Shutdown VA: PowerChute Services are disabled due to invalid credentials after each reboot

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Shutdown VA: PowerChute Services are disabled due to invalid credentials after each reboot
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
edvzim
edvzim
Cadet

Posted: ‎2023-06-11 10:35 AM . Last Modified: ‎2023-06-11 10:54 AM

0 Likes
3
6289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-11 10:35 AM . Last Modified: ‎2023-06-11 10:54 AM

Shutdown VA: PowerChute Services are disabled due to invalid credentials after each reboot

I installed the PowerChute Shutdown Virtual Appliance 5.0 on a standalone ESXi 8.0 host. I finished the Setup Wizard successfully and configured the shutdown options.

 

But after every reboot of the Virtual Appliance the message "PowerChute Services are disabled due to invalid credentials" is shown on the console.

 

Also I cannot access the Web Interface.

 

Only after entering username and password again in pcnsconfig.ini under [NetworkManagementCard] and restarting the PowerChute service am I able to login. The rest of the configuration seems to have stayed to same - only username and password are lost.

 

What can I do?

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2023-06-12 12:55 PM . Last Modified: ‎2023-06-14 06:21 AM

0 Likes
2
6268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-12 12:55 PM . Last Modified: ‎2023-06-14 06:21 AM

@edvzim 

 

After entering the username and password in the pcnsconfig.ini are you manually starting the PowerChute service to access the web UI? If so log into the PowerChute VM and run the command systemctl enable PowerChute. The next time there is a restart the PowerChute service will start automatically. 

Reply

Link copied. Please paste this link to share this article on your social media post.

edvzim
edvzim
Cadet

Posted: ‎2023-06-12 02:03 PM

In response to BillP
0 Likes
1
6264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-12 02:03 PM

Hi Bill,

 

thank you for your reply. I already ran that command previously. The PowerChute service does start automatically after rebooting. I can navigate to the login form via https sucessfully. But after entering the correct user and password on the web page I only get the error message that user or password is invalid.
Only after stopping the service, saving user and password in the pcnsconfig.ini and restarting the service am I able to login.

 

Could you try to reboot your Virtual Appliance and check if you can still login?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2023-07-06 09:55 AM . Last Modified: ‎2023-07-06 09:59 AM

In response to edvzim
0 Likes
0
5936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-06 09:55 AM . Last Modified: ‎2023-07-06 09:59 AM

Hi,

 

Sorry for the delayed reply.

 

I tested 3 VMs and could not reproduce the issue. Since the OVF has not been configured with vCenter I suggest powering off the VM and install a clean/new VM. It is possible the pcnsconfig.ini or M11.cfg files have been corrupted and that would cause the issue. 

 

• The maximum number of characters for the user name is 10.
• The password requires:
• Minimum 8 and maximum 128 characters in length
• One upper and lower case letter
• One number and special character
• The username cannot be part of the password.
• Leading and trailing white spaces in passwords are removed.
• Passwords containing a white space are kept.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore