Script against PowerChute Personal Edition?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Script against PowerChute Personal Edition?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:47 AM . Last Modified: ‎2024-03-06 12:13 AM

0 Likes
2
1632
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:47 AM . Last Modified: ‎2024-03-06 12:13 AM

Script against PowerChute Personal Edition?

I just purchased a Back-UPS (BE750G) and installed PowerChute Personal Edition. Is there any way I can pull information from PowerChute via a script? Does PowerChute write the the Windows event log? I was thinking about writing a powershell script to email me when it goes on battery power. I'm not sure if the UPS beep will wake me up if I'm asleep, and I won't receive a notification if I'm away from my home office. Is there a WMI object I can access since the battery is connected via USB? I'm really looking for any way to get battery/power status for scripting. Thanks!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • apc
  • back-ups
  • be750g
  • e-mail
  • event
  • log
  • notification
  • personal
  • PowerChute
  • powershell
  • script
  • windows
  • wmi
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:47 AM . Last Modified: ‎2024-03-06 12:13 AM

1 Like
0
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:47 AM . Last Modified: ‎2024-03-06 12:13 AM

I have set up email notification for UPS events triggered by entries that PowerChute Personal Edition writes in the Event Log.
All information below is based on my implementation on Windows 7 Professional. I expect it works on other Windows 7 versions but I have not tested it on anything else.
The following UPS-related events are the ones I use to trigger email alerts:
Application Log / Event ID 174 (Battery backup transferred to battery power due to a blackout.)
Application Log / Event ID 61455 (Battery backup transferred to AC utility power.)
System Log / Event ID 13 (The operating system is shutting down at system time ?2012?-?12?-?10T22:09:22.256932100Z.) - the email may or may not get sent out for this event,
depending on the timing of shutting down the SMTP server used to relay the email.

Open Event Viewer and locate an instance of the Event ID for which you want to send an email notification. You may need to remove AC power from your UPS input to generate Events 174 and 61455 if you don't already have any instances in your Event Log. Right-click on the event and select "Attach task to this event."
Add a description if you wish and click Next, then Next again.
Click the button for "Send an e-mail" and click Next.
Fill out the From, To, Subject, and SMTP Server. I send from myself to myself and put a brief description of the event (i.e., Computer on Battery) in the subject and leave the message field blank.
For SMTP server, enter 127.0.0.1 to use a local SMTP relay server.
Mke sure the box is checked to "Open the properties dialog for this task when I click Finish," then click Finish.
On the General tab I have clicked on the button to Run whether user is logged on or not and ticked the box to Run with highest priveleges. (My account is an admin acct.)
On the Conditions tab I have unchecked the box to Start the task only if the computer is idle ... and Start the task only if the computer is on AC power.
On the Settings tab I have checked Allow task to be run on demand (so I can easily test it), Stop the task if it runs longer than [1 hour, the minimum], and If the running task
does not end when requested, force it to stop, I have unchecked all the other boxes.

If you already have an SMTP relay server running, you are done. If you don't have one, you can download one free here:
http://www.windows7download.com/win7-free-smtp-server/dxnrjvpv.html
Note: This Free SMTP Server does not run as a service. It must be started in order to relay email messages. I put a shortcut for it into my Startup folder and start it minimized.

I hope this information may be of use to someone else.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:47 AM . Last Modified: ‎2024-03-06 12:13 AM

0 Likes
0
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:47 AM . Last Modified: ‎2024-03-06 12:13 AM

i locked your other thread since it was a duplicate and this one is located in the correct spot.

we can refer to it here: Referenced content removed

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:47 AM . Last Modified: ‎2024-03-06 12:13 AM

1 Like
0
1632
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:47 AM . Last Modified: ‎2024-03-06 12:13 AM

I have set up email notification for UPS events triggered by entries that PowerChute Personal Edition writes in the Event Log.
All information below is based on my implementation on Windows 7 Professional. I expect it works on other Windows 7 versions but I have not tested it on anything else.
The following UPS-related events are the ones I use to trigger email alerts:
Application Log / Event ID 174 (Battery backup transferred to battery power due to a blackout.)
Application Log / Event ID 61455 (Battery backup transferred to AC utility power.)
System Log / Event ID 13 (The operating system is shutting down at system time ?2012?-?12?-?10T22:09:22.256932100Z.) - the email may or may not get sent out for this event,
depending on the timing of shutting down the SMTP server used to relay the email.

Open Event Viewer and locate an instance of the Event ID for which you want to send an email notification. You may need to remove AC power from your UPS input to generate Events 174 and 61455 if you don't already have any instances in your Event Log. Right-click on the event and select "Attach task to this event."
Add a description if you wish and click Next, then Next again.
Click the button for "Send an e-mail" and click Next.
Fill out the From, To, Subject, and SMTP Server. I send from myself to myself and put a brief description of the event (i.e., Computer on Battery) in the subject and leave the message field blank.
For SMTP server, enter 127.0.0.1 to use a local SMTP relay server.
Mke sure the box is checked to "Open the properties dialog for this task when I click Finish," then click Finish.
On the General tab I have clicked on the button to Run whether user is logged on or not and ticked the box to Run with highest priveleges. (My account is an admin acct.)
On the Conditions tab I have unchecked the box to Start the task only if the computer is idle ... and Start the task only if the computer is on AC power.
On the Settings tab I have checked Allow task to be run on demand (so I can easily test it), Stop the task if it runs longer than [1 hour, the minimum], and If the running task
does not end when requested, force it to stop, I have unchecked all the other boxes.

If you already have an SMTP relay server running, you are done. If you don't have one, you can download one free here:
http://www.windows7download.com/win7-free-smtp-server/dxnrjvpv.html
Note: This Free SMTP Server does not run as a service. It must be started in order to relay email messages. I put a shortcut for it into my Startup folder and start it minimized.

I hope this information may be of use to someone else.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of