We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on
Cloud Connected vs On-Premise Services. Your feedback can
help us shape the future of services.
Learn more about the survey
or
Click here to Launch the survey
Schneider Electric Services Innovation Team!
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-07-01 02:10 AM . Last Modified: 2024-03-05 11:51 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 02:10 AM . Last Modified: 2024-03-05 11:51 PM
Context:
We never performed a runtime calibration on our Smart-UPS. So we're new on that action. After replacing two UPS we want to perform a runtime calibration via PowerChute Business Edition. There are 8 servers attached and shutdown sequence is configured to shutdown these servers (7 via shutdown script triggered via PowerChute and 1 directly by that software).
Question:
If we perform runtime calibration via PowerChute Business Edition will the configured shutdown sequence be triggered or not? We assume, no shutdown sequence will be triggered. Correct?
Thanks for your answers!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 02:10 AM . Last Modified: 2024-03-05 11:51 PM
You're right - runtime calibrations issued via software should only discharge the UPS to between 10-20% and not turn the UPS off.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 02:10 AM . Last Modified: 2024-03-05 11:51 PM
Oh sorry, no, it will not execute your script. This is not treated as a shutdown or on battery event.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 02:10 AM . Last Modified: 2024-03-05 11:51 PM
You're right - runtime calibrations issued via software should only discharge the UPS to between 10-20% and not turn the UPS off.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 02:10 AM . Last Modified: 2024-03-05 11:51 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 02:10 AM . Last Modified: 2024-03-05 11:51 PM
Sorry, but the meaning of shutdown sequence was concerning the shutdown script and not the UPS here. So will the script get triggered via software calibration (and we have to disable it) or not?
Thank you,
Sebastian
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 02:10 AM . Last Modified: 2024-03-05 11:51 PM
Oh sorry, no, it will not execute your script. This is not treated as a shutdown or on battery event.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 02:10 AM . Last Modified: 2024-03-05 11:51 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 02:10 AM . Last Modified: 2024-03-05 11:51 PM
Thanks for your, and sorry for my late response. I successfully performed a runtime calibration without any shutdown.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of