Self-Test Refused for unknown reason
  • Self-Test Refused for unknown reason
Posted: ‎2021-06-28 06:19 AM . Last Modified: ‎2024-03-18 02:30 AM
4228
Your NMC web interface is set up to call for a self-test, correct?  If so, what option did you select?  Mine is set to call for the self-test on startup and every fourteen days after the last test.  My log looks like this:
UPS Tests
Test Result Date Source Cause
Self-Test Passed 07/26/2017 internal operation NA
Calibration Failed 07/26/2017 Aborted NA
I am not sure what "internal operation" means but I suspect that was when I started the UPS up after powering it down and removing and reinstalling the battery and not the fourteen day scheduling that I set up.  Can you turn the UPS off, remove the battery, and restart the UPS with the load attached and see if the self-test runs to completion?  If not, it could be something with your battery system either having low capacity, etc.
UPS Tests