Shutdown my server ????

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Shutdown my server ????
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:36 PM . Last Modified: ‎2024-03-15 03:54 AM

0 Likes
7
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:36 PM . Last Modified: ‎2024-03-15 03:54 AM

Shutdown my server ????

HI,

I have a Smart UPS RT 7500 RM XL. I would like to shutdown my server automaticly after X mins. I Install PCNS version 2.2.2 on my client.

I have 33 mins of runtime with my batterie

I realy need somes help, Thnaks you.

Franc

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:37 PM . Last Modified: ‎2024-03-15 03:54 AM

0 Likes
0
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:37 PM . Last Modified: ‎2024-03-15 03:54 AM

Thanks you very much.

All work correctly.

Thank again.

Franc

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:36 PM . Last Modified: ‎2024-03-15 03:54 AM

0 Likes
0
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:36 PM . Last Modified: ‎2024-03-15 03:54 AM

HI,

I have a Smart UPS RT 7500 RM XL. I would like to shutdown my server automaticly after X mins. I Install PCNS version 2.2.2 on my client.

I have 33 mins of runtime with my batterie

I realy need somes help, Thnaks you.

Franc

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:36 PM . Last Modified: ‎2024-03-15 03:54 AM

0 Likes
0
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:36 PM . Last Modified: ‎2024-03-15 03:54 AM

Franc,

Perhaps just a typo, I don't think PCNS v 2.2.2 is released yet. 2.2.1 is the latest revision offered by APC. To setup your server to shutdown after the UPS has been on battery for X number of minutes you would need to log into the PCNS agent on the server by opening a browser and typing http://ipaddressofserver:3052 (actually use ip address or loopback address) From this menu, you would click on Configure Events. The options on the right, use the event UPS:On Battery. Hit the radio button for shutdown system under this event and you can configure the shutdown after the UPS has been on battery for X number of seconds, make sure you hit apply. Back in the blue section on the right, click Configure Shutdown. There is a checkbox there that says "Shutdown UPS after shutdown finishes". Make sure this box is unchecked if you want the UPS to continue to run, if you want the UPS to shutdown when that server shutsdown, leave it checked. Let me know if you have any questions.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:36 PM . Last Modified: ‎2024-03-15 03:54 AM

0 Likes
0
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:36 PM . Last Modified: ‎2024-03-15 03:54 AM

I Grenade,

I have another quetion for you...

I have a Smart-UPS 1500 connect with a USB cable. I install Powerchute business basic edition 7.0.5 on one server. I install first the agent after I intall the server on the same server and I install the console on my PC, this work correctly. But I install the agent on another server but the PCBE do not see the another server, the service APC PBE is running and all of the firewall is off ( Windows XP SP2, Windows 2000, Windows 2003) ????

Thanks again

Franc

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:36 PM . Last Modified: ‎2024-03-15 03:54 AM

0 Likes
0
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:36 PM . Last Modified: ‎2024-03-15 03:54 AM

Hello,

Are you getting "Failed to Apply Configuration Profile" when adding the second Agent to the Server/Console portion? What UPS are you using with the second Agent and what comm cable? What version of java is running on the second server? Can you get to the Agent direct on the second server via http://127.0.0.1:3052 ? Please check out the Kbase document regarding "Failed to Apply Configuration Profile"

http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=2596

Let us know how it goes. Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:36 PM . Last Modified: ‎2024-03-15 03:54 AM

0 Likes
0
1595
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:36 PM . Last Modified: ‎2024-03-15 03:54 AM

HI,

I juste have one UPS, is the Smart-UPS 1500 connect with a USB Cable.

I connect 5 applications server with one Smart-UPS 1500.

The server who have the direct connection with the batterie is OK, but the other server I have a "Failed to Apply Configuration Profile" when adding the second Agent ????

Thanks you again....

Franc

Sorry for my english...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:37 PM . Last Modified: ‎2024-03-15 03:54 AM

0 Likes
0
1596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:37 PM . Last Modified: ‎2024-03-15 03:54 AM

In order for the Agent portion of the software to work, it needs a direct line of communication to a UPS. If you do not have a communication cable to the UPS from that server, you are going to get that message every time, because the Agent software does not see a UPS.

You should use the black serial cable that came with the UPS and our Interface Expansion Card, AP9607CB, to add more serial ports for PowerChute Business Edition communication.

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9607CB

The other option is to use our Network Management Card, AP9617, and PowerChute Network Shutdown to put the UPS on your network and initiate that shutdown signal via network communication. This avoids using any communication cable.

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9617

The last option is to use the PowerChute Business Edition software on the main server, and run a shutdown script from the Agent to the second server.

Hope this helps. Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:37 PM . Last Modified: ‎2024-03-15 03:54 AM

0 Likes
0
1596
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:37 PM . Last Modified: ‎2024-03-15 03:54 AM

Thanks you very much.

All work correctly.

Thank again.

Franc

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore