Posted: 2023-09-28 11:03 AM
Hello,
I have a couple of UPS's (SRT5KRMXLT) which I would like to get onto the network. One of them is all set, but the other simply won't obtain an IP address, so I would like to try setting a static IP. I have not been successful setting the IP via the front LCD console and I don't have the original RJ45 console cable.
Looking at the back of the UPS, I see there is a reset button. Would pushing this just reboot the built in network card, or does it do more than that?
As a follow up question I don't see firmware specifically for this built in adapter (AP9537SUM). Where would I find the firmware to update these cards?
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-29 05:19 AM
Go to https://www.apc.com/us/en/download/software-firmware/.
Enter AP9630 as the model/part number and download Network Management Card 2 (NMC2) v7.1.2 Firmware for Smart-UPS with AP9630/31 The SUMX firmware is the correct firmware for the AP9537SUM
To reset the NMC, press and hold the reset button that will be found on the right-hand side of the card for 20 seconds.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-29 05:19 AM
Go to https://www.apc.com/us/en/download/software-firmware/.
Enter AP9630 as the model/part number and download Network Management Card 2 (NMC2) v7.1.2 Firmware for Smart-UPS with AP9630/31 The SUMX firmware is the correct firmware for the AP9537SUM
To reset the NMC, press and hold the reset button that will be found on the right-hand side of the card for 20 seconds.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-04 07:31 AM
Thank you that solved my problem.