Hi all,
Please, help! How to set up the time of automatic turn on the Smart-UPS SMT2200 without PCBE after a power restore?
Where for Main Outlets the option 'Turn on outlet group automatically when AC utility power returns'?
There are only such options for Main Outlets Config: Turn On Delay, Turn Off Delay, Reboot Duration, Minimum Return Time.
But they do not affect the automatic turning on of the UPS.
Under the control of the PCBE, when the server is turned on, shutting down the UPS when the power is interrupted and automatically turning on the UPS when power is restored without any problems.
At the moment, when server and PCBE are not running, with a loss of power, the UPS turn off (Main Outlet and Group 1) according to settings Load Shed on Battery. When the power is restored, the UPS does not turn on automatically.
Any help would be greatly appreciated.
Thanks for help
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:12 AM . Last Modified: 2024-03-15 06:01 AM
Hi,
On 5/7/2019 12:22 AM, Mark said:At the moment, when server and PCBE are not running, with a loss of power, the UPS turn off (Main Outlet and Group 1) according to settings Load Shed on Battery. When the power is restored, the UPS does not turn on automatically.
You will need to install a network management card into the UPS. Within the NMC interface you can configure the UPS to power back on when AC is restored. This would be found under Configuration, Outlet Groups, Select the outlet group and go to load shedding. You would need to uncheck stay off after power returns.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:12 AM . Last Modified: 2024-03-15 06:01 AM
Hi,
On 5/7/2019 12:22 AM, Mark said:At the moment, when server and PCBE are not running, with a loss of power, the UPS turn off (Main Outlet and Group 1) according to settings Load Shed on Battery. When the power is restored, the UPS does not turn on automatically.
You will need to install a network management card into the UPS. Within the NMC interface you can configure the UPS to power back on when AC is restored. This would be found under Configuration, Outlet Groups, Select the outlet group and go to load shedding. You would need to uncheck stay off after power returns.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.