Shutdown settings of PCNS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Shutdown settings of PCNS
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:49 PM . Last Modified: ‎2024-03-12 01:08 AM

0 Likes
1
625
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:49 PM . Last Modified: ‎2024-03-12 01:08 AM

Shutdown settings of PCNS

Hi Support,

Good day.

I've setup my UPS to perform graceful shutdown on my vCenter VMs and ESXi hosts.

I'm a bit confused with the PCNS Shutdown Settings:

https://:6547 --> Shutdown Settings --> UPS Shutdown.

The default option is "Do not turn off the UPS". Is it the recommended settings? When should I choose "Turn Off the UPS" or "Turn off the UPS Outlet Group" ?

Thank you.

Best regards,

Kong

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:49 PM . Last Modified: ‎2024-03-12 01:07 AM

0 Likes
0
625
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:49 PM . Last Modified: ‎2024-03-12 01:07 AM

Hi,

On 10/17/2017 6:41 AM, kong said:

The default option is "Do not turn off the UPS". Is it the recommended settings?

Yes. The default seeing has been determined based on customer feedback.

On 10/17/2017 6:41 AM, kong said:

When should I choose "Turn Off the UPS" or "Turn off the UPS Outlet Group" ?

Once PCNS has powered down the VMs and hosts they will stay off until a user intervenes and turns them on. If you would like the hosts to power on automatically when AC is restored the UPS must cut power to the host/server. If you do not select turn UPS off or turn off outlet group the UPS will continue to run on battery until drained. If AC is restored prior to the battery being drained the UPS will switch back to AC output and AC will not be cut to the host/server. In most servers BIOS you have the option to configure the system to power back up once AC has been restored so AC must be cut to have it restored.

You should configure that option and select turn off UPS or turn off outlet group if you would like the host/server to power on automatically when AC is restored. When the shutdown process is run by PCNS it will send a signal to the UPS or outlet group to power down. The UPS and or outlet group will wait a delay set on the NMC allowing the VMs and host to power down and then cut AC. When AC is restored the UPS and or outlet group will re-energize and the host will start up automatically if the BIOS has been configured properly. 

You would select turn off UPS if you want the entire load connect to the UPS to have AC cut. You would select turn off outlet group if you would like the outlet group that the host is plug into to have AC cut. Turning off only the UPS would allow the other outlet group / groups to remain powered on until AC is restored or the battery drains. 

The process is discussed on the PCNS VMware User's Guide on page 91 of the PDF. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:49 PM . Last Modified: ‎2024-03-12 01:07 AM

0 Likes
0
626
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:49 PM . Last Modified: ‎2024-03-12 01:07 AM

Hi,

On 10/17/2017 6:41 AM, kong said:

The default option is "Do not turn off the UPS". Is it the recommended settings?

Yes. The default seeing has been determined based on customer feedback.

On 10/17/2017 6:41 AM, kong said:

When should I choose "Turn Off the UPS" or "Turn off the UPS Outlet Group" ?

Once PCNS has powered down the VMs and hosts they will stay off until a user intervenes and turns them on. If you would like the hosts to power on automatically when AC is restored the UPS must cut power to the host/server. If you do not select turn UPS off or turn off outlet group the UPS will continue to run on battery until drained. If AC is restored prior to the battery being drained the UPS will switch back to AC output and AC will not be cut to the host/server. In most servers BIOS you have the option to configure the system to power back up once AC has been restored so AC must be cut to have it restored.

You should configure that option and select turn off UPS or turn off outlet group if you would like the host/server to power on automatically when AC is restored. When the shutdown process is run by PCNS it will send a signal to the UPS or outlet group to power down. The UPS and or outlet group will wait a delay set on the NMC allowing the VMs and host to power down and then cut AC. When AC is restored the UPS and or outlet group will re-energize and the host will start up automatically if the BIOS has been configured properly. 

You would select turn off UPS if you want the entire load connect to the UPS to have AC cut. You would select turn off outlet group if you would like the outlet group that the host is plug into to have AC cut. Turning off only the UPS would allow the other outlet group / groups to remain powered on until AC is restored or the battery drains. 

The process is discussed on the PCNS VMware User's Guide on page 91 of the PDF. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of