Servers panic abrupt loss power SRT10KVA

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Servers panic abrupt loss power SRT10KVA
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
adiriot
adiriot
Cadet

Posted: ‎2021-11-17 11:39 PM

0 Likes
0
962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-17 11:39 PM

Servers panic abrupt loss power SRT10KVA

One of the racks have all the servers crashed abruptly. Can anyone interpret from this log? It returned from bypass and the message graceful shutdown period has ended and outlet groups was turned off. We had a power shutdown for a few minutes, the ups lcd panel states that it should last 3hrs.

 

11/10/2021 11:18:26 Device UPS: Main input bad cleared. 0x01B1
11/10/2021 11:18:25 Device UPS: No longer on battery power. 0x010A
11/10/2021 11:18:25 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
11/10/2021 11:16:57 Device UPS: Main input bad. 0x01B0
11/10/2021 11:16:57 Device UPS: On battery power in response to low input frequency. 0x0109
11/10/2021 11:16:56 Device UPS: Bypass not in range ; distorted waveform. 0x020F
11/10/2021 11:05:26 Device UPS: Self-Test passed. 0x01D2
11/10/2021 11:05:05 Device UPS: Self-Test started by front panel. 0x0137
11/10/2021 11:04:37 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned on. 0x0134
11/10/2021 11:04:37 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned on. 0x0134
11/10/2021 11:04:37 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on. 0x0134
11/10/2021 11:04:37 Device UPS: The power for the main outlet group, Unswitched Group, is now turned on. 0x0134
11/10/2021 11:04:36 Device UPS: The output power is now turned on. 0x0113
11/10/2021 11:04:34 Device UPS: Main outlet group, Unswitched Group, has been commanded to turn on, sequenced. 0x0174
11/10/2021 11:04:33 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to turn on, sequenced. 0x0174
11/10/2021 11:04:33 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to turn on, sequenced. 0x0174
11/10/2021 11:04:33 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to turn on, sequenced. 0x0174
11/10/2021 11:04:30 Device UPS: An abnormal output voltage no longer exists. 0x0129
11/10/2021 11:00:43 Device UPS: Main input bad cleared. 0x01B1
11/10/2021 11:00:42 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
11/10/2021 10:56:48 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
11/10/2021 10:56:48 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
11/10/2021 10:56:48 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
11/10/2021 10:56:48 Device UPS: The power for the main outlet group, Unswitched Group, is now turned off. 0x0135
11/10/2021 10:56:48 Device UPS: Main input bad. 0x01B0
11/10/2021 10:56:48 Device UPS: The output power is turned off. 0x0114
11/10/2021 10:56:48 Device UPS: The graceful shutdown period has ended. 0x014F
11/10/2021 10:56:48 Device UPS: Return from bypass, internal hardware fault no longer present. 0x01B2
11/10/2021 10:56:48 Device UPS: Bypass not in range ; distorted waveform. 0x020F
11/10/2021 10:43:39 Device UPS: In bypass in response to an internal hardware fault. 0x011B
11/10/2021 10:43:39 Device UPS: An abnormal output voltage exists. 0x0128
11/10/2021 10:43:34 Device UPS: Main input bad cleared. 0x01B1
11/10/2021 10:43:33 Device UPS: No longer on battery power. 0x010A
11/10/2021 10:43:33 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
11/10/2021 10:43:11 Device UPS: On battery power in response to rapid change of input. 0x0109
11/10/2021 10:43:11 Device UPS: Bypass not in range ; low voltage. 0x020F
11/10/2021 10:43:11 Device UPS: Main input bad. 0x01B0

Labels
  • Labels:
  • Datacenter Accessories
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore