Self-Test Refused for unknown reason

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Self-Test Refused for unknown reason
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:30 AM

0 Likes
1
3647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:30 AM

Self-Test Refused for unknown reason

Self-Test Refused for unknown reason
Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:30 AM

0 Likes
0
3646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:30 AM

Your NMC web interface is set up to call for a self-test, correct?  If so, what option did you select?  Mine is set to call for the self-test on startup and every fourteen days after the last test.  My log looks like this:

UPS Tests

Test Result Date Source Cause
Self-Test Passed 07/26/2017 internal operation NA
Calibration Failed 07/26/2017 Aborted NA

I am not sure what "internal operation" means but I suspect that was when I started the UPS up after powering it down and removing and reinstalling the battery and not the fourteen day scheduling that I set up.  Can you turn the UPS off, remove the battery, and restart the UPS with the load attached and see if the self-test runs to completion?  If not, it could be something with your battery system either having low capacity, etc.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:30 AM

0 Likes
0
3647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:30 AM

Your NMC web interface is set up to call for a self-test, correct?  If so, what option did you select?  Mine is set to call for the self-test on startup and every fourteen days after the last test.  My log looks like this:

UPS Tests

Test Result Date Source Cause
Self-Test Passed 07/26/2017 internal operation NA
Calibration Failed 07/26/2017 Aborted NA

I am not sure what "internal operation" means but I suspect that was when I started the UPS up after powering it down and removing and reinstalling the battery and not the fourteen day scheduling that I set up.  Can you turn the UPS off, remove the battery, and restart the UPS with the load attached and see if the self-test runs to completion?  If not, it could be something with your battery system either having low capacity, etc.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of