Should I buy the SUA2200XL-NETPKG or SMX2200RMLV2U and network adapter

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Should I buy the SUA2200XL-NETPKG or SMX2200RMLV2U and network adapter
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:12 AM

0 Likes
10
2352
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:12 AM

Should I buy the SUA2200XL-NETPKG or SMX2200RMLV2U and network adapter

My goal is to protect 3 servers with one UPS. I read in [this forum post|http://forums.apc.com/spaces/5/smart-ups-symmetra-lx-rm/forums/general/1865/lost-communication-with-...] that there are two approaches to monitoring multiple servers from one ups: either add more serial ports to the UPS, or a network card. I would like to use the network option, and i'm a bit confused about which UPS to buy.

Does the SUA2200XL-NETPKG come with everything I need to protect 3+ servers? Would I get any additional features by going with the SMX2200RMLV2U and adding a SmartSlot network adapter?

If it helps, the servers are averaging about 550W total under normal load, but my company is growing fast and I believe that this load could rise substantially in the next 2 years. If that happens, I want a UPS that supports additional external batteries, which would allow me to maintain run times as the load grows.

Thanks,
Matt

Message was edited by: mweeks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:11 AM

0 Likes
0
2352
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:11 AM

sir = miss O:-)

you're welcome..let us know if you need anything else.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:12 AM

0 Likes
0
2352
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:12 AM

SUA2200XL is going to be discontinued soon and SMX2200 is going to be taking its place. SMX2200 is a more modern UPS that utilizes the microlink protocol. SMX has a nifty LCD as well.

for what you want to do via the network method, both units will work with an AP9630 or AP9631 network management card though since they are both compatible. i guess it just depends if you want the latest and greatest UPS model since both support the latest and greatest network card model and multiple server shutdown.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:12 AM

0 Likes
0
2353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:12 AM

I just got off the phone with APC sales and they said that the SMX2200RMLV2U is out of stock, and backordered until August. The sales agent also contacted resellers and could not find one available. Unfortunately, I need a new UPS right now, because my existing one has failed completely.

What is the microlink protocol and which features does is bring to the UPS? Is it proprietary to APC?

The SUA2200XL-NETPKG is in stock, so I might have to buy the older one out of necessity.

Thanks,E

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:12 AM

0 Likes
0
2353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:12 AM

Hi Matt,

I hope this link gives you an idea about Microlink.

Thank you for using APC Discussion Forum. Have a good one!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:12 AM

0 Likes
0
2353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:12 AM

we will have support for SUA2200XL so there wont be a problem there - i guess i did not realize they were backordered 😞

so yes, microlink is the internal communication protocol for the UPS. the article that judy posted will help you out. but, for using the network management cards to gracefully shutdown the network management card with powerchute network shutdown, everything works the same between SUA2200XL and SMX2200. i would go ahead and get the SUA2200XL if you need a UPS immediately and can do without the fancy LCD.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:11 AM

0 Likes
0
2353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:11 AM

I read in [this article|http://nam-en.apc.com/app/answers/detail/a_id/10816/kw/Microlink%20FAQS/related/1] that the new models offered power savings as well as the shiny new LCD. Are there any other significant internal hardware improvements?

Thanks for all the support thus far πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:11 AM

0 Likes
0
2353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:11 AM

yes, i think that they are more efficient and i also think that incase of failure, there are preventive measures in place internally to prevent a dropped load. i think both UPSs have some type of that but i think it is a different design in the SMX units. i used to support the Smart UPS more so than i do now but i can find out more tomorrow if you want. my focus now is more network management cards, rack pdus and those types of things.

outlet groups with load shedding is another feature the SMX units have that the SUA units dont and the battery packs that the SMX units have are intelligent meaning you just plug them in and the UPS detects them. on the SUA unit you have to program them in manually either via the NMC by typing the quantity in or via some other type of software. hmm what else..SUA units are compatible with some of our currently existing smart slot accessories besides the network management cards if you needed those but SMX units arent as of today besides a few like the Network Management Card and AP9620 that was in one of those knowledgebases. don't think that matters for what you wanted though.

