Shutdown a UPS using a dry contact, but stay off until battery charged

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Shutdown a UPS using a dry contact, but stay off until battery charged
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-07-07 10:46 PM . Last Modified: โ€Ž2024-03-01 12:26 AM

0 Likes
3
1292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-07-07 10:46 PM . Last Modified: โ€Ž2024-03-01 12:26 AM

Shutdown a UPS using a dry contact, but stay off until battery charged

I'm trying to get my SMX3000HV to be shutdown either by a dry contact or when battery is too low. In both cases i want the UPS to stay off, until the battery is charged to some level.

The shutdown shall be signalized to the connected PCs using snmp and powerchute (if there is another solution, i can write batch-files and receive smnp-traps)

This is my hardware

  • SMX3000HV
  • AP9631
  • AP9810
  • AP9630
  • AP9613

First level support told me to buy the additional hardware AP9631 and AP9810 but this didnt help at all!

Any good ideas very appreciated, because i'm desperate and we really need to get this working!

I've tried a lot of combinations, but using the dry contact, the UPS either stays off on power return, or is turned on no matter of battery level.

Thanks in advance, i really hope there is one exerienced person out there, that knows a solution!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • level
  • minimum
  • network-management-card
  • shutdown
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: โ€Ž2021-07-07 10:46 PM . Last Modified: โ€Ž2024-03-01 12:26 AM

0 Likes
0
1292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-07-07 10:46 PM . Last Modified: โ€Ž2024-03-01 12:26 AM

In addition to what Angela said, I'll summarize a bit before discussing simple signaling.

- APC prefers to work in terms of runtime rather than % of charge. This is because as the battery ages, 20% charge may be less and less runtime.

- Outlet Turn Off Delay (lets call this X) - Set this to the amount of time loads need to turn off. PCNS will automatically set this for outlets its registered with.

- Minimum Return Runtime - Set this to X + whatever time loads need to start up. This ensures UPS can deliver this much runtime before it turns on the outlets after a power outage.

- Load Shedding or PCNS - either PCNS or the NMC can initiate UPS shutdown. From the NMC, this is done by enabling "Turn off outlet groups when... UPS runtime is less than Y seconds". Set this to at least X.

For the dry contact: If you can't make the AP9810 work, the UPS should have built in support for a mechanism called "Simple Signaling" where there's an input "lo_batt" on the RJ50 port. Shorting it to ground causes the UPS to tell PCNS to shut down. See pinout here:

http://pinoutsguide.com/UPS/apc_usb_cable_pinout.shtml

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: โ€Ž2021-07-07 10:46 PM . Last Modified: โ€Ž2024-03-01 12:26 AM

0 Likes
0
1292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-07-07 10:46 PM . Last Modified: โ€Ž2024-03-01 12:26 AM

Hello Angela

Thanks for your reply!

I found those settings in the Webinterface. AFIK if I use the turn off and stay off setting, the UPS stays off. But this is not what i want.

We are using the UPS as a buffer. In case of a powerloss, the system should be operatable as usual, until the battery is empty or someone turns it off using a dry contact.

In an optimal case, turning off the system would also work when power is still there. But i think this is against the nature of the UPS ๐Ÿ˜ƒ So we cut the powerline with the same dry contact as well using a relay.

We need the UPS to charge its battery before turning on. When does the "Min return time" apply? What command do i need to use? I've tried many. Upon Shutdown from the dry contacts the UPS is not charging first. Same if I use Telnet and CLI.

Could Powerchute confuse the shutdown?

If you have another good idea, working with relays and UPS outputs, this is doable as well. We just need to get this behaviour.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-07-07 10:46 PM . Last Modified: โ€Ž2024-03-01 12:26 AM

0 Likes
0
1292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-07-07 10:46 PM . Last Modified: โ€Ž2024-03-01 12:26 AM

Hi Mathias,

Ok, I misunderstood on the turn off thing and read it wrong I think. So the turn off and stay off would not apply or work for what you want. I thought you said turn off and stay off OR wait to charge up to a particular charge level.

You can turn off the UPS output power when AC power is present even if the battery is charged but then you'll need to command it back on via some means (dry contact, web interface, etc). Minimum return runtime would not apply here since the battery would be charged up. You may want to do a separate input for on and off and then the only things at the outlet group level that should apply would be your power on/off delay. 

Minimum runtime is usually used for scenarios where you have a power outage, your UPS is discharged, and you want to avoid a situation where the power is trying to come back on but going on/off constantly while stabilizing. When AC power tries to come back, the UPS will try to turn back on (assuming it is set to 0 seconds) and you won't want that if the power goes off again and the UPS has no charge and turns everything off while it was trying to start up again.

In your situation, would shutting off the UPS and specifying a sleep time work for the scenarios where the UPS hasn't run out of battery? That would avoid you having to turn it back on and you could specify a sleep time for it to automatically come back on.

For the situation when the UPS runs out of battery, minimum return runtime setting on each outlet group should be the key to make the UPS wait before it turns right back on when it is discharged. When the UPS turns off, it takes a snapshot of the load percentage so that it knows what it will take to reach whatever you set it to for your particular load % (ex. 20 minutes).

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: โ€Ž2021-07-07 10:46 PM . Last Modified: โ€Ž2024-03-01 12:26 AM

0 Likes
0
1293
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-07-07 10:46 PM . Last Modified: โ€Ž2024-03-01 12:26 AM

In addition to what Angela said, I'll summarize a bit before discussing simple signaling.

- APC prefers to work in terms of runtime rather than % of charge. This is because as the battery ages, 20% charge may be less and less runtime.

- Outlet Turn Off Delay (lets call this X) - Set this to the amount of time loads need to turn off. PCNS will automatically set this for outlets its registered with.

- Minimum Return Runtime - Set this to X + whatever time loads need to start up. This ensures UPS can deliver this much runtime before it turns on the outlets after a power outage.

- Load Shedding or PCNS - either PCNS or the NMC can initiate UPS shutdown. From the NMC, this is done by enabling "Turn off outlet groups when... UPS runtime is less than Y seconds". Set this to at least X.

For the dry contact: If you can't make the AP9810 work, the UPS should have built in support for a mechanism called "Simple Signaling" where there's an input "lo_batt" on the RJ50 port. Shorting it to ground causes the UPS to tell PCNS to shut down. See pinout here:

http://pinoutsguide.com/UPS/apc_usb_cable_pinout.shtml

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of