from 10.6.20.88.+
+10/05/2012 13:20:07 System: File transfer failed.+
+10/05/2012 13:18:37 System: FTP user 'apc' logged in from 10.6.20.88.+
I tried changing to another port (5050 for the record) but that behaved the same way.
I also tried with the "device" account, but that didn't work either, although with a different error. I presume "device" doesn't have the rights to mess with the firmware. π
C:\Temp\apc>ftp 10.67.2.18
Connected to 10.67.2.18.
+220 AP9617 Network Management Card AOS v2.6.4 FTP server ready.+
User (10.67.2.18:(none)): device
+331 User name okay, need password.+
Password:
+230 User logged in, proceed.+
ftp> bin
+200 TYPE Command okay.+
ftp> put apc_hw02_aos_202.bin
+200 PORT Command okay.+
+550 STOR requested action not taken.+
ftp>
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:41 AM . Last Modified: β2024-03-19 12:39 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:41 AM . Last Modified: β2024-03-19 12:39 AM
No other suggestions? Can I do the firmware update via the serial connection? I haven't tried that yet but I'm not sure if it's possible.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:41 AM . Last Modified: β2024-03-19 12:39 AM
sorry, i must have missed your previous response.
i just noticed, you are already at AOS 2.6.4 - why are you trying to put 2.0.2 on it? you should be attempting to put 3.7.3 on it. and yes the device account does not have permission to do this.
i found that this would happen to me and it was actually my VPN client service blocking me even though I was not using it at the time but the service was still active.
anyways, you can do it over Xmodem it will just be really slow. you'd send over AOS 3.7.3 then dp3e app 3.7.2.
directions for XMODEM should be in the same document i sent you if you want to try it but it still appears the FTP data port is blocked on the computers or network to me. π
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:41 AM . Last Modified: β2024-03-19 12:38 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:41 AM . Last Modified: β2024-03-19 12:38 AM
Right, had another attempt today. Login via serial, go to do the transfer, switch speeds to 38400, fail.
Try it again, same issue. After switching speeds it prompts me to start the transfer, I do so, and it quickly racks up 10 "unexpected response" errors then fails.
Tried at 2400, and it works, although of course it's going to take 2 hours to transfer the AOS. Cancel that.
Tried at 19200, fail.
Tried at 9600, works. OK, sure, 40 minutes but I'll live.
Came back 15 minutes later and it had quietly failed, no reason given. Aaaargh.
Tried again at 9600, this time it completes the transfer. Repeated the process with the dp3e app, another 55 minutes, success. Web interface takes 10 minutes to stop showing an error but eventually everything comes right, I can log in and I can see the UPS stats etc.
What a mission this was. Next time one of these cards has an issue I'll get the client to replace the whole UPS. π
Thanks picKed, you saved my bacon a number of times. π
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-06-26 05:41 AM . Last Modified: β2024-03-19 12:38 AM
lol no problem. glad it worked..slowly but surely that is π
Link copied. Please paste this link to share this article on your social media post.
Youβve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.