SMX units allow you to do all the CO2 calculations and stuff within the network management card where as SUA units don't support that.

i guess the biggest issue that i can stress is that the SMX units are what is being currently developed on firmware wise and its firmware upgradable. SUA2200XL is a solid unit but it is being replaced. it will certainly get the job done and be supported hardware wise but just does not have those bells and whistles i mentioned.

let me know if there are any points you'd like me to elaborate on for you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:11 AM

0 Likes
0
2353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:11 AM

Of course there are more questions πŸ˜„

bq. "outlet groups with load shedding is another feature the SMX units have \\ that the SUA units dont and the battery packs that the SMX units have \\ are intelligent meaning you just plug them in and the UPS detects them. \\ on the SUA unit you have to program them in manually either via the NMC \\ by typing the quantity in or via some other type of software."
What is load shedding on the outlet groups? I'm also curious about the smart battery packs. Are you talking about the internal batteries or the external battery packs like SMX120RMBP2U or SUA48XLBP.
My experience to this point has been with consumer grade Back-UPSs, which have batteries connected by two wires (pretty dumb technology but it works).

More importantly, are the SUA48XLBP supplemental batteries being discontinued as well? Are the SMX120RMBP2U batteries backwards compatible with the SUA model? I chose an extended run product because I want this UPS to be flexible enough to meet our business demands for a few years, and the ability to tack on some extra batteries played a large role in this plan.

Thanks,E

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:11 AM

0 Likes
0
2353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:11 AM

i attached the applicable app note since i couldnt get it to link from the apc.com website for some reason. that should cover the abilities of the outlet groups and the load shedding.

the battery packs for SMT/SMX and SUA are not forward or reverse compatible or interchangeable unfortunately 😞 when i say battery packs, i am talking external battery packs like the SMX120RMBP2U or SUA48XLBP that you mentioned.

some more information that I found for you:

we typically sell the complete battery pack, e.g., SUA48RMXLBP3U or SMX120RMBP2U for 1 to 2 years after the UPS is EOL, removed from the market. And the RBCs for both UPS and External Battery Pack are continued for 10 years after EOL of the UPS and Battery Pack.

also:

i wanted you to know if you are currently looking at SUA2200XL-NETPKG, that is not technically end of life yet... it is a short depth, wide tower form factor. you can definitely use SMX instead, but SMX2200RMLV2U has L5-30P input whereas SUA2200XL-NETPKG has a 5-20P. The correct SMX SKU with the same input is SMX2000RMLV2U, which is now available with the NC suffix, so it is the replacement for SUA2200R3XLNETPKG and can replace SUA2200XL-NETPKG. If you 'want' a NEMA L5-30P input, you can order SMX2200RMLV2U, but would need to order the NMC in addition, which is AP9630 or AP9631.

SMX that have the NMC preinstalled are SMX2000RMLV2UNC 5-20P input and SMX3000RMLV2UNC L5-30P input. One other item to look at is how many outlets you require... SMX RM2U have only seven total outlets compared to SUA2200XL-NETPKG and the former RMXL3U having 11 total outlets. SMX2000RMLV2U/NC have a locking L5-20R for external PDU if needed.

SUA2200XL-NETPKG will still be an active SKU through mid year next year... but I would say SMX is nicer due to the high frequency platform... if you don't mind a tall skinny tower with fewer outlets

anyway.. but I suspect the correct SMX for you... SMX2000RMLV2U is NOT on backorder... if you had ordered SMX2200RMLV2U he would have gotten a surprise with the input being L5-30P (2000 vs 2200VA).

hope this helps πŸ˜„

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:11 AM

0 Likes
0
2352
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:11 AM

Wow! I did not even notice the plug change from the 2200VA SUA to SMX series. Good call sir B-)

I would have indeed be upset (mostly at myself) when the new unit arrived, and then promptly called an electrician. I was already starting to lean towards the 2000VA model as my need is great, but I don't want to get old-ish hardware, and your help sealed the deal.

My new 2000VA unit arrived and is installed. Now I'v just got to figure out the settings for a graceful shutdown.

Thanks
Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:11 AM

0 Likes
0
2353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 02:11 AM . Last Modified: β€Ž2024-03-11 12:11 AM

sir = miss O:-)

you're welcome..let us know if you need anything else.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